Need some clarification on sub panel breakers and possible undersized wires.
The 200 amp main service supplied a sub panel from a 40 amp breaker using #8 AWG. This # 8 AWG wire was connected to a 100 amp main breaker in the sub panel. Is this a situation where you would report an undersized wire attached to the 100 amp breaker or is it redundant as the 40 amp breaker in the main panel should prevent more the 40 amps running through the #8 AWG wire? If you need clarification please ask. Awaiting your responses. Thanks all. |
| Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
|||
|
|||
|
If it is within the same building then the 100A breaker at the remote distribution panel is simply a disconnect, In fact, it is not actually required but in many cases it is cheaper than a MLO panel so they install it. The conductors and panel are protected by the 40A OCPD at the source.
Paul W. Abernathy |
|
#3
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
There could be a possible problem is if the 100 amp CB is not listed for use with a small #8 conductor.
|
|
#4
|
|||
|
|||
|
Thank you Paul, that is what I thought but needed to be sure. Thanks to you also Robert.
|
|
#5
|
||||
|
||||
|
Quote:
Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#6
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
I'm not one so I cannot answer that. But given all that I've read on this forum about HI's doing IR scans I would think that the use of the proper termination that matches the conductor size is somewhat important.
|
|
#7
|
||||
|
||||
|
Quote:
Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#8
|
||||
|
||||
|
The only thing I can see as being an issue is if the smaller wire is completely on one side of a large lug where a somewhat poor connection is possible.
I would make a note of the condition and check that it looks like a solid connection, but I just don't see it a being a significant issue unless it was poorly installed. JMO & 2-Nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#9
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
So if the 100 amp CB is clearly labeled as suitable for use with #6-#1/0 conductors you don't see a problem with connecting a #8?
|
|
#10
|
||||
|
||||
|
Quote:
I indicated I would make a note of that as an issue. But if there is a solid connection, why would you consider that a significant issue or safety hazard (which for an HI would mean an immediate correction recommendation)? Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#11
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Well there's right and wrong according to the listing of the equipment. I've seen double taps that have been in panels for 20 years without any problems. Should a HI not report those either because they look good or have been there for a long time? Where do you draw the line? |
|
#12
|
||||
|
||||
|
Quote:
Quote:
Thats a difficult call for HI's on some issues. Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
|
#13
|
|||
|
|||
|
Would be a listing violation. Being that I can't see the breaker....I will leave that to the origional poster.
Paul W. Abernathy |
| Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Yup, that was my point it could be. I'm assuming that an HI should note that in his report, yes or no? |
|
#15
|
|||
|
|||
|
Do you have pictures for the panel you inspected?
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| GE Main Panel 2 seperate 50amp breakers | sziedman | Electrical Inspections | 6 | 4/19/11 6:13 AM |
| Zinsco Main and Sub panels | dmcmullen | Electrical Inspections | 3 | 4/13/11 9:17 PM |
| Two Main panels? Pic included | dnasser | Electrical Inspections | 19 | 8/3/08 12:08 PM |
| FPE Panel - Do you open them up? | menser | Electrical Inspections | 11 | 2/7/06 6:31 PM |