  #1  
Old 2/19/09, 1:31 PM
gbaccus gbaccus is offline
InterNACHI Member
 
Join Date: Oct 2008
Posts: 2
Default main breaker panel location

New house construction... customer says he wants main breaker panel located in a small closet in living room. I say he shouldn't. (He contends that it is not an entry closet since it not near the entry nor a clothes closet. The code states that it can not be located in Clothes Closet or Bathroom. I say it should not be located in the closet because it could be used as a coat closet which would be a clothes closet. Doesn't this go back to what the small room was intended for ... thus a coat closet? ?Thanks, Garry
Reply With Quote
  #2  
Old 2/19/09, 1:39 PM
mnahrgang's Avatar
mnahrgang mnahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Springfield, OH
Posts: 5,763
Default Re: main breaker panel location

Regardless of what he is going to use it for, it is a "clothes closet". Recommend he shouldn't. Then go on.

It's his house, and it's between him, his electrician, and the AHJ.

We observe and report. What the client decides to do with the info is his/her business.



Mark Nahrgang
www.DaytonSpringfieldHomeInspector.com
www.HeyMark.info

Home Inspections for Springfield, Dayton, and surrounding OH areas.
Reply With Quote
  #3  
Old 2/19/09, 2:45 PM
gbaccus gbaccus is offline
InterNACHI Member
 
Join Date: Oct 2008
Posts: 2
Default Re: main breaker panel location

Thanks for your thoughts!
Reply With Quote
  #4  
Old 2/19/09, 3:08 PM
Billy Boerner's Avatar
Billy Boerner Billy Boerner is offline
InterNACHI Member
 
Join Date: Jun 2008
Location: St. Louis, MO
Posts: 11,474
Send a message via Yahoo to bboerner
Default Re: main breaker panel location

NEC 230.70 & 240.24 Electrical panels shall be readily accessible and shall not be
located in bathrooms or in the vicinity of easily ignitable materials such as clothes closets.

I would recommend that he's simply wasting good closet space. Put the thing in the garage like most people do.



STL Home Inspection Services LLC
Residential / Radon / Sewer / Thermal / Termite

Bill Boerner
Multi Inspector Firm
(314) 805-2137
office@stlhomeinspector.com
Stlhomeinspector.com
Serving: St. Louis and Surrounding
Reply With Quote
  #5  
Old 2/19/09, 3:15 PM
Jim Port Jim Port is online now
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 1,473
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: main breaker panel location

You said a small closet. It might not be possible to meet the work space requirements in the closet. You need a 30" width, not necessarily centered on the panel and at least a 36" depth. Headroom might also be an issue.

You also said it is not close to the entry. This would mean to me that the service cable would not be as short as practical and would require an exterior disconnect.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Outlet off of Main Panel? jlevy Electrical Inspections 2 8/5/08 5:18 PM
Neutral bus bar failed inspection Greg Moritz Electrical Inspections 18 1/19/08 1:53 PM
Main panel double tap dmccauley Electrical Inspections 20 1/25/07 5:31 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM

All times are GMT -4. The time now is 3:58 PM.
no new posts