Old 4/11/13, 3:57 PM
Mitch Waldon, CCHI Mitch Waldon, CCHI is offline
Default Main house panel fed from garage
Hi Folks,
I'm hoping you can help me understand sub panel wiring. It seems to me that this panel is wired incorrectly. Apparently a licensed electrician did the work, but something is not sitting well with me.
The main power feed is to a panel in the garage. This panel is fed from that panel in the garage, making it a sub panel.
Should there not be a 4 wire feed from the main panel? 2 supply, neutral and ground.
They have twisted together the bare wires in the supply cable to create a neutral, and run a separate ground to the copper main water supply. OK, I can see how that might work, but they've bonded that ground to the neutral bus. That's a serious no no is it not?
The fix I can see is to remove the ground from the neutral bus and attach it to the short bar to the left of the neutral bar, as shown in the last pic.,(thereby grounding the panel) and to pull the bonding jumper screw in the top of the neutral bus in the center of the panel.
I know the proper protocol is to have a licensed electrician evaluate. I'm trying to understand for myself what is going on. (besides, a licensed electrician did the work!)
Thanks all.
main-house-panel-fed-garage-download-4112013-002.jpg   main-house-panel-fed-garage-download-4112013-003.jpg   main-house-panel-fed-garage-download-4112013-004.jpg   main-house-panel-fed-garage-download-4112013-005.jpg   main-house-panel-fed-garage-download-4112013-007.jpg
Mitch Waldon
Waldon Works Ltd.
Edmonton, Alberta.
www.waldonworks.com
Need a home inspection in Alabama? Check out InterNACHI's listing of Alabama certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
Old 4/11/13, 5:25 PM
Robert Meier's Avatar
Robert Meier Robert Meier is offline
Default Re: Main house panel fed from garage
The GEC from the water pipe should go to the ground bus not the neutral bus. The feeder must have 4 conductors not three.
Old 4/11/13, 5:32 PM
Unmoderated Guest
Is the garage attached or detached?
Old 4/11/13, 5:39 PM
It's detached.
Mitch Waldon
Waldon Works Ltd.
Edmonton, Alberta.
www.waldonworks.com
Old 4/12/13, 12:43 PM
Unmoderated Guest
Prior to the 08 NEC a three wire feeder was allowed to outbuildings if no metallic path existed between the two buildings. The panel was bonded neutral to ground the same as a service panel.
A three wire feeder is allowed to remain under the NEC. A new installation would require a 4 wire feeder.
Old 4/12/13, 1:05 PM
Thanks for the replies folks.
Just so I'm clear: The wiring is OK based on 08 NEC (there is no metallic path), but because this work was completed in 2010, the feed should have been 4 wire.
Seems the electrician was not up to date with his code knowledge.
Also turns out the City inspector only looked at the work done in the garage. Never came inside to check the replacement panel inside.
Thanks again for your help. It's always great to learn something from the experts!
Cheers-
Mitch Waldon
Waldon Works Ltd.
Edmonton, Alberta.
www.waldonworks.com
Old 4/12/13, 2:05 PM
Unmoderated Guest
Mitch, sometimes the adoption of the latest NEC is several years after the date of the code. As such the 2010 install may still have been under a code prior to the 08.
Here I know of one jurisdiction that was still on the 93 up until 2002.
Old 4/12/13, 2:15 PM
Thanks for the reminder Jim. Best to check with AHJ.
Thanks to Robert too.
Mitch Waldon
Waldon Works Ltd.
Edmonton, Alberta.
www.waldonworks.com
Old 4/12/13, 5:26 PM
Humberto Carvajal's Avatar
Humberto Carvajal Humberto Carvajal is online now
Very good point you've brought up Jim. We sometimes tend to forget this when onsite looking at an install. Thanks as usual for your insight and knowledge.
Bert
Humberto Carvajal Jr.
Florida State Property Inspections, LLC
Florida Home Inspector License# HI884
LEED® Accredited Professional
Member USGBC South Florida Chapter
Old 4/15/13, 12:18 AM
scuthbert scuthbert is offline
InterNACHI Student
Don't forget gentlemen, Mitch is from Edmonton, and the NEC does Not apply.
Mitch, I can't really tell from the pictures you posted and would have to look at the service. I would be very glad to come out and let you know if the work is done properly.
Steven Cuthbert
Red Seal Journeyman Electrician
Proud InterNACHI Student.
Old 4/17/13, 11:49 PM
Erik Schmidt Erik Schmidt is offline
There should be an inspection sticker if it is Edmonton.
Erik Schmidt
East Side Home Inspection
Edmonton Alberta
780 477 2666
Old 4/19/13, 2:23 AM
Yes Erik, there is a sticker on the panel. On closer inspection it turned out it's for a sewer backwater valve! There is a sticker on the panel in the garage for the service. Apparently the inspector didn't get inside the house.
Thanks.
Mitch Waldon
Waldon Works Ltd.
Edmonton, Alberta.
www.waldonworks.com
Main Panel or not? tgreenwald Miscellaneous Discussion for Inspectors 0 12/20/12 1:20 AM
Main panel installed at floor level in garage jfrederick Electrical Inspections 5 7/5/09 9:39 AM
Main and Sub Panel gheller Electrical Inspections 10 9/25/08 10:22 PM
Main disconnect at meter instead of main panel. OK? kshepard Electrical Inspections 14 11/8/06 7:24 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM