Default Main Ground

Although todays code is specific about this and therefore would not be a questions this is an older home,...

would you ignore a situation where branch circuit wire was used gound the electrical system in the house? There is no evidence of a ground rod, or any other form of grounding,... just branch wire connected to the other side of the water meter.??
Reply With Quote
  #2  
Old 5/3/08, 11:13 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Ground

"Branch wire"?
What size wire? You should still add another electrode to suppliment the water pipe but if this is an old house and they never disturbed the 3/4-1" copper water or galvanized line in the yard it is a pretty good electrode. There is a good chance that it is plastic at the street if the utility ever worked on it.
If it is all metal then you have an excellent electrode.
Reply With Quote
  #3  
Old 5/3/08, 11:41 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Ground

Quote:
Originally Posted by csteele
would you ignore a situation where branch circuit wire was used gound the electrical system in the house?
What I think you're saying is that someone connected the ground of a circuit in the house to the water line instead of the ground/neutral bar in the panel? If that's the case, that's not really a ground at all, and should not be ignored. That doesn't meet any code or standard that ever existed in the history of electricity, and is a genuine hazard in the event of a ground fault. This potentially could (and probably will) energize all the pipework in the home during a ground fault without opening the overcurrent protection device (fuse or breaker).
Reply With Quote
  #4  
Old 5/3/08, 5:24 PM
csteele csteele is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Arnprior, On
Posts: 166
Default Re: Main Ground

My apologies I didn't do a good job explaining.

They used old romex 14 gauge wire from the ground bus to the other side of the water meter to ground the system. The water pipe coming in from the street is copper. They simple twisted the black and white together, connected it to the bus in the panel, then connected it to the other side of the water meter. This wire is not connected to anything else. Just not sure if this is acceptable.

Thanks again.
CS
Reply With Quote
  #5  
Old 5/3/08, 5:48 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Ground

Quote:
Originally Posted by csteele
My apologies I didn't do a good job explaining.

They used old romex 14 gauge wire from the ground bus to the other side of the water meter to ground the system. The water pipe coming in from the street is copper. They simple twisted the black and white together, connected it to the bus in the panel, then connected it to the other side of the water meter. This wire is not connected to anything else. Just not sure if this is acceptable.

Thanks again.
CS
This is not acceptable for several reasons.
Reply With Quote
  #6  
Old 5/4/08, 7:52 AM
csteele csteele is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Arnprior, On
Posts: 166
Default Re: Main Ground

Quote:
Originally Posted by Mike Whitt
This is not acceptable for several reasons.
This is what I thought but I'm not sure exactly why it is unacceptable. Several reason?
Reply With Quote
  #7  
Old 5/4/08, 9:23 AM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Unmoderated Guest
 
Join Date: Sep 2005
Location: North Carolina
Posts: 477
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Ground

Quote:
Originally Posted by csteele
This is what I thought but I'm not sure exactly why it is unacceptable. Several reason?
First the smallest conductor allowed by Table 250.66 is a #8

Then we have an issue with the two conductors being connected in parallel. Section 310.4 requires that conductors connected in parallel to be at least 1/0

These are two major issues with this installation.
Reply With Quote
  #8  
Old 5/4/08, 12:48 PM
gmortensen gmortensen is offline
New User
 
Join Date: Aug 2007
Location: Cambridge, ON
Posts: 94
Please Note: gmortensen is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Ground

The code is the same in Ontario Chris. Minimum #8 ground and 1/0 for parallel conductors
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What's this video worth? jtedesco1 Inspection Education & Training 5 4/18/08 9:24 AM
Main Panel Ground dnasser Electrical Inspections 10 12/2/07 4:31 PM
4 ground wires into 1 in main panel psiposs Electrical Inspections 13 5/18/06 1:27 PM


All times are GMT -4. The time now is 7:38 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts