Default Locations Where Gfci Protection Is Required

Ground-fault circuit interrupters



Accessory buildings, dwelling
units, 210.8(A)(2)
Aircraft hangars, 513.12
Appliances
Drinking fountains, 422.51
High-pressure spray washers,
422.49
Vending machines, 422.51
Basements, dwelling units, unfinished,
210.8(A)(5)
Bathtubs, hydromassage, 680.71
Carnivals, circuses, fairs, and
similar events, 525.23
Definition, Art. 100–I
Electrically operated pool covers,
680.27(B)(2)
Electric signs, portable or mobile,
600.10(C)(2)
Electrified truck parking space
supply equipment,
626.24(D)
Elevators, dumbwaiters, escalators,
moving walks,
platform lifts, and stairway
chairlifts, 620.85
Fixed electric space-heating
equipment cables,
424.44(G)
Fountains, 680.51(A)
Garages, commercial, 511.12
Garages, dwelling units,
210.8(A)(2)
Generators, portable, 445.20
Naturally and artificially made
bodies of water, electrical
equipment for,
682.15
Permitted uses, 210.8, 215.9
Personnel, protection for, 426.32







Pipeline heating, 427.27




Pools and tubs for therapeutic
use, 680.62(A),
680.62(E)
Receptacles, 210.8
Bathrooms, in dwelling units,
210.8(A)(1)
Bathrooms in other than
dwelling units,
210.8(B)(1)
Boathouses, 555.19(B)(1)
Construction sites, at, 590.6
Fountains, 680.57(B), 680.58
Garages, in dwelling units,
210.8(A)(2)
Health care facilities,
517.20(A), 517.21
Kitchens in dwelling units,
210.8(A)(6)
Marinas and boatyards,
555.19(B)(1)
Mobile homes, 550.13(B),
550.32(E)
Outdoors, dwelling units,
210.8(A)(3)
Park trailers, 552.41(C)
Pools, 680.5, 680.6,
680.22(A)(4),
680.22(B), 680.32,
680.62(E)
Recreational vehicles,
551.40(C), 551.41(C)
Replacement, 406.3(D)(2)
Required, 210.8
Rooftops in other than dwelling
units, 210.8(B)
Sensitive electronic equipment,
647.7(A)
Spas and hot tubs, 680.43(A),
680.44
Wet bar sinks, 210.8(A)(7)
Swimming pools,









see Swimming




pools, fountains, and
similar installations

Split Second Safety GFCI

Code Proposal Development for the 2011 NEC
The NEC is revised every 3 years. What are some of your ideas for any changes?

Any new ideas for your proposals for the 2011 NEC must be done at this proposal stage and sent in before 11/7/08.

Otherwise, you’ll have to wait for the 2014 NEC!

Here's a new Power Point file developed by the IAEI: www.IAEI.org

1. Developing good proposals

2. Online proposals are also permitted by NFPA.

Last edited by jtedesco1; 5/6/08 at 7:14 AM.. Reason: add video and links
Reply With Quote
  #2  
Old 4/30/08, 10:25 AM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: Locations Where Gfci Protection Is Required

Do you have the dates each of those went into effect?



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #3  
Old 4/30/08, 11:40 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Locations Where Gfci Protection Is Required

Reviewing the NEC editions from 1968 on, and searching the index will have that information, Very good question.

I sold most of my old NEC's to Jerry Peck, but maybe the NFPA Library 617-770-3000 can help with that information.

I will bet Mike knows, or will give this assignement to his students, I hope.
Reply With Quote
  #4  
Old 4/30/08, 11:48 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Locations Where Gfci Protection Is Required

Quote:
Originally Posted by bwiley
Do you have the dates each of those went into effect?
I know that the book that many home inspectors have "Electrical Inspection of Existing Dwellings" has a chart in it with all those dates. I think that book might be out of print now. It was pretty expensive, as I remember.
Reply With Quote
  #5  
Old 4/30/08, 1:59 PM
Blaine Wiley Blaine Wiley is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Rotonda West, FL
Posts: 3,186
Send a message via MSN to bwiley
Default Re: Locations Where Gfci Protection Is Required

I have a list that I believe came from that book, but it isn't up to date and as inclusive as the locations that Joe posted.



Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties.
Abraham Lincoln



www.qualityhomeinspectionsfl.com
Reply With Quote
  #6  
Old 4/30/08, 2:07 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Locations Where Gfci Protection Is Required

That list could be updated so we can be sure of the dates, again the index in each code can be a good place for us to start.

Here's another option:

215.9 Ground-Fault Circuit-Interrupter Protection for Personnel.
Feeders supplying 15- and 20-ampere receptacle branch circuits shall be permitted to be protected by a ground-fault circuit interrupter in lieu of the provisions for such interrupters as specified in 210.8 and 590.6(A).

Reply With Quote
  #7  
Old 5/4/08, 2:40 PM
Bruce Erny Bruce Erny is offline
New User
 
Join Date: Apr 2008
Location: SW Florida
Posts: 18
Please Note: Bruce Erny is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Locations Where Gfci Protection Is Required

[quote=Marc D. Shunk]I know that the book that many home inspectors have "Electrical Inspection of Existing Dwellings" has a chart in it with all those dates. I think that book might be out of print now. It was pretty expensive, as I remember.[/quot

Here is an easy to follow version. http://www.mikeholt.com/documents/ne...ment_page2.pdf
Reply With Quote
  #8  
Old 5/4/08, 3:00 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Locations Where Gfci Protection Is Required

cutting through the chatter.

When if at all does GFCI need to be on an counter Island .I thought only with in 6 feet.

Some one said they all need it.

Refering to near a kitchen though it should not matter .
Reply With Quote
  #9  
Old 5/4/08, 3:52 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Locations Where Gfci Protection Is Required

For a few code cycles now in a residence it has been ALL receptacles serving kitchen counters. The "six foot rule" as been gone for a while.

General use wall receptacles do not require GFI protection.
Reply With Quote
  #10  
Old 5/4/08, 8:55 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Locations Where Gfci Protection Is Required

Ok... serving kitchen counters

What constitutes a kitchen counter since an Island is far away from water?
Reply With Quote
  #11  
Old 5/4/08, 9:11 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Locations Where Gfci Protection Is Required

I agree. I have done kitchens with isolated sections of counter that were on opposite walls from the sink and totally removed.
GFI's made NO sense whatsoever, but were required.

I don't think there is any denying that an island counter is still a counter though.
Reply With Quote
  #12  
Old 5/4/08, 9:51 PM
Bob Elliott's Avatar
Bob Elliott Bob Elliott is offline
InterNACHI Member
 
Join Date: Aug 2006
Location: Chicago
Posts: 21,916
Default Re: Locations Where Gfci Protection Is Required

Ok ....
I always figure part of a continuous counter, but will make note.
Reply With Quote
  #13  
Old 5/4/08, 11:29 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Locations Where Gfci Protection Is Required

The 210.08(A)(6) rule about GFCIs just says "countertops", there is no reference to sinks or water. They specifically address peninsulas and islands.
Basically if you are barefoot on a ceramic tile floor you might as well be ankle deep in water.

Last edited by Greg Fretwell; 5/4/08 at 11:36 PM..
Reply With Quote
  #14  
Old 5/4/08, 11:47 PM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,973
Default Re: Locations Where Gfci Protection Is Required

Quote:
Originally Posted by relliott
cutting through the chatter.

When if at all does GFCI need to be on an counter Island .I thought only with in 6 feet.

Some one said they all need it.

Refering to near a kitchen though it should not matter .
They all need it Bob, it turns out that many of the appliances you plug in, in the kitchen have something to do with liquid.
Reply With Quote
  #15  
Old 5/5/08, 12:08 AM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Locations Where Gfci Protection Is Required

Quote:
Originally Posted by bkelly2
They all need it Bob, it turns out that many of the appliances you plug in, in the kitchen have something to do with liquid.
Hi all,

it's simpler than that, if the outlet services a horizontal surface in or adjacent to the kitchen it needs to be GFCI.

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Emergency Lighting (commercial) mcyr Electrical Inspections 24 6/10/06 10:06 AM


All times are GMT -4. The time now is 8:20 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts