Question Magnetrip panels ?? (aka: Zinsco ????)

I inspected a house built in 1958 today and it had a Magnetrip panel with a 60-amp main breaker. All copper service (supply and branch).

No obvious problems with panel.

I was doing a quick search on the web regarding same and the Inspect-NY site seems to link it to being a Zinsco panel ... with another name.

Any input?
Reply With Quote
  #2  
Old 3/24/07, 11:03 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Magnetrip panels ?? (aka: Zinsco ????)

Yep.....here is an image for you...look familiar....note the name on the side of it...




Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #3  
Old 3/24/07, 11:12 PM
nkienitz's Avatar
nkienitz nkienitz is offline
New User
 
Join Date: Feb 2006
Location: Plano, TX
Posts: 72
Please Note: nkienitz is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Magnetrip panels ?? (aka: Zinsco ????)

Paul,

Tnx here and at TIJ as well.

Input most appreciated.
Reply With Quote
  #4  
Old 3/24/07, 11:14 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Magnetrip panels ?? (aka: Zinsco ????)

No problem my brother...thats what I am here for...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 3/24/07, 11:44 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Magnetrip panels ?? (aka: Zinsco ????)

Zinsco patented the name "Magnatrip" as a reference to the "technology" used to open the circuit breaker. This was during the transition years from fuses to breakers.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 3/25/07, 6:08 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Magnetrip panels ?? (aka: Zinsco ????)

And there you have it....From Mr.Zinsco Pope himself....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Zinsco Magnetrip Panel jhagarty Electrical 6 6/27/07 9:00 PM
Distribution panels bking Electrical 2 3/11/07 11:29 AM
Electric Radiant Ceiling Panels bbernier Canadian Inspectors 4 2/15/07 2:22 PM
FPE Panel - Do you open them up? menser Electrical 11 2/7/06 7:31 PM
Old electrical panels? ysoltis Electrical 0 1/13/06 12:38 PM


All times are GMT -4. The time now is 12:00 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts