Default Looking For A Reference

Can anyone tell me, is there a requirement that interior and exterior circuits be separate?

The three garage receptacles and three exterior receptacles were protected by an upstream GFCI receptacle located in the hallway of the home.

This was a warranty inspection on a home built under the 1999 NEC guidelines.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #2  
Old 2/1/06, 4:38 PM
lfranklin lfranklin is offline
New User
 
Join Date: Jan 2003
Location: Kodak, TN
Posts: 31
Please Note: lfranklin is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Looking For A Reference

No requirment that I know of
Reply With Quote
  #3  
Old 2/1/06, 5:58 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: Looking For A Reference

Quote:
Originally Posted by lfranklin
No requirment that I know of
Ditto.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #5  
Old 2/1/06, 6:05 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Looking For A Reference

Quittro



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #6  
Old 2/1/06, 6:18 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,447
Default Re: Looking For A Reference

Heck, I don't know.



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #7  
Old 2/1/06, 6:27 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Looking For A Reference

Jeff,

They are all correct.

The common practice is to hit a receptacle at the main panel and place the GFCI recept. at that location and then loop to the exterior receptacles as well.

Now we do not see this done very much in the manner you stated by a hall receptacle....because in most cases the outside recepts and garage recepts are done in 12-2 ( 20A ) and in many cases the interior wiring lets say in the hall would be 14-2 ( 15A)....not to say it all cant be done in 12-2..but I think you get the point.

The thing I see alot on homes in the mid 90's is the GFCI understanding when it came to bathrooms.....It used to be a thing to hit the bathroom recepts with GFCI and then hit all the outside recepts also....but then the 1999 NEC took care of that.......with the bathroom requirements and it expanded from that.

But their is nothing that prohibits the exterior recepts from being on a circuit with the interior circuits....keeping in mind as you stated the outside ones are protected by GFCI either 15A or 20A......can be either.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #8  
Old 2/1/06, 8:16 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Looking For A Reference

I've never seen it done this way before so I had to ask. It was the only interior receptacle on the circuit, all protected by a 20 amp OCPD at the distribution panel.

Thanks for the confirmation.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #9  
Old 2/2/06, 12:27 AM
Timothy A. Pope's Avatar
Timothy A. Pope Timothy A. Pope is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Cedar Park, TX
Posts: 34
Default Re: Looking For A Reference

Quote:
Originally Posted by pabernathy

The thing I see alot on homes in the mid 90's is the GFCI understanding when it came to bathrooms.....It used to be a thing to hit the bathroom recepts with GFCI and then hit all the outside recepts also....but then the 1999 NEC took care of that.......with the bathroom requirements and it expanded from that.
So, can bathroom and exterior GFCI be on the same circuit?



Timothy Pope
TREC License #7494
www.craftsmaninspections.com
Reply With Quote
  #10  
Old 2/2/06, 12:40 AM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,269
Default Re: Looking For A Reference

Quote:
Originally Posted by tpope
So, can bathroom and exterior GFCI be on the same circuit?
Yes.

I have not found anything to suggest otherwise to date.



Joseph P. Hagarty, CMI
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
  #11  
Old 2/2/06, 2:22 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Looking For A Reference

The bathroom receptacles can have no other outlets, same with the kitchen. That leaves the basement and/or garage GFCI(s). Either could go outside.The advantage is that your GFCI device is not out in the weather.
Reply With Quote
  #12  
Old 2/2/06, 9:40 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Looking For A Reference

NO....they cant be on the same circuit...in regards to bathroom recepts and other receptacles.....



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #13  
Old 2/2/06, 9:46 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Looking For A Reference

NEC states in Art 210.11(C)(3)- Bathroom Branch Circuits- In addition to the number of branch circuitd required by parts of this section, at least one 20-ampere branch circuit SHALL BE provided to supply the bathroom receptacle outlet(s). Such circuit SHALL have no other outlets.

Exception: Where the 20-ampere circuit supplies a single bathroom, outlets from other equipment within the same bathroom SHALL BE permitted to be supplied in accordance with 210.23(A)



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #14  
Old 2/2/06, 10:33 AM
Timothy A. Pope's Avatar
Timothy A. Pope Timothy A. Pope is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Cedar Park, TX
Posts: 34
Default Re: Looking For A Reference

Quote:
Originally Posted by pabernathy
NO....they cant be on the same circuit...in regards to bathroom recepts and other receptacles.....
Thanks guys. Glad I asked.



Timothy Pope
TREC License #7494
www.craftsmaninspections.com
Reply With Quote
  #15  
Old 4/23/06, 11:31 AM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Looking For A Reference

The requirements for GFCI protected circuits/receptacles undergoes changes in every code cycle. The code cycles for awhile now have been every three years (this was not always the case). When inspecting for this type of situation, it is important to know which code cycle the installation was performed under. There are a lot of installations (even just a couple of years old) that would not meet todays code, but were compliant when installed.
Remember most codes are not retroactive. If you feel it is a safety hazard, maybe a suggestion to have a qualified licensed electrical contractor to take a look at it.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Need Title 24 (CA) reference for TPR valves jhugenroth Plumbing Inspections 12 8/31/09 3:12 PM
Good Reference Material? fnewman Miscellaneous Discussion for Inspectors 11 8/27/07 12:07 PM
Technical Reference Guide Vs Carrier Blue Book waksell Inspecting HVAC Systems 12 1/22/07 6:45 PM
Reference books question jclark1 Inspecting HVAC Systems 4 3/1/06 5:06 PM
Good Reference for Wood Shake Roof krichardson Exterior Inspections 5 1/17/06 7:59 AM


All times are GMT -4. The time now is 4:25 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts