Default Main Disconnect

I am schueduled to do an inspection on New Years day. I set up a radon monitor this afternoon & took a quick look around the basement & outside. I didnt open the panel yet. I will take pictures & post on Monday.

Question. The inside service has a white sticker that says main disconnect. There is no main in the panel. Is the main located outside below the meter. It is locked & I wont be able to inspect the outside. Home was built in 2004.

As you can see the city inspector signed off on the inspection.

It looks like a homeowner electrical job in the basement as there is a wire hanging from the ceiling. I bet it was done without a permit. Looks like the basement was just partially finished. Stay tuned!!

Oh I hope the utility company isnt going to leave there swimming pool around to long. I did a quick look but what utility is the box? Phone? And what is the cylindercal utility next to the green box?

Thanks
Attached Thumbnails
main-disconnect-89107-broadview-heights-002-small-.jpg.jpg
Views:	68
Size:	26.0 KB
ID:	8035   main-disconnect-89107-broadview-heights-003-small-.jpg.jpg
Views:	90
Size:	41.0 KB
ID:	8036   main-disconnect-89107-broadview-heights-013-small-.jpg.jpg
Views:	83
Size:	31.9 KB
ID:	8037   main-disconnect-89107-broadview-heights-012-small-.jpg.jpg
Views:	75
Size:	95.3 KB
ID:	8038  

Last edited by dmacy; 12/29/06 at 6:28 PM..
Reply With Quote
  #2  
Old 12/29/06, 6:28 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Main Disconnect

See the meter base's bottom door. I'm willing to bet money it's in there.

Remember to ask for the key(to that padlock) from the home owner to check it out.

tom
Reply With Quote
  #3  
Old 12/29/06, 6:32 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: Main Disconnect

Quote:
Originally Posted by dmacy
I did a quick look but what utility is the box? Phone? And what is the cylindercal utility next to the green box?
Plastic box next to the meter is phone.
The white cylider is probably fiber optic.

Last edited by mlarson; 12/29/06 at 6:36 PM..
Reply With Quote
  #4  
Old 12/29/06, 6:40 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Main Disconnect

Dave,

If you are not able to look into the panel on the outside under the meter socket....you may not be able to inspect that portion. However, since it is underground SEC....you can assume that the connection from the disconnect below is tried to the meter socket..even if it is not...chances are it will be sized based on the rating of the enclosure.

Be more concerned about looking at the size of the SEC's as they enter into the panel inside...as for the labeling...many stick stickers on things not knowing...would not worry to much about that.....BUT make sure the conductors coming into the panel inside are sized right based on the panels rating.....compare it to the conductors inside as well....

Do all the things you have come to learn with regards to the inside panel....you are doing a fine job at that.....most excellent !

I also agree with TOM here as well.......ask about a KEY.....someone has to have one....and IF you are not able to inspect that part of the system be sure to disclaim it on your report as to WHY you could not inspect it...and snap a shot of it...( which you already have ) and make reference to the picture in your report.

The key to me will be your observation of the panel inside when you get to remove the panel cover.

AS for the others.....thats the Transformer and the TV Cable connection pod.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #5  
Old 12/29/06, 6:49 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,465
Default Re: Main Disconnect

Quote:
Originally Posted by pabernathy

AS for the others.....thats the Transformer and the TV Cable connection pod.
What is the transformer for? cable??

Does this panel comply with the 6 or less breakers for shutting off. Is not this misleading to the home owner having a white sticker saying main shut off. They may think the top breakers shut off the entire service.

If the main is under lock & key does the NEC have an exception for that?

Sorry about all the questions. I am sure that when I take off the covers I can answer my questions. And of course if I dont know you know where to find me!!

Thanks everyone for your help.

Master Paul

Grass hopper is going to figure this out someday & then I can answer more questions then I ask.
Reply With Quote
  #6  
Old 12/29/06, 6:59 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Disconnect

That partially submerged padmount transformer scares the crap out of me. As a former lineman, I can tell you that the water level is very near the 7600V "elbows" inside. The secondary flag terminals may or may not be presently submerged. This is something that any ordinary citizen should call into the POCO immediately. Somebody may have recently drastically changed the grade, or the padmount was set at the wrong elevation when the development was piped out, and ended up that way by accident. I suspect that this transformer is in a back easement that doesn't get many eyeballs on it.

That cylinder is the catv splicing pedestal.

Your main disconnect is in that lower section below the meter. If there's a utility seal tag on that section, there rightfully shouldn't be. This is the customer's section. Sometimes, the meterman or the lineman will mistakenly seal this section. Feel free to cut a utility seal tag off this section with full immunity. If there's a lock on that section, that's the customer's. A customer will sometimes lock their outdoor main disconnect to prevent tampering or for no good reason at all. It may interest you to know that these underground fed meter cans that have a main disconnect section below have an enclosed "gutter section" inside along the edge to prevent access to the meter line side conductors that pass through the lower section.

That's about all I know about that. Hope that helps.

Last edited by Marc D. Shunk; 12/29/06 at 7:03 PM..
Reply With Quote
  #7  
Old 12/29/06, 6:59 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Disconnect

If you are talking about the big green box in the sinkhole, that is the POCO transformer, for the electricity.
Reply With Quote
  #8  
Old 12/29/06, 7:11 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Main Disconnect

Dave....no those are VERY good questions..........VERY GOOD ones and I am in NO way the master....found that out today.......

No that panel would not comply to a 6 disconnect rule IF that was the only panel.....we can only assume right now the MAIN disconnect is out under the meter socket.....

I would mention that as well about the sticker....however personally I would not get overly concerned on that part......but it really depends on IF you can get into that outside panel.....to take a PEAK at it.


Dave I had a reference for you....BUT can't get it to POST right....so I will leave it off...





I personally do not have a problem with it being locked as long as the KEY is present, chances are people come and screw with their panel so they had to resort to locking it....if the owner of the house has the key I would not have a problem with them locking it. If its POCO's they will TAG it...and it is UP to them......

The moral picture here is that your client may choose to not lock it if it is their choice....that is their choice...not really something I would call a problem...but make them aware that it is the main shut off for the house...if indeed it is...which I hope it is.

If they have children of a certain age...they might have locked it. I know in an area around here the local AHJ's require a lock on the service equipment IF located outside......many have locks built into the panel cover itself in commercial applications.....but again being practicle just make your client aware of it.

On the big BOX...thats the Electrical Transformer...the smaller TUBE is a CATV connection hub.

If you would like a CODE reference...check out SECTION 110.26 as it will say a panel can be locked and considered accessible to qualified persons.





Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 12/29/06 at 7:30 PM..
Reply With Quote
  #9  
Old 12/29/06, 7:27 PM
Thomas H. Dietrich's Avatar
Thomas H. Dietrich Thomas H. Dietrich is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Main Disconnect

Quote:
Originally Posted by pabernathy
I also agree with TOM here as well
I get to now mark this down on my calendar, but then my calender comes down in a few days.

As far as the lock, I've heard the same question asked many time. Relating to some fire or other emergency. If this was a typical installation, the shutoff would be inside the house, inaccessible to the outside. So regardless of where the main disconnect is, emergency crews carry tools to cut locks, or they just yank the meter.

tom
Reply With Quote
  #10  
Old 12/29/06, 7:33 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Main Disconnect

Heck yeah....and they YANK EM very quickly....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #11  
Old 12/29/06, 7:52 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: Main Disconnect

Aren't the keys tucked into the panel just below the breakers in picture #2?



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #12  
Old 12/29/06, 7:54 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Main Disconnect

OMG.........man Larry you have some GOOD eyes.....yes those DO look like keys........great VIEW larry....



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
  #13  
Old 12/29/06, 7:59 PM
David C. Macy's Avatar
David C. Macy David C. Macy is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Broadview Hts., OH
Posts: 1,465
Default Re: Main Disconnect

Quote:
Originally Posted by lkage
Aren't the keys tucked into the panel just below the breakers in picture #2?
Damm

Now I need to inspect the outside.

Excellent Eyes!! I bet you find things that some may overlook!!
Reply With Quote
  #14  
Old 12/29/06, 8:00 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Disconnect

Quote:
Originally Posted by Marc D. Shunk
That partially submerged padmount transformer scares the crap out of me. As a former lineman, I can tell you that the water level is very near the 7600V "elbows" inside. The secondary flag terminals may or may not be presently submerged. This is something that any ordinary citizen should call into the POCO immediately. Somebody may have recently drastically changed the grade, or the padmount was set at the wrong elevation when the development was piped out, and ended up that way by accident. I suspect that this transformer is in a back easement that doesn't get many eyeballs on it.

That cylinder is the catv splicing pedestal.

Your main disconnect is in that lower section below the meter. If there's a utility seal tag on that section, there rightfully shouldn't be. This is the customer's section. Sometimes, the meterman or the lineman will mistakenly seal this section. Feel free to cut a utility seal tag off this section with full immunity. If there's a lock on that section, that's the customer's. A customer will sometimes lock their outdoor main disconnect to prevent tampering or for no good reason at all. It may interest you to know that these underground fed meter cans that have a main disconnect section below have an enclosed "gutter section" inside along the edge to prevent access to the meter line side conductors that pass through the lower section.

That's about all I know about that. Hope that helps.
Welcome Marc: Your input will be a breath of fresh air here!
Reply With Quote
  #15  
Old 12/29/06, 8:01 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Main Disconnect

Yep....you have to now check that outside panel Dave...lol......now you know they could not make it too easy for ya.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main disconnect at meter instead of main panel. OK? kshepard Electrical 14 11/8/06 7:24 PM
Tenant access to main disconnect in apartment bldg? lhoffman Electrical 4 9/1/06 12:54 PM
Disconnect and Main panel srowe Electrical 10 6/13/06 8:49 PM
No main disconnect ecox1 Electrical 15 3/7/06 10:59 PM
Main Disconnect Manufactured Home dbreen Electrical 1 3/4/06 1:42 PM


All times are GMT -4. The time now is 1:26 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts