Default Look here for a Water Heater Blast!






Reference Only:

422.47 Water Heater Controls.



All storage or instantaneous-type water heaters shall be equipped with atemperature-limiting means in addition to its control thermostat to disconnect all ungrounded conductors. Such means shall comply with both of the following:

(1) Installed to sense maximum water temperature.

(2) Be either a trip-free, manually reset type or a type having a replacement element. Such water heaters shall be marked to require the installation of a temperature and pressure relief valve.







Exception No. 1: Storage water heaters that are identified
as being suitable for use with supply water temperature of 82°C (180°F) or above and a capacity of 60 kW or above.


Exception No. 2: Instantaneous-type water heaters that are identified as being suitable for such use, with a capacity of 4 L (1 gal) or less.







FPN: See ANSI Z21.22-1999/CSA 4.4-M99,
Relief Valves for Hot Water Supply Systems.


Reply With Quote
  #2  
Old 1/31/06, 11:49 AM
Carla Horne's Avatar
Carla Horne Carla Horne is offline
InterNACHI Member
 
Join Date: Feb 2003
Location: Meredith, NH
Posts: 531
Default Re: Look here for a Water Heater Blast!

Joe,
thanks for sharing that, OMG!

Carla
Reply With Quote
  #3  
Old 1/31/06, 12:50 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Look here for a Water Heater Blast!

It's probably not a bad idea to flip the pop off valve open every once in a while to be sure it isn't corroded shut. Just be aware it may stick open when you do.
My water heater is outside so that is not that big a deal. I bet you folks up in the frozen north don't have that option.
Reply With Quote
  #4  
Old 1/31/06, 10:52 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,717
Default Re: Look here for a Water Heater Blast!

" Such water heaters shall be marked to require the installation of a temperature and pressure relief valve."

Marked by whom. Code inspectors?

We are not code inspectors.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #5  
Old 2/1/06, 12:54 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Look here for a Water Heater Blast!

http://www.wbdg.org/ccb/HUD/HUDSPEC/h15451.pdf


2.3 ELECTRIC RESIDENTIAL WATER HEATERS


A. Water Heaters: UL 174, energy-efficient, fully automatic.
1. Water Heaters: Type(s) and size(s) indicated, specified, or scheduled with necessary accessories
for complete installation ready for operation.
2. Tapping for Hot and Cold Water: 20 mm (3/4 inch) NPT minimum.
3. Thermostats: Interlocked so that only one heating element may be operative at any one time.
4. When required to meet warranty requirements, provide anodic rod.
5. Safety Pressure and Temperature Control Valves: ANSI Z21.22.
6. Heaters: 230 volt, 60 cycle current.
7. Heaters: NEC (ANSI/NFPA 70) for hard wire connections to service wiring.
8. Water Heaters: Bear UL label.
9. Water Heaters: Certification by accredited independent testing laboratory that water heater is
properly labeled and is in compliance with ASHRAE/IES 90.1 and 90.1b when tested in accordance with
DOE test procedures in 10 CFR, Part 430.

Reply With Quote
  #6  
Old 2/1/06, 1:41 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Look here for a Water Heater Blast!

Will you may not be a code inspector but you are a safety inspector in the sense that you should be pointing out safety related defects. Joe is pointing out that the water heater was marked to say it requires a relief valve. In fact it will be sold with one built in. For the home inspector, you should look to see if it is still there and that nobody screwed a pipe plug in the outlet because it was leaking. I think it is opening yourself up to some liability if you operate it, since it might start leaking after that ... assuming the homeowner never tests it. Trick the homeowner into doing it
Reply With Quote
  #7  
Old 2/1/06, 1:53 AM
Brian E. Kelly's Avatar
Brian E. Kelly Brian E. Kelly is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Phoenix, AZ
Posts: 15,862
Default Re: Look here for a Water Heater Blast!

This guy says test them

http://askfoxroach.katabat.com/page....k=3.27.231.386


Barry says no. I would never test one for a client, nor have I ever tested one at my house. I also have not tested the airbags in my car.


Quote:
Dear Barry,
I have some questions regarding the temperature pressure relief (TPR) valve on my water heater. How can I tell if it has been activated? Does it reset by itself? Can I reset it manually? And should it be tested? -- Buzz

Dear Buzz,
TPR valves are installed on water heaters to prevent the tanks from exploding if the fixture should overheat. The valve is held in the closed position by means of a spring. When the pressure or temperature in the tank causes the valve to open, hot water is released from the system. If the valve is working properly, it will reseal by itself when the temperature or pressure returns to normal. Most TPR valves, however, never fully reseal because of corrosion or mineral deposits. That is when the valve needs to be replaced. Testing of TPR valves is not recommended because they often tend to leak after having been tested.
To write to Barry Stone, please visit him on the Web at www.housedetective.com.
Reply With Quote
  #8  
Old 2/1/06, 2:07 AM
JLilly's Avatar
JLilly JLilly is offline
InterNACHI Member
 
Join Date: Jan 2006
Location: Parkersburg, WV
Posts: 232
Default Re: Look here for a Water Heater Blast!

They are few and far between that don't leak after you test them. Especially on a hot water boiler.
Reply With Quote
  #9  
Old 2/1/06, 3:04 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Look here for a Water Heater Blast!

Quote:
Originally Posted by JLilly
They are few and far between that don't leak after you test them. Especially on a hot water boiler.
It really depends on your water quality and how often you test. I used the pop off like a hot water faucet to fill mop buckets and such in Md, never having a problem but they had better water than I do here. I still try to check mine every now and then here. I did have had to replace it once because it dripped afterward.
Reply With Quote
  #10  
Old 2/1/06, 11:11 AM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Look here for a Water Heater Blast!

In some localities it was and or still is permissable to direct the piping from the TPT upwards into the attic or roof before exiting the dwelling. This is usually done in older residences that originally had no TPT line installed to the outside and later had new heaters installed in utility rooms with no outside walls.
There is supposed to be a drain valve located in these lines right at the low point. This valve should be periodically opened to check if the TPT is leaking. Also, if you should open the TPT and fail to drain the line afterwords, water will sit on the pressure spring of the TPT and corrode it to the point where it fails. I would say it is risky business to open any valve on a water heater except for the drain valve on the TPT line. If you ever plan to open the tank drain for any reason other than tank replacement, be prepared with a threaded hose cap and washer since it will probably drip afterwords.
Reply With Quote
  #11  
Old 2/6/06, 4:32 PM
Jeffrey S. Campbell's Avatar
Jeffrey S. Campbell Jeffrey S. Campbell is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Pittston, ME
Posts: 835
Send a message via AIM to jcampbell Send a message via MSN to jcampbell Send a message via Yahoo to jcampbell
Question Re: Look here for a Water Heater Blast!

this info is from a boiler plate item on the INspectVue software... I was hoping for some more detailed requirements. 9/10 of the electrical hot water heaters have standard romex wiring... nothing armored.

thanks in advance.

Substandard wiring was found for the water heater's power supply. This is both a fire and a shock hazard. Recommend having a qualified, licensed electrician evaluate and make repairs as necessary. Typically, electric water heater power supply wires require flexible, armored "BX" conduit, bushing(s) and possibly a covered junction box.
Reply With Quote
  #12  
Old 2/6/06, 4:39 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Look here for a Water Heater Blast!

Thanks, and I will ad that the supply to a water heater often was required to be not less than 105 degrees C, so that the insulation would be able to withstand temperatures.

Sometimes a "whip" will be used from a J-Box with that higher rated wire.
Reply With Quote
  #13  
Old 2/6/06, 4:51 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Look here for a Water Heater Blast!

Why would you need 105c wire in a water heater. The heater usually trips the top thermostat overload when it gets much over 140f/60c
I looked at mine and there is no labelling to indicate this.

I know you usually need 105c on range and oven whips. That is why they are usually factory installed.
Reply With Quote
  #14  
Old 2/6/06, 5:02 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Look here for a Water Heater Blast!

Quote:
Originally Posted by Greg Fretwell
Why would you need C wire in a water heater. The heater usually trips the top thermostat overload when it gets much over 140f/60c
I looked at mine and there is no labelling to indicate this.

I know you usually need 105c on range and oven whips. That is why they are usually factory installed.
Greg:

I remember long ago 1969 when I was an Assistant Electrical Inspector in New Haven, Connecticut where I saw the label at the splice compartment calling for 105 degrees C wire:

I thought that we could look at the history of UL
UL milestones in product safety certification and UL’s contribution to advancement of new technologies

Click on the appropriate time period below for more information.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Client wants a new water heater adirienzo General Inspection Discussion 47 7/14/10 3:03 PM
Venting an oil-fired water heater mh718 Inspecting HVAC Systems 3 11/16/06 10:36 AM