Question Main hallway bath GFCI

I was inspecting an older, but updated Town House today and when I tested the main hallway bath GFCI it killed the hallway recess light as well.

It seems to me that I read something someplace that said that was ok, but I still have an weird feeling about it and I don't know why.

And one other thing in the kitchen... the dishwasher was on a switched circuit. One switch was for the disposal, the other interrupted power to the dishwasher. I could trace the disposal
power to the outlet onder the sink, but never could find the power cord for the dishwasher.

Could be that I have a bad cold and I'm just not thinking right tonight...

Paul, Joe...anyone?

Quote:
edited due to being a bonehead speller tonight



Brian R. Sumpter
First Call Inspections
Proudly serving most Bay Area Counties

www.firstcallinspections.com

Last edited by bsumpter; 12/20/06 at 12:57 AM..
Reply With Quote
  #2  
Old 12/20/06, 6:02 AM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main hallway bath GFCI

Brian,

The GFCI controlling the hall light is OK. I beleive that newer codes may call for the bathrooms to be on their own circuit, but I am sure Paul or Joe will verify that.

Was the kitchen remodeled. They may have moved the diswahser and are using a circuited outlet. It really is not a problem so long as everyone knows the switch controls the dishwasher.
Reply With Quote
  #3  
Old 12/20/06, 10:31 AM
bsumpter bsumpter is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Martinez, CA
Posts: 232
Default Re: Main hallway bath GFCI

Thanks William, I appreciate your thoughts.

As to the dishwasher, thats kind of what I was thinking, but just want to be certain before I release the report this today.



Brian R. Sumpter
First Call Inspections
Proudly serving most Bay Area Counties

www.firstcallinspections.com
Reply With Quote
  #4  
Old 12/20/06, 11:14 AM
tdietrich1's Avatar
tdietrich1 tdietrich1 is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Northampton County - Pa
Posts: 1,954
Send a message via Yahoo to tdietrich1
Default Re: Main hallway bath GFCI

Today's codes only seem to only allow bathroom receptacles on a dedicated bathroom receptacle circuit(with an exception for bathroom loads like lights under certain conditions). So by code it wouldn't be ok, today.

However, I would point out the the client, that the GFCI can be wired in such a way, that if the receptacle trips, the lights remain on. This way a bad hair dryer doesn't create for a dark and dangerous situation. Recommend deferring to a qualified electrician for further evaluation, as needed.

As for the dishwasher, you might have some code junkie trying to meet some disconnect in sight rule. Or someone that just wired it with what they had. Once again, for the convenience of the home owner, might want to have a qualified electrician to investigate further.

tom
Reply With Quote
  #5  
Old 12/20/06, 3:03 PM
smcarthur smcarthur is offline
New User
 
Join Date: Jul 2006
Location: Rock Hill, SC
Posts: 96
Please Note: smcarthur is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main hallway bath GFCI

As for the dishwasher, Thomas is correct. All fastened in place appliances are required by the NEC to have a service disconnect. The cord can be used ifthe appliance is cord and plug connected, but if the appliance is hardwired, as I suppect this one was and the reason you couldn't find the appliance cord, then you must have a disconnecting means and a switch meets that requirement. By the way, that's how I usually wire a dishwasher and disposal. One two gang bo with one switch for the disposal and one for the dishwasher and hard wire to both.
Reply With Quote
  #6  
Old 12/20/06, 6:23 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Main hallway bath GFCI

Hello All,

I will have to agree on the switch for the dishwasher, as many areas would like it disconnected in this manner as most of the time we simply cord and plug them as Steve was refering to.

On the hall Recess on the GFCI....really depends on when the remodel was done and IF this was part of the remodel....technically speaking the GFCI in the bathroom should not have anything else on it except another bathroom GFCI from a different bathroom ( or if only one bathroom..it can have the lights of that same bathroom as well...but the circuit can't leave that single bathroom. )

Again....no major red flags on the dishwasher thing to worry about...unless of course the switch is a ROCKER style...then it would not be allowed for use as the disconnection means for that circuit because rockers are not labeled with on and off.

AS for the recess again......Really depends on when the house was built...and when a remodel takes place....but if the bathroom recept. is on GFCI...and is protected...I would probably say it is fine....



Paul W. Abernathy
Reply With Quote
  #7  
Old 12/20/06, 6:57 PM
dchew dchew is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: San Ramon, CA
Posts: 317
Default Re: Main hallway bath GFCI

It sounds like this is a older home where electrical wiring can be a bit of a mystery sometimes. I work Contra Costa county too, so I've seen a lot of variation in electrical wiring depending on the age of the house.

Ideally, the bathroom(s) and dishwasher outlet should be on separate circuits. Unless, this is a relatively new house, I wouldn't write it up as a electrical hazard. However, I would definitely insert a comment about it.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
AFCI Questions and Answers - Mike Holt pabernathy Electrical Inspections 7 4/16/12 9:51 PM
GFCI Safety Notice rcooke Electrical Inspections 1 10/30/07 12:29 PM
GFCI below the main panel dmacy Electrical Inspections 14 9/21/07 6:14 PM
Another GFCI Question rnewland Electrical Inspections 2 6/16/07 2:25 PM
The question asked on the new HI Study test here? jtedesco1 Electrical Inspections 28 10/4/06 9:31 AM


All times are GMT -4. The time now is 7:38 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts