I am wondering if I missed something here?

The meter is on the outside of the home, no disconnect noted, inside the basement is the panel directly below the outside meter with main coming through the siding right to the panel. No main breaker in the panel.

Does this seem accurate?
Attached Thumbnails
main-breaker-img_9031.jpg   main-breaker-img_91215.jpg   main-breaker-img_91255.jpg  



Scott Falvey
Clear View Home Inspections, LLC
Newbury, NH
NACHI#05051292
www.clearviewhomeinspectionsllc.com
Reply With Quote
  #2  
Old 1/25/08, 11:31 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,542
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Breaker

If all you have is six throws, then you do not need a main breaker. It looks like you have six in that picture.

If I am looking at that correctly, the ground wires are all bunched up under one lug. That is a no-no.

The wires leaving the box are not protected from physical damage.

Looks like yo have plenty to write up.
Reply With Quote
  #3  
Old 1/25/08, 11:32 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Breaker

There is only one way that would be compliant: If there were six two-pole breakers in that main lug panel.
Obviously that is not the case.

Just one look at the workmanship/mess should cause you to defer to an qualifed electrician.
Reply With Quote
  #4  
Old 1/25/08, 11:35 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Breaker

Huston we have a problem.

That panel has more than 10% of its overcurrent devices protected at 30 amps or less that also has a grounded (neutral) so no matter if there is no more than six disconnects or not it is required to have no fewer than two mains.

I would write this up as a cluster sex orgy and needs attention.
Reply With Quote
  #5  
Old 1/25/08, 11:41 PM
rwand1 rwand1 is offline
Active Poster
 
Join Date: Sep 2005
Location: Caledon, ON
Posts: 7,861
Please Note: rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Breaker

Is a cluster sex orgy an electrical term?
Reply With Quote
  #6  
Old 1/26/08, 1:41 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Breaker

Looks like the SE cable is missing a sill plate and may be of questionable condition. If this cable in in a driveway it would require protection from physical damage.I cannot see the pictures clearly here on my palm and I am in the airport waiting for a flight home.
Reply With Quote
  #7  
Old 1/26/08, 1:52 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Breaker

Quote:
Originally Posted by jtedesco1
Looks like the SE cable is missing a sill plate...
A bigger screen shows that the sill plate does exist in that installation.

I am aware that sill plates for SE cable are manufactured, but I am unaware of any specific NEC, UL, or manufacturer requirement that they are to be used. They sure make for a more "finished" appearance often times, and may provide some mechanical benefit. That said, in areas where load side SE cable accepted, I'm not sure what would compel me to use a sill plate, save for the fact that they exist and it "seems" like the thing to do. I am well aware that cable that is exposed to physical damage requires protection, but I'd be hard pressed to say that the last 4" of SE cable before it goes through the wall is any more subject to physical damage than the other 4 feet up to the meter socket.
Reply With Quote
  #8  
Old 1/26/08, 2:01 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Breaker

MarcPlease look at 230.50 for the protection rule. In MA we have an amendment calling for protection because a kid used a hacksaw once to cut the cable for scrap. Got to go now plane ready to depart.
Reply With Quote
  #9  
Old 1/26/08, 9:07 AM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,047
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Main Breaker

Ok.....

The SE Cables sheath does not extend into the enclosure, Also it is clear to see that a main breaker is needed....while it is entirely possible for the 6 disconnect rule to apply with this enclosure...it does not in this shown setup and would indeed require the main.
Also it appears the majority of cables are not supported properly......simply defer for evaluation from an electrical contractor.



Paul W. Abernathy,CMI,CPI,CME
National Electrical Code Expert
Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA
Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru
Weekly Chat on Wednesdays -7:30 PM E.S.T
* Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections"

2007 InterNACHI Member of the Year
Reply With Quote
  #10  
Old 1/26/08, 9:12 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,490
Default Re: Main Breaker

Quote:
Originally Posted by pabernathy
Ok.....

The SE Cables sheath does not extend into the enclosure, Also it is clear to see that a main breaker is needed....while it is entirely possible for the 6 disconnect rule to apply with this enclosure...it does not in this shown setup and would indeed require the main.
Also it appears the majority of cables are not supported properly......simply defer for evaluation from an electrical contractor.
Where it is evident that a main is necessary...we would defer for repair or replacement, and additional evaluation by a qualified electrical contractor. A qualified electrical contractor who, in this case, would argue against the need for a main would be in error. Correct? Especially considering the possibility that it was a qualified electrical contractor who installed this service panel to begin with.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
  #11  
Old 1/26/08, 9:28 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Breaker

Quote:
Originally Posted by jbushart
Where it is evident that a main is necessary...we would defer for repair or replacement, and additional evaluation by a qualified electrical contractor. A qualified electrical contractor who, in this case, would argue against the need for a main would be in error. Correct? Especially considering the possibility that it was a qualified electrical contractor who installed this service panel to begin with.
YES! I counted 11 overcurrent protective devices in this panelboard. I also see where the existing cables appear to be without an equipment grounding conductor since they are the old 2 wire types, and if they did have the EGC may have been the earlier types with one size smaller. The gas pipe, although there for many years would present a question in an installation today, because the space above that equipment is restricted to electrical materials, etc.

Last edited by jtedesco1; 3/6/08 at 10:09 AM..
Reply With Quote
  #12  
Old 1/26/08, 9:44 AM
Mario A. Kyriacou, CHI's Avatar
Mario A. Kyriacou, CHI Mario A. Kyriacou, CHI is offline
ESOP Committee Member
 
Join Date: Jun 2006
Location: Toronto, Ontario, Canada
Posts: 5,856
Default Re: Main Breaker

Electrical geniuses,

Is the double tap on the right side of the panel of no concern?





'Imagination is more important than knowledge' (sometimes)
Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007

www.360degreeshomeinspections.com
Tel.# 416-722-6132
e-mail torontohomeinspector@yahoo.com
Reply With Quote
  #13  
Old 1/26/08, 9:54 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Breaker

Quote:
Originally Posted by mkyriacou
Electrical geniuses,

Is the double tap on the right side of the panel of no concern?
I ain't no genius, but I would write that it up too!

Last edited by jtedesco1; 3/6/08 at 10:09 AM..
Reply With Quote
  #14  
Old 1/26/08, 10:16 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Breaker

Quote:
Originally Posted by jbushart
Where it is evident that a main is necessary...we would defer for repair or replacement, and additional evaluation by a qualified electrical contractor. A qualified electrical contractor who, in this case, would argue against the need for a main would be in error. Correct? Especially considering the possibility that it was a qualified electrical contractor who installed this service panel to begin with.


Any panel including one that has only six single pole breakers that has more than 10% of its breakers 30 amps or less and also utilizes the grounded (neutral) conductor is required to have a main. This is covered in 408.36 of the NEC and has been in place for many years.

Never jump to the conclusion that just because it is present that a “qualified” electrician made the installation. Not all electricians are qualified and some should be run out of town.
Reply With Quote
  #15  
Old 1/26/08, 10:24 AM
James H. Bushart's Avatar
James H. Bushart James H. Bushart is offline
InterNACHI Member
 
Join Date: Dec 2004
Location: Southwest Missouri
Posts: 20,490
Default Re: Main Breaker

Quote:
Originally Posted by Mike Whitt
Never jump to the conclusion that just because it is present that a “qualified” electrician made the installation. Not all electricians are qualified and some should be run out of town.
Mike,

You are the one who is jumping to conclusions.

Re-read my post.



James H. Bushart

Professional Building Analyst, BPI
Missouri, Kansas and Arkansas
314-803-2167
Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas.

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
main Breaker vriverajr Electrical Inspections 5 1/2/08 11:52 AM
Arching Causes Main Breaker To Trip? msylvester Electrical Inspections 10 10/22/07 4:57 PM
oversized main breaker bandrews Electrical Inspections 3 4/16/07 11:48 AM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 3:52 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts