Default Main disconnect at meter instead of main panel. OK?

Is it OK to have the main disconnect at a combination enclosure at the meter instead of at the main panel (wired as a main panel)?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #2  
Old 11/7/06, 10:47 AM
Jeffrey S. Campbell's Avatar
Jeffrey S. Campbell Jeffrey S. Campbell is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Pittston, ME
Posts: 817
Send a message via AIM to jcampbell Send a message via MSN to jcampbell Send a message via Yahoo to jcampbell
Default Re: Main disconnect at meter instead of main panel. OK?

absolutely and very common... easier for fire dept access
Reply With Quote
  #3  
Old 11/7/06, 11:33 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,440
Default Re: Main disconnect at meter instead of main panel. OK?

That would be the service equipment (where the service disconnect is located). The other panel would be load side equipment and should have a four wire feed with isolated neutrals. . .



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #4  
Old 11/7/06, 12:22 PM
Michael R. Boyett's Avatar
Michael R. Boyett Michael R. Boyett is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Austin, TX
Posts: 4,352
Default Re: Main disconnect at meter instead of main panel. OK?

What I am seeing a lot of is a pedestal type meter/disconnect that feeds, via a lateral, a panel on the outside of the home that may or may not feed a load side panel in the garage. Typically, the panel at the outside of the home is wired as a service equipment panel with the neutrals & Gnd bonded together and 3 wires from the pedestal disconnect. The GEC to the ground rod or other grounding means enters the outside panel and is connected to the Gnd buss there.
Attachment 6721 Attachment 6722

Last edited by mboyett; 4/9/09 at 9:38 PM..
Reply With Quote
  #5  
Old 11/7/06, 12:58 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is online now
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,566
Send a message via ICQ to kshepard
Default Re: Main disconnect at meter instead of main panel. OK?

Quote:
Originally Posted by jpope
That would be the service equipment (where the service disconnect is located). The other panel would be load side equipment and should have a four wire feed with isolated neutrals. . .
There are split neutrals with a tie bar, but the bonding screw was missing at the neutral bus and the grounding bus bar was connected directly to the box. If the disconnect is in a separate panel, as it is, this seems correct to me.

4 wire feed? I see two hot conductors, one insulated neutral conductor and one uninsulated stranded aluminum conductor that looks like a neutral (there was another sub-panel in the garage). If the unisulated aluminum wire is the grounding conductor (GEC) why isn't it single strand copper?




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289


Last edited by kshepard; 10/2/08 at 1:40 AM..
Reply With Quote
  #6  
Old 11/7/06, 1:56 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,440
Default Re: Main disconnect at meter instead of main panel. OK?

That's a proper set-up Kenton. It's a four wire feed with isolated neutrals. It is not the service equipment.

The service equipment has the service disconnect (pic #1).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #7  
Old 11/7/06, 2:01 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is online now
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,566
Send a message via ICQ to kshepard
Default Re: Main disconnect at meter instead of main panel. OK?

Ah-ha! GEC goes from the service equipment (combination meter/disconnect enclosure to a grounding electrode. The stranded aluminum conductor is one of the isolated neutrals.

Thanks, Jeff.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #8  
Old 11/7/06, 2:03 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,440
Default Re: Main disconnect at meter instead of main panel. OK?

Michael, what you have described is common but improper. The "pedestal" is the service disconnect. The lateral should include a four wire feed to the next panel(s), which be considered "remote" panel(s).

The pedestal should have its own grounding electrode and the building should have one as well.

There may be some sparkies that will disagree because there are some exceptions to this, but as a home inspector, this is what you should expect to see, otherwise it should be deferred to an expert for verification.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #9  
Old 11/7/06, 2:07 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,440
Default Re: Main disconnect at meter instead of main panel. OK?

Almost Kenton.

The bare stranded conductor is the equipment grounding conductor (EGC), which should be attached to the grounding bus in the load side panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #10  
Old 11/7/06, 2:20 PM
Kenton H. Shepard, CMI's Avatar
Kenton H. Shepard, CMI Kenton H. Shepard, CMI is online now
InterNACHI Member
 
Join Date: Aug 2004
Location: Boulder, CO
Posts: 2,566
Send a message via ICQ to kshepard
Default Re: Main disconnect at meter instead of main panel. OK?

Ooop, yep, you can see it under the lug at the top of the grounding bus bar in picture #2.




Kenton Shepard, InterNACHI member # 04082383
Certified Master Inspector (CMI)
EXPERT WITNESS

Director of Green Building
Director for International Development

(303) 717-8940
(303) 258-8289

Reply With Quote
  #11  
Old 11/7/06, 8:58 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Main disconnect at meter instead of main panel. OK?

lol....Jeff beat me to it...lol.....yep thats the EGC...not the GEC...



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #12  
Old 11/8/06, 12:07 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Main disconnect at meter instead of main panel. OK?

One careful item with service disconnects separate from the service panel, [other ensuring the unbonding of neutral and ground bars], check where the grounding electrode conductor(s) is attached.

Heard stories where the outside electrician thought the inside electrician was doing 'them', and vice-versa.

tom
Reply With Quote
  #13  
Old 11/8/06, 6:00 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Main disconnect at meter instead of main panel. OK?

lol........outside electrician and inside electrician...lol........man where I come from only (1) electrician on the job...lol.....and he is KING...the helpers dont get to mess with the panels...lol.....not in my electrical company anyway..lol

But I am ANAL like that.....



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
  #14  
Old 11/8/06, 6:20 PM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Main disconnect at meter instead of main panel. OK?

Quote:
Originally Posted by pabernathy
But I am ANAL like that.....
Hey, doesn't show.

I'm saying in new construction. You should see the yahoo's that do the work, since the house isn't hooked up yet, no PPE and they move around like misguided army ants.

later,

tom
Reply With Quote
  #15  
Old 11/8/06, 6:24 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,697
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Main disconnect at meter instead of main panel. OK?

Tom,

Oh I hear ya brother......many times and in many states the actual guys out wiring the house do not even have to be licensed....they work under the owners license....sad but true.....and who knows WHAT they might do...

For example.....I caught (2) AHJ's today signing up for a local seminar I am doing that did not understand grounding and bonding correctly, AFCI's Correctly and a few other things...so IMAGINE how the local guys who actually DO the work are doing it....scary....



Paul W. Abernathy,CMI,CEI,CEPE
National Electrical Code Expert-ONLY
Weekly Live Chat :http://www.theelectricalguru.com/chat.html
Weekly Chat on Mondays & Wednesdays -8PM E.S.T
* Notice- I will not be conducting any future seminars for the HI Industry. I am a CODE GUY so I will be focusing efforts on the NEC Code. If you have CODE question visit my website...if you have Electrical HI questions ask Nick or Ben Gromicko.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Subpanel wired as main panel. jlybolt Electrical 15 5/23/07 4:10 PM
Metal Rigid or PVC Rigid what is code bpotts Electrical 5 12/4/06 2:40 PM
100 Amp Meter, 200 Amp Disconnect jweinberg Electrical 8 8/15/06 12:32 PM
Disconnect and Main panel srowe Electrical 10 6/13/06 7:49 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 3:38 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts