Default Main Breaker Size

I could not find the amin breaker. Could someone please tell tell what the size would be from the mains in the pic

Thanks

main-breaker-size-img_0092-small-.jpg.JPG
Views:	65
Size:	44.0 KB
ID:	5658



www.wisemovehomeinspection.com
407- 282 0774
407- 928 8489
Reply With Quote
  #2  
Old 9/20/06, 7:41 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Breaker Size

I can't see any mains. All I see is what looks like a 200 amp stainless steel meter base.

Is that thing actually stainless???
Reply With Quote
  #3  
Old 9/20/06, 8:47 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Main Breaker Size

Carl,

I would NOT guess at it....while it looks the size of a 200A meter can...I would say NOTHING of the sort unless I found the Main Breaker....and their HAS to be one.......either at the POINT of enterance..or atleast a disconnect should be their........SOMETHING......but never by just the meter can size...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #4  
Old 9/20/06, 8:50 PM
Carl Pennick's Avatar
Carl Pennick Carl Pennick is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Orlando, FL
Posts: 898
Default Re: Main Breaker Size

Ok thanks



www.wisemovehomeinspection.com
407- 282 0774
407- 928 8489
Reply With Quote
  #5  
Old 9/20/06, 9:28 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,033
Default Re: Main Breaker Size

Shore is a purdy meter can. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #6  
Old 9/20/06, 9:29 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Main Breaker Size

Yep........they are TOO tight around here to go for the Stainless Ones...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #7  
Old 9/20/06, 10:09 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Breaker Size

They must have SOME acid rain problem!
Reply With Quote
  #8  
Old 9/20/06, 11:08 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Main Breaker Size

There may not be a main breaker. One isn't required if < 6 throws. My state doesn't require me to report on a main breaker presence--it requires me to report the service amperage.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #9  
Old 9/20/06, 11:22 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Main Breaker Size

BUT their HAS to be a PANEL.....and the statement was....and I quote:

"I could not find the amin breaker"

Not that I found the breakers......but could not find a main...

P.S. I know that rule........and regardless.....to be ABLE to properly REPORT my friend on the service amperage...you need all the factors....simply assuming it is under the 6 or less rule is assuming.....not enough to assume that from the statement....that they could not find the main breaker.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #10  
Old 9/20/06, 11:26 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Breaker Size

I bet it is aluminum. That is what they look like before the weather gets to them. When I did my service upgrade FPL gave me a shiny one like that fresh out of a big case of them. It is still fairly shiny but you can't see your face in it anymore.
Reply With Quote
  #11  
Old 9/20/06, 11:28 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Main Breaker Size

yeah...all the ones we have are the grey coated ones.....glad I CAN'T see MY face in em...



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #12  
Old 9/20/06, 11:34 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 3,827
Send a message via Yahoo to jfunderburk
Default Re: Main Breaker Size

Paul, you said there had to be a main breaker, in an earlier post. I think the author of the thread meant that he couldn't find a main panel. But for the sake of the uninformed, I replied as I did (that a main "breaker" is not required). Certainly, a main panel should be located in order to properly perform the inspection.

Once I almost gave up looking and finally located the main panel inside the house behind a piece of furniture, on the wall.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #13  
Old 9/20/06, 11:55 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Main Breaker Size

lol...yeah I found one in a house behind a 250 pound oriental rug they hung on the wall...lol...But I knew that enclosure was their because the meter was on the outside wall......

Yeppers.......but to the question at hand.......Carl would need to post more information......and IF he found the panel at all....regardless of the main breakers and such....OH...on a 6 and less...they are all main breakers ( for the circuits they protect )...thehehehe......if we gotta be technical about it....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #14  
Old 9/20/06, 11:56 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Main Breaker Size

lol...HAS to be...as in their HAS to be something other than JUST a meter can on the wall...lol



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Arching Causes Main Breaker To Trip? msylvester Electrical 10 10/22/07 4:57 PM
A/C Breaker size dnice Electrical 31 9/21/07 3:45 PM
Minimum Size Breaker for Sub Panel rmoewe Electrical 7 5/21/07 7:24 PM
Service wire size to breaker panel sfalvey Electrical 12 10/31/06 5:28 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 4:09 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts