I am wondering if I missed something here?
The meter is on the outside of the home, no disconnect noted, inside the basement is the panel directly below the outside meter with main coming through the siding right to the panel. No main breaker in the panel. Does this seem accurate? Scott Falvey Clear View Home Inspections, LLC Newbury, NH NACHI#05051292 www.clearviewhomeinspectionsllc.com |
|
#2
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
If all you have is six throws, then you do not need a main breaker. It looks like you have six in that picture.
If I am looking at that correctly, the ground wires are all bunched up under one lug. That is a no-no. The wires leaving the box are not protected from physical damage. Looks like yo have plenty to write up. |
|
#3
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
There is only one way that would be compliant: If there were six two-pole breakers in that main lug panel.
Obviously that is not the case. Just one look at the workmanship/mess should cause you to defer to an qualifed electrician. |
|
#4
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Huston we have a problem.
That panel has more than 10% of its overcurrent devices protected at 30 amps or less that also has a grounded (neutral) so no matter if there is no more than six disconnects or not it is required to have no fewer than two mains. I would write this up as a cluster sex orgy and needs attention. |
|
#5
|
|||
|
|||
|
Please Note:
rwand1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Is a cluster sex orgy an electrical term?
|
|
#6
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Looks like the SE cable is missing a sill plate and may be of questionable condition. If this cable in in a driveway it would require protection from physical damage.I cannot see the pictures clearly here on my palm and I am in the airport waiting for a flight home.
|
|
#7
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I am aware that sill plates for SE cable are manufactured, but I am unaware of any specific NEC, UL, or manufacturer requirement that they are to be used. They sure make for a more "finished" appearance often times, and may provide some mechanical benefit. That said, in areas where load side SE cable accepted, I'm not sure what would compel me to use a sill plate, save for the fact that they exist and it "seems" like the thing to do. I am well aware that cable that is exposed to physical damage requires protection, but I'd be hard pressed to say that the last 4" of SE cable before it goes through the wall is any more subject to physical damage than the other 4 feet up to the meter socket. |
|
#8
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
MarcPlease look at 230.50 for the protection rule. In MA we have an amendment calling for protection because a kid used a hacksaw once to cut the cable for scrap. Got to go now plane ready to depart.
|
|
#9
|
||||
|
||||
|
Ok.....
The SE Cables sheath does not extend into the enclosure, Also it is clear to see that a main breaker is needed....while it is entirely possible for the 6 disconnect rule to apply with this enclosure...it does not in this shown setup and would indeed require the main. Also it appears the majority of cables are not supported properly......simply defer for evaluation from an electrical contractor. Paul W. Abernathy,CMI,CPI,CME National Electrical Code Expert Electrical & Fire Protection Systems Code Supervisor- Alexandria,VA Weekly Live Radio Show :http://en.1000mikes.com/show/the_electrical_guru Weekly Chat on Wednesdays -7:30 PM E.S.T * Get my 13 hour commentary audio CD for the book "How to Perform Electrical Inspections" 2007 InterNACHI Member of the Year |
|
#10
|
||||
|
||||
|
Quote:
James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas. |
|
#11
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Last edited by jtedesco1; 3/6/08 at 10:09 AM.. |
|
#12
|
||||
|
||||
|
Electrical geniuses,
Is the double tap on the right side of the panel of no concern? 'Imagination is more important than knowledge' (sometimes) Mario Kyriacou CHI CMI-NACHI Canadian Member of the Year 2007 www.360degreeshomeinspections.com Tel.# 416-722-6132 e-mail torontohomeinspector@yahoo.com |
|
#13
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Last edited by jtedesco1; 3/6/08 at 10:09 AM.. |
|
#14
|
||||
|
||||
|
Please Note:
Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Any panel including one that has only six single pole breakers that has more than 10% of its breakers 30 amps or less and also utilizes the grounded (neutral) conductor is required to have a main. This is covered in 408.36 of the NEC and has been in place for many years. Never jump to the conclusion that just because it is present that a “qualified” electrician made the installation. Not all electricians are qualified and some should be run out of town. |
|
#15
|
||||
|
||||
|
Quote:
You are the one who is jumping to conclusions. Re-read my post. James H. Bushart Professional Building Analyst, BPI Missouri, Kansas and Arkansas 314-803-2167 Inspecting in Aurora, Branson, Carthage, Granby, Joplin, Kimberling City, Monett, Mount Vernon, Neosho, Nixa, Purdy, Reed Spring, Republic, Springfield and surrounding areas. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| main Breaker | vriverajr | Electrical Inspections | 5 | 1/2/08 11:52 AM |
| Arching Causes Main Breaker To Trip? | msylvester | Electrical Inspections | 10 | 10/22/07 4:57 PM |
| oversized main breaker | bandrews | Electrical Inspections | 3 | 4/16/07 11:48 AM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 10:26 PM |