Default Main Disconnect missing verbage & cut main wire

This 5800 sq home has a main panel with no main breaker, a 100 amp sub panel, and a disconnect only box. Is it required that a main breaker be installed or can the lever type disconnect be an alternative? How would you word this?


We could not open the smaller lever disconnect box so I will state as such.


On the main panel what kind of verbage would you use for the main alumimum 4/0 wire that was spliced at the end just before reaching the lug. looks like the elec. was not skilled enough to fit it into the lug. The buyer claims that the panel has lost it's rating because of this. I believe so but had not seen this.

Thanks.
Attached Thumbnails
main-disconnect-missing-verbage-and-cut-main-wire-dsc05050.jpg   main-disconnect-missing-verbage-and-cut-main-wire-dsc05051.jpg   main-disconnect-missing-verbage-and-cut-main-wire-dsc04982.jpg  



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 1/15/11, 12:31 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Main Disconnect missing verbage & cut main wire

A "main breaker" is not required. The requirement is for a "service disconnect," which is what you have pictured. There is nothing to report here.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 1/15/11 at 12:35 PM..
Reply With Quote
  #3  
Old 1/15/11, 12:35 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Main Disconnect missing verbage & cut main wire

NEC 408.36
IN addition to the requirement of 408.30, a panelboard shall be protected by an overcurrent protective device having a rating not greater than the panelboard.

So if there is no over current protection then the panel is wrong. Also if the wire has been cut to fit the lug then it is derated and not suitable for the panel.

WHat was the power coming into the throw switch??




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #4  
Old 1/15/11, 12:54 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Main Disconnect missing verbage & cut main wire

Quote:
Originally Posted by sfogarty View Post
So if there is no over current protection then the panel is wrong.
The panel board requires over-current protection. The service disconnect for the structure is not required to be a "breaker" or "over-current device." Apples & oranges.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 1/15/11, 1:03 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Main Disconnect missing verbage & cut main wire

Quote:
Originally Posted by jpope View Post
The panel board requires over-current protection. The service disconnect for the structure is not required to be a "breaker" or "over-current device." Apples & oranges.
I understand that, but if the wires go straight from the switch to the panel board, then from the pics it appears there is no applicable overcurrent protection for the main panel....
Correct??




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #6  
Old 1/15/11, 1:09 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Main Disconnect missing verbage & cut main wire

Possibly, but we don't know what's in the other box. That may very well be a fused disconnect for the distribution panel.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 1/15/11, 1:13 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Main Disconnect missing verbage & cut main wire

Quote:
Originally Posted by rwashington View Post
We could not open the smaller lever disconnect box so I will state as such.
Guess there is our answer...




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
  #8  
Old 1/15/11, 4:31 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Disconnect missing verbage & cut main wire

Quote:
Originally Posted by jpope View Post
Possibly, but we don't know what's in the other box. That may very well be a fused disconnect for the distribution panel.

Could be, but I wouldn't bet on it. The conductors in the larger disconnect seem to be the same size as the conductors in the panel. The smaller disco to the right is a 100 amp and it's likely that #4/0 conductor wouldn't even fit in the lugs. There is a smaller enclosure to the right of the panel in photo #3 maybe the small disco feeds that. Either way the MLO panel with a non fused disconnect are a violation.
Reply With Quote
  #9  
Old 1/15/11, 4:48 PM
John Scaparo John Scaparo is offline
InterNACHI Member
 
Join Date: Apr 2009
Location: Canton, MI
Posts: 309
Default Re: Main Disconnect missing verbage & cut main wire

Shouldn't the interior main panel have a main disconnect because it looks like more than 6 hand movements to power down the panel or is the external switch consider the main disconnect.



John Scaparo
Innovative Home Inspection, LLC
Canton, Michigan 48187
734.664.5853

john@InnovativeHomeInspection.com


Michigan Licensed Residential Builder

2101201845

InterNACHI MI #09041012, AHIT Member
Plymouth Michigan Home Inspector
Canton Michigan Home Inspector



"Helping To Secure Your Home Investment"

Looking for link exchange partners.
If interested send me your link.

Reply With Quote
  #10  
Old 1/15/11, 5:29 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Main Disconnect missing verbage & cut main wire

Quote:
Originally Posted by sfogarty View Post
I understand that, but if the wires go straight from the switch to the panel board, then from the pics it appears there is no applicable overcurrent protection for the main panel....
Correct??
Is the "throw switch" the same thing as the "overcurrent protection"?



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #11  
Old 1/15/11, 5:42 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Main Disconnect missing verbage & cut main wire

Quote:
Originally Posted by Robert Meier View Post
Could be, but I wouldn't bet on it. The conductors in the larger disconnect seem to be the same size as the conductors in the panel. The smaller disco to the right is a 100 amp and it's likely that #4/0 conductor wouldn't even fit in the lugs. There is a smaller enclosure to the right of the panel in photo #3 maybe the small disco feeds that. Either way the MLO panel with a non fused disconnect are a violation.
Yes, they were 4/0 alum in the panel and also in the lg. disconnect.

The 4/0 conductor would fit. Just one of the wires is cut and the other lug is the same size but not "beaten" up like the one with the wires cut.

Is it ok for the 100 amp for the sub to be in the main panel? I have always seen it in the main.

The wall that the throw's are on is a detached 150-200sf office that has it's own smaller AC. I am thiinking the smaller throw is tied into this building.



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #12  
Old 1/15/11, 6:09 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Main Disconnect missing verbage & cut main wire

Quote:
Originally Posted by rwashington View Post
Is the "throw switch" the same thing as the "overcurrent protection"?
No. The switch does not provide over-current protection.

Quote:
Originally Posted by jscaparo View Post
Shouldn't the interior main panel have a main disconnect because it looks like more than 6 hand movements to power down the panel or is the external switch consider the main disconnect.
Quote:
Originally Posted by rwashington View Post
Is it ok for the 100 amp for the sub to be in the main panel? I have always seen it in the main.
You guys are really making this confusing by not using the proper terminology.

Forget the terms "main panel" and "main disconnect." The exterior panel is the "service" panel, which is where the "service" disconnect is located. All other panels are "load-side" equipment - call them sub-panels, distribution-panels, equipment-panels, lighting-panels, even just "panels."

Quote:
Shouldn't the interior main panel have a main disconnect because it looks like more than 6 hand movements
The rule applies to service equipment. The interior panel is not the service equipment.

Quote:
Is it ok for the 100 amp for the sub to be in the main panel? I have always seen it in the main
I don't know what you're asking here. The 100 OCPD can be located in the service equipment. If the distribution panel is in the same building, there is no need for an additional OCPD.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #13  
Old 1/15/11, 7:51 PM
Sean Fogarty's Avatar
Sean Fogarty Sean Fogarty is offline
InterNACHI Member
 
Join Date: Sep 2009
Location: Somewhere in Knoxville TN flipping breakers
Posts: 2,267
Default Re: Main Disconnect missing verbage & cut main wire

Quote:
Originally Posted by rwashington View Post
Is the "throw switch" the same thing as the "overcurrent protection"?
No......
its pretty simple.
The service disconnect is just what it is.. A disconnect, and not overcurrent protection. (I E cicuit breaker)

The panel itself needs some type of breaker between the disconnect and the panel. No matter if its a main or sub, somewhere at the begining it must have overcurrent protection.

If the "service disconnect were fused, then that would serve the purpose. Since it is not, and no other exists between it and the panel, in theory, then IT IS WRONG!!!

If you can find one then great, but if not it needs fixin!




Infraspection Institute Level 1 Certified Infrared Thermographer

Fogarty Inspection Services Group of Knoxville TN

Home inspections, Commercial Inspections, Thermal Imaging, Mold, Enviromental Testing and Radon Testing for Knoxville TN, Oak Ridge TN, Maryville, Clinton, Farragut, Lenoir City, Pigeon Forge, Sevierville and all the surrounding areas.

865-256-5397

www.homeinspectorknoxville.com

www.moldandradon.com

www.thermal-inspection.net

www.commercial-building-inspector.net
Reply With Quote
Need a home inspection in Nebraska? Check out InterNACHI's listing of Nebraska certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 1/15/11, 11:14 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Main Disconnect missing verbage & cut main wire

Quote:
Originally Posted by jpope View Post
The panel board requires over-current protection. The service disconnect for the structure is not required to be a "breaker" or "over-current device." Apples & oranges.
So.... since there is no breaker at the panel or sub panel to provide "over current protection" for the panel then it is wrong unless.....there is a fused over current at the small throw box.

In other words the throw boxes just act a "service disconnect".



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #15  
Old 1/15/11, 11:18 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Main Disconnect missing verbage & cut main wire

I don't know what you're asking here. The 100 OCPD can be located in the service equipment. If the distribution panel is in the same building, there is no need for an additional OCPD.[/quote]

So it does not matter if the 100 amp breaker for the sub panel can be located in the panel or sub panel?



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Main panel cover...anything missing? jfunderburk Electrical Inspections 6 2/9/10 7:44 PM
Disconnect and Main panel srowe Electrical Inspections 10 6/13/06 7:49 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 7:37 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts