Default Looking at this panel

A home I inspected yesterday had a subpanel for the pool. The main service panel is outside at the meter. Wires into the main distribution panel from the "pool panel" are black, white, red, and green. Can I assume the green is the ground? and if so, it should not be on the neutral bass. Right?
Attached Thumbnails
looking-panel-p1050732.jpg   looking-panel-p1050737.jpg  
Reply With Quote
Find an InterNACHI certified Washington Home Inspector (and anywhere else in North America)
  #2  
Old 11/12/09, 2:44 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 544
Send a message via Skype™ to gwells
Default Re: Looking at this panel

Quote:
Originally Posted by acox View Post
A home I inspected yesterday had a subpanel for the pool. The main service panel is outside at the meter. Wires into the main distribution panel from the "pool panel" are black, white, red, and green. Can I assume the green is the ground? and if so, it should not be on the neutral bass. Right?
The main concern with ground connections is not to have parallel ground paths. When inspecting these types of installations, look to see if there are parallel ground paths. If not, the grounding (normally non-current carrying) conductor and the grounded (current carrying) conductor need to be tied together. On the other hand, if connecting them together would create a parallel ground path, they need to be separated from one another.

It looks as though the feeder is service entrance cable inside plastic conduit. If this is the case, then that part of the installation is OK. The grounding conductors and the system grounded conductor should be connected together. The ground bars should also be connected together and bonded to the panel. Generally, there should also be a made electrode (ground rod, etc). However, an inspector may waive the requirement for an additional made electrode if the sub-panel is close to the service.

There are situations in which following the NEC to the letter, can result in an unsafe installation. One such situation is where there is a remote panel that might otherwise require a separate made electrode but that made electrode would be in close proximity to the ground from the main system. Even though they are not mechanically connected, electrolytes in the soil can create a ground path parallel to the feeder. In that situation, it is preferable to move the made electrode to the main service. Strictly speaking, that could result in a violation of the NEC.

In the legal system, a phrase that is used often is, "in the spirit of the law". I once got a traffic ticket for going too far into a lane of traffic so I could see beyond a 15' snow pile in an adjacent parking lot. When I went to court, the judge reprimanded the cop for issuing a citation that was "contrary to the spirit of the law" and he reprimanded the prosecutor for wasting the court's time for the same reason. In other words, what I did was the safest thing to do under the circumstances and any reasonable person should have been able to see that. The cop and the prosecutor went by the letter of the law.

The key is to know the underlying reasons for code requirements. That is, the spirit of the requirement. Once you have a clear understanding of why the rules are what they are, it is easier to look at an electrical installation and make a good call. In the case of grounding, just remember that the ultimate goal is not to have parallel ground paths.

Discolored?

Is the white grounded conductor's insulation discolored? I cannot tell from the photo if it is discolored or there is oxide inhibitor on the wire.



Licensed Electrical Contractor
Master Electrician
BS Electrical Engineering
Certified Master Inspector

B
estInspectors.Net

License Prep and Continuing Education
Home and Commercial Building Inspection - Electrical
Plumbing - HVAC- Hydronics - Refrigeration - Fire Alarm
Fire and Explosion Investigation - Commercial Sign
Installation - Real Estate (Agent and Broker) - Appraisal

Inspection Report Software for
Windows - iOS - Mac - Android - Linux



est. 1992

Last edited by gwells; 11/12/09 at 3:00 PM..
Reply With Quote
  #3  
Old 11/12/09, 2:57 PM
acox acox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,047
Please Note: acox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Looking at this panel

The wire was slightly discolored. Thanks for the help.
Reply With Quote
  #4  
Old 11/12/09, 3:02 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 544
Send a message via Skype™ to gwells
Default Re: Looking at this panel

Quote:
Originally Posted by acox View Post
The wire was slightly discolored. Thanks for the help.
The connection must be loose (or was loose).



Licensed Electrical Contractor
Master Electrician
BS Electrical Engineering
Certified Master Inspector

B
estInspectors.Net

License Prep and Continuing Education
Home and Commercial Building Inspection - Electrical
Plumbing - HVAC- Hydronics - Refrigeration - Fire Alarm
Fire and Explosion Investigation - Commercial Sign
Installation - Real Estate (Agent and Broker) - Appraisal

Inspection Report Software for
Windows - iOS - Mac - Android - Linux



est. 1992

Last edited by gwells; 11/12/09 at 3:21 PM..
Reply With Quote
  #5  
Old 11/12/09, 3:05 PM
acox acox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,047
Please Note: acox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Looking at this panel

They are tight, but who knows - was put in in 1999.
Reply With Quote
  #6  
Old 11/12/09, 5:12 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Looking at this panel

The circuit for the pool equipment is not grounded properly. You've essentially got two hots (ungrounded conductors), two neutrals (grounded conductors) and no equipment ground.

The neutral terminal at a distribution (sub) panel cannot be used to ground circuits/panels that are downstream (load side) of that panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 11/12/09, 5:21 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 746
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Looking at this panel

Having the grounding conductor on the wrong buss is not the only problem shown in that panel. There are multiple cables in knockouts without the proper clamps.
Reply With Quote
  #8  
Old 11/12/09, 7:27 PM
Chuck Lambert Chuck Lambert is offline
Unmoderated Guest
 
Join Date: Jan 2008
Location: Southern California
Posts: 228
Please Note: Chuck Lambert is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Looking at this panel

Quote:
Originally Posted by acox View Post
Can I assume the green is the ground?
You can but you may not be correct. Are you sure the green is the ground? There are other possiblities. The only way to know for sure is to back trace the green wire. Maybe the electrician only had green wire when he ran it? Maybe he did not correct the colored coding within the panel when he wired it. Maybe it is the ground, if it is, it is wrong.

State in your report that the wiring appears to be incorrect with a possible grounding conductor attached to a neutral buss bar within a "sub" panel. Have the system further evaluated by the appropriate specialist.

Chuck
Reply With Quote
  #9  
Old 11/13/09, 5:32 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 544
Send a message via Skype™ to gwells
Default Re: Looking at this panel

Quote:
Originally Posted by jpope View Post
The circuit for the pool equipment is not grounded properly. You've essentially got two hots (ungrounded conductors), two neutrals (grounded conductors) and no equipment ground.

The neutral terminal at a distribution (sub) panel cannot be used to ground circuits/panels that are downstream (load side) of that panel.
Andrew, I hope I did not confuse you with my comments. when I read your original question, I thought you had a separate structure such as a pool house. In looking at the other responses and rereading your original message, I realize that the sub-panel is on the main house. That being the case, I agree with the others who answered your question. We do not have many pools here in Michigan but houses that have pools often have pool houses that are detached from the main house but are very close to the main house. I apologize if I caused any confusion.



Licensed Electrical Contractor
Master Electrician
BS Electrical Engineering
Certified Master Inspector

B
estInspectors.Net

License Prep and Continuing Education
Home and Commercial Building Inspection - Electrical
Plumbing - HVAC- Hydronics - Refrigeration - Fire Alarm
Fire and Explosion Investigation - Commercial Sign
Installation - Real Estate (Agent and Broker) - Appraisal

Inspection Report Software for
Windows - iOS - Mac - Android - Linux



est. 1992
Reply With Quote
  #10  
Old 11/17/09, 11:05 AM
acox acox is offline
InterNACHI Member
 
Join Date: May 2006
Location: Kissimmee, FL
Posts: 1,047
Please Note: acox is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Looking at this panel

No confusion, and yes, I reported the other issues - using basic language, and then recommended an electrician evaluate and repair the issues.
As always, I appreciate the help I get here.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 8:28 PM
Electrical for Dummies mcyr Electrical Inspections 16 6/9/08 10:59 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 7:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts