  #1  
Old 7/4/11, 12:53 PM
RICHARD R. GREEN RICHARD R. GREEN is offline
InterNACHI Member
 
Join Date: Mar 2011
Posts: 2
Exclamation Main breakers in sub panels

Need some clarification on sub panel breakers and possible undersized wires.

The 200 amp main service supplied a sub panel from a 40 amp breaker using #8 AWG. This # 8 AWG wire was connected to a 100 amp main breaker in the sub panel. Is this a situation where you would report an undersized wire attached to the 100 amp breaker or is it redundant as the 40 amp breaker in the main panel should prevent more the 40 amps running through the #8 AWG wire? If you need clarification please ask.

Awaiting your responses. Thanks all.
Reply With Quote
Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/4/11, 1:30 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Main breakers in sub panels

If it is within the same building then the 100A breaker at the remote distribution panel is simply a disconnect, In fact, it is not actually required but in many cases it is cheaper than a MLO panel so they install it. The conductors and panel are protected by the 40A OCPD at the source.



Paul W. Abernathy
Reply With Quote
  #3  
Old 7/4/11, 8:18 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main breakers in sub panels

There could be a possible problem is if the 100 amp CB is not listed for use with a small #8 conductor.
Reply With Quote
  #4  
Old 7/5/11, 10:26 AM
RICHARD R. GREEN RICHARD R. GREEN is offline
InterNACHI Member
 
Join Date: Mar 2011
Posts: 2
Default Re: Main breakers in sub panels

Thank you Paul, that is what I thought but needed to be sure. Thanks to you also Robert.
Reply With Quote
  #5  
Old 7/5/11, 11:36 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Main breakers in sub panels

Quote:
Originally Posted by Robert Meier View Post
There could be a possible problem is if the 100 amp CB is not listed for use with a small #8 conductor.
Good point ... but how significant that is for an HI is another story ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #6  
Old 7/5/11, 11:44 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main breakers in sub panels

Quote:
Originally Posted by roconnor View Post
Good point ... but how significant that is for an HI is another story ...
I'm not one so I cannot answer that. But given all that I've read on this forum about HI's doing IR scans I would think that the use of the proper termination that matches the conductor size is somewhat important.
Reply With Quote
  #7  
Old 7/5/11, 5:33 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Main breakers in sub panels

Quote:
Originally Posted by Robert Meier View Post
I'm not one so I cannot answer that. But given all that I've read on this forum about HI's doing IR scans I would think that the use of the proper termination that matches the conductor size is somewhat important.
It is.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #8  
Old 7/6/11, 8:32 AM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Main breakers in sub panels

The only thing I can see as being an issue is if the smaller wire is completely on one side of a large lug where a somewhat poor connection is possible.

I would make a note of the condition and check that it looks like a solid connection, but I just don't see it a being a significant issue unless it was poorly installed.

JMO & 2-Nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #9  
Old 7/6/11, 8:52 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main breakers in sub panels

So if the 100 amp CB is clearly labeled as suitable for use with #6-#1/0 conductors you don't see a problem with connecting a #8?
Reply With Quote
  #10  
Old 7/6/11, 10:50 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Main breakers in sub panels

Quote:
Originally Posted by Robert Meier View Post
So if the 100 amp CB is clearly labeled as suitable for use with #6-#1/0 conductors you don't see a problem with connecting a #8?
Things are not always that black or white for home inspectors ... there are different shades of grey.

I indicated I would make a note of that as an issue. But if there is a solid connection, why would you consider that a significant issue or safety hazard (which for an HI would mean an immediate correction recommendation)?



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #11  
Old 7/7/11, 7:01 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main breakers in sub panels

Quote:
Originally Posted by roconnor View Post
Things are not always that black or white for home inspectors ... there are different shades of grey.

I indicated I would make a note of that as an issue. But if there is a solid connection, why would you consider that a significant issue or safety hazard (which for an HI would mean an immediate correction recommendation)?

Well there's right and wrong according to the listing of the equipment. I've seen double taps that have been in panels for 20 years without any problems. Should a HI not report those either because they look good or have been there for a long time? Where do you draw the line?
Reply With Quote
  #12  
Old 7/7/11, 11:39 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Main breakers in sub panels

Quote:
Originally Posted by Robert Meier View Post
Well there's right and wrong according to the listing of the equipment.
Thats the black and white for electricians and AHJ's ... HI's often have to make judgment calls as to how significant an issue is. I agree a small wire on a large breaker is likely an issue with the listing. I just don't agree it's a significant issue if there's a solid connection.

Quote:
Originally Posted by Robert Meier View Post
I've seen double taps that have been in panels for 20 years without any problems. Should a HI not report those either because they look good or have been there for a long time?
How about a smaller wire on a larger breaker with a poor connection (say to one side of the lug) thats been there for 20 years without a problem. I would consider that a significant issue, because loads on circuits can change, and just like double lugs with wire-to-wire contact, there is a potential for a poor connection.

Quote:
Originally Posted by Robert Meier View Post
Where do you draw the line?
Thats a difficult call for HI's on some issues.



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
  #13  
Old 7/11/11, 5:20 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Main breakers in sub panels

Quote:
Originally Posted by Robert Meier View Post
So if the 100 amp CB is clearly labeled as suitable for use with #6-#1/0 conductors you don't see a problem with connecting a #8?
Would be a listing violation. Being that I can't see the breaker....I will leave that to the origional poster.



Paul W. Abernathy
Reply With Quote
Need a home inspection in North Dakota? Check out InterNACHI's listing of North Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/11/11, 5:43 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main breakers in sub panels

Quote:
Originally Posted by pabernathy View Post
Would be a listing violation. Being that I can't see the breaker....I will leave that to the original poster.

Yup, that was my point it could be. I'm assuming that an HI should note that in his report, yes or no?
Reply With Quote
  #15  
Old 7/11/11, 5:55 PM
Chiun D. Ng Chiun D. Ng is offline
InterNACHI Member
 
Join Date: Jun 2011
Location: South Florida
Posts: 131
Default Re: Main breakers in sub panels

Do you have pictures for the panel you inspected?
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
GE Main Panel 2 seperate 50amp breakers sziedman Electrical Inspections 6 4/19/11 6:13 AM
Zinsco Main and Sub panels dmcmullen Electrical Inspections 3 4/13/11 9:17 PM
Two Main panels? Pic included dnasser Electrical Inspections 19 8/3/08 12:08 PM
FPE Panel - Do you open them up? menser Electrical Inspections 11 2/7/06 6:31 PM


All times are GMT -4. The time now is 7:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts