Default Main disconect, Main and subpanel

If I have entrance conductors, meter, main breaker and box rated at 200 amp. and a subpanel(box rated for 100 Amp) (interior lights) in the house es feeded from the main through a dual 80 A breaker with its correspondant wiring shall I report 200 Amps as the amperage service for this house?
Reply With Quote
Find an InterNACHI certified Utah Home Inspector (and anywhere else in North America)
  #2  
Old 5/25/09, 4:10 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,904
Default Re: Main disconect, Main and subpanel

Sounds like it. I don't get the lights being protected with an 80A breaker though.
Reply With Quote
  #3  
Old 5/25/09, 4:51 PM
jmondragon jmondragon is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Clermont, FL
Posts: 20
Please Note: jmondragon is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main disconect, Main and subpanel

The dual 80 A breaker is in the main, feeding from here into the subpanel inside of the house where all branch circuits (20,30 A's) breakers are. In other words, the interior lights subpanel is feeded through a 80A breaker and wires.
Reply With Quote
  #4  
Old 5/25/09, 5:28 PM
Mark Nahrgang's Avatar
Mark Nahrgang Mark Nahrgang is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Saint Peters, MO
Posts: 3,904
Default Re: Main disconect, Main and subpanel

Gotcha... It's still a 200 Amp service (Everything up through the Main). If they wanted to add additional circuits they could by adding an additional 100Amp sub panel. For all practical purposes though it sounds like they are only are utilizing 80 AMPS. For modern usage they will likely need to add additional circuits for such things as: big screen TV's, computers, jacuzzi, etc.
Reply With Quote
  #5  
Old 5/25/09, 5:57 PM
jmondragon jmondragon is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Clermont, FL
Posts: 20
Please Note: jmondragon is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main disconect, Main and subpanel

Thanks Mark for your response.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
underamped subpanel?? wstafford Electrical 12 5/13/09 6:08 PM
Neutral/ground bond in subpanel gkeene Electrical 2 1/23/09 11:14 PM
Subpanel for new addition? Stan Kuter General Inspection Discussion 2 11/13/08 8:24 PM
6 breaker exceeded mhazelwood Electrical 48 3/14/08 2:57 AM
Subpanel wired as main panel. jlybolt Electrical 15 5/23/07 5:10 PM


All times are GMT -4. The time now is 9:42 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts