Default Loose wires in electrical panel

I noticed the two loose wires at the bottom of the electrical panel. I also noticed that the wiring to the water heater was replaced with an orange insulated wire when the replacement water heater was installed in 2003. I'm guessing those two loose wires originally went to the water heater. I'm not clear on what to say about these two loose wires in my report that aren't being used. Any suggestions would be appreciated.

Thanks,

Steve
Attached Thumbnails
loose-wires-electrical-panel-bennetts-123010-232.jpg   loose-wires-electrical-panel-bennetts-123010-227.jpg  



Shore-Footed Property Services, LLC
Stephen P. Shockley

MD Licensed Home Inspector
410-726-3471
Salisbury, Md
Reply With Quote
Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/3/11, 4:57 AM
zswieca zswieca is offline
New User
 
Join Date: Sep 2007
Location: San Antonio, TX
Posts: 95
Please Note: zswieca is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Loose wires in electrical panel

Improperly terminated wires noted at the --- panel. The ends of spliced wires should be covered with a wire nut and electrical tape should be wrapped over the nut and onto the wires. Note, the inspector does not pull or track the source of terminated wires.

Last edited by zswieca; 1/3/11 at 7:15 AM..
Reply With Quote
  #3  
Old 1/3/11, 5:05 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Loose wires in electrical panel

I agree they would be safer if the ends were either taped or a wire nut were installed. This would keep inadvertent contact with the live buss from energizing the other end of the cable or worse causing some arcing which may lead to other problems. According to the NEC abandoned line voltage cables and conductors can remain for possible future use. Abandoned CATV and data/phone wiring must be removed or tagged for future use. No such requirement exist for line voltage cables.

Quote:
ARTICLE 800 Communications Circuits

I. General

800.25 Abandoned Cables.
The accessible portion of abandoned communications cables shall be removed. Where cables are identified for future use with a tag, the tag shall be of sufficient durability to withstand the environment involved
Reply With Quote
  #4  
Old 1/3/11, 6:26 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Loose wires in electrical panel

Quote:
Originally Posted by sshockley View Post
I noticed the two loose wires at the bottom of the electrical panel. I also noticed that the wiring to the water heater was replaced with an orange insulated wire when the replacement water heater was installed in 2003. I'm guessing those two loose wires originally went to the water heater. I'm not clear on what to say about these two loose wires in my report that aren't being used. Any suggestions would be appreciated.

Thanks,

Steve
"Abandoned line voltage cable found in electrical panel. It can be removed or, if left in place, bare copper conductor ends should be covered
by wire nuts or electrical tape. Consult licensed electrician"
Reply With Quote
  #5  
Old 1/3/11, 8:56 PM
Stephen P. Shockley's Avatar
Stephen P. Shockley Stephen P. Shockley is offline
InterNACHI Member
 
Join Date: May 2009
Location: Salisbury, Maryland
Posts: 216
Default Re: Loose wires in electrical panel

Wow, great comments. I was about to only suggest removing the loose wires. Thanks gentlemen.


Regards,

Steve



Shore-Footed Property Services, LLC
Stephen P. Shockley

MD Licensed Home Inspector
410-726-3471
Salisbury, Md
Reply With Quote
  #6  
Old 1/3/11, 8:58 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Loose wires in electrical panel

Quote:
Originally Posted by sshockley View Post
Wow, great comments. I was about to only suggest removing the loose wires. Thanks gentlemen.


Regards,

Steve
Brian summed it up nicely.
Reply With Quote
  #7  
Old 1/4/11, 5:41 PM
Kenneth Greene's Avatar
Kenneth Greene Kenneth Greene is offline
InterNACHI Member
 
Join Date: Mar 2009
Location: Albany NY
Posts: 61
Default Re: Loose wires in electrical panel

it looks like from the photo that the orange wire come through exterior of the house wall then travels up into an exterior mounted breaker panel. shouldn't that cable be protected from cutting in conduit?




Hudson-Mohawk Inspections LLC
Ken Greene
NYS license 16000041691
IAC2 Cert. # IAC2-01-6345
NY State Pest Technician: T5865955

www.hudsonmohawkinspections.com
Reply With Quote
  #8  
Old 1/4/11, 7:36 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Loose wires in electrical panel

Quote:
Originally Posted by kgreene1 View Post
it looks like from the photo that the orange wire come through exterior of the house wall then travels up into an exterior mounted breaker panel. shouldn't that cable be protected from cutting in conduit?
No, the problem is that that type of cable is not listed for use outdoors.

Conduit would only be required if it was deemed that the cable was subject to physical damage.
Reply With Quote
  #9  
Old 1/4/11, 8:32 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Loose wires in electrical panel

Quote:
Originally Posted by Jim Port View Post
No, the problem is that that type of cable is not listed for use outdoors.

Conduit would only be required if it was deemed that the cable was subject to physical damage.
Isn't the orange cable (10ga) ) subject to physical damage?




Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #10  
Old 1/4/11, 8:36 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,090
Default Re: Loose wires in electrical panel

Quote:
Originally Posted by ccurrins View Post
Isn't the orange cable (10ga) ) subject to physical damage?

That misses the point Chris.

The cable is not out door rated. It it was UF there would be no problem.



You can argue with intelligent people but to argue with a mush head is like trying to grab fog-Thomas Sowell

Never underestimate the difficulty of changing false beliefs by facts. - Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI

Reply With Quote
  #11  
Old 1/4/11, 8:45 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Loose wires in electrical panel

Physical damage is a very subjective term and is not defined in the NEC. What you may consider may vary widely from what someone else considers subject to damage.
Reply With Quote
  #12  
Old 1/4/11, 9:07 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Loose wires in electrical panel

Quote:
Originally Posted by Jim Port View Post
Physical damage is a very subjective term and is not defined in the NEC. What you may consider may vary widely from what someone else considers subject to damage.
So, in this installation, other than not being UF, you would not consider it a safety defect?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #13  
Old 1/4/11, 9:13 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Loose wires in electrical panel

Quote:
Originally Posted by ccurrins View Post
So, in this installation, other than not being UF, you would not consider it a safety defect?
UF or NM I would consider an exposed cable installed as in that photo subject to physical damage. Now use UF and properly support it then it might be OK. SE cable is run out of the bottom of a meter pan exposed everywhere around here.
Reply With Quote
Need a home inspection in Arkansas? Check out InterNACHI's listing of Arkansas certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/4/11, 9:17 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Loose wires in electrical panel

Quote:
Originally Posted by Robert Meier View Post
UF or NM I would consider an exposed cable installed as in that photo subject to physical damage. Now use UF and properly support it then it might be OK. SE cable is run out of the bottom of a meter pan exposed everywhere around here.
Thanks. Same here with SE cable in rural areas.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #15  
Old 1/4/11, 9:20 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Loose wires in electrical panel

Quote:
Originally Posted by ccurrins View Post
Thanks. Same here with SE cable in rural areas.

As Jim stated it's not defined by the NEC so subject to physical damage is open to interpretation. I used the SE cable as an example because in many area (including this one) that's an acceptable wiring method in an exposed location. Run it in a driveway and then you would have a problem.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical Inspections 50 6/15/10 7:28 PM
Main panel...recommendation ? dnasser Electrical Inspections 6 11/22/09 9:55 PM
4 ground wires into 1 in main panel psiposs Electrical Inspections 13 5/18/06 1:27 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 8:23 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts