Question Main at meter pole, distribution in home

At todays inspection, house was built in 1999, and is in the county, not city. The main panel was on the meter pole at the far end of the yard and with no common connection (fence) to the home. 2/0 CU to a 200 Amp panel, with 200 amp main breaker.

In the house was another 200 Amp panel with 3 wire feed, neutrals (grounded) and grounding mixed under the same terminal screw, and it was bonded.

In my tired brain condition tonight this would need (correct me if I'm wrong, please) --
- remove bonding strap
- add grounding bus bar and separate the grounded / grounding conductors
- what about the missing incoming ground?

I would refer to qualified electrician, but I need to know for my own info.
Thanks,
Linda
Attached Thumbnails
main-meter-pole-distribution-home-101_0762x-medium-.jpg.jpg
Views:	63
Size:	92.4 KB
ID:	22629   main-meter-pole-distribution-home-101_0806x-medium-.jpg.jpg
Views:	54
Size:	112.1 KB
ID:	22630  



Linda Foster
www.HomeInspectionsByFoster.com
HomeInspectionsByFoster@yahoo.com

(210) 347-1023
TREC #7654
InterNACHI #06032691

Reply With Quote
  #2  
Old 7/13/08, 12:29 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main at meter pole, distribution in home

You might have to under the 2008 code but this is fine before that. (separate structure, no metalic paths).
Reply With Quote
  #3  
Old 7/13/08, 12:55 AM
pdoane's Avatar
pdoane pdoane is offline
Active Poster
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,040
Please Note: pdoane is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main at meter pole, distribution in home

Was it a manufactured home? If not, its odd to have a meter on a pole if its relatively new construction (1999)

BUT
Some thoughts,...
- The pole main panel could have been service for an empty lot, someone may have used for hooking up to a camping trailer etc.
- There may have been an old manufactured home site prior to the new construction and they left the meter on the pole and then tapped (split) off at the meter making two main panels, etc.
Too many "what if's" to make recommendation for "corrective" repairs. You can call it out as non standard, note your support info and have a qualified electrician review for determination of proper set up. I wouldn't recommend correcting anything per say, let the electrician determine proper set up fist as it might be ok.... IMO
Reply With Quote
  #4  
Old 7/13/08, 9:07 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main at meter pole, distribution in home

We have a lot of this here. Either customer poles or what we call pedestal services. Just the meter on a pedestal and then on to the house. Many times we will put a feed-through panel (similar to the one in the pic) on the pole or pedestal for construction power. Then later go from the feed-through lugs to the house.

As Greg said, it is perfectly legal and typical to run a "3-wire" service lateral to the house and treat the house as a "main" service.

So unless the house was built under the 2008 NEC this is quite typical and correct.

NOW......

Only thing I don't see is IS there a disconnect for the house? A main lug panel is NOT sufficient without a disconnect somewhere at the structure.
Problem is the fact that the panel THEN becomes a sub-panel and the grounds and neutrals must be kept isolated.

Last edited by Speedy Petey; 7/13/08 at 9:11 AM..
Reply With Quote
  #5  
Old 7/13/08, 1:22 PM
Linda J. Foster's Avatar
Linda J. Foster Linda J. Foster is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Utopia, TX
Posts: 463
Default Re: Main at meter pole, distribution in home

Sorry for the duplicate post. Thought I lost the first one, and created a second.

The conduit from the meter pole to the house is PVC.

The panel at the pole has breaker for water
well, previously had breaker for RV at the adjacent barn. I 'assume' the conductors from bottom of this panel is for the barn panel.

Not used for manufactured home.
There is no shut-off in the house. Only in the meter pole panel, which is a long way to go in an emergency.

I will refer to electrician for evaluation.

Thanks for the help,
Linda



Linda Foster
www.HomeInspectionsByFoster.com
HomeInspectionsByFoster@yahoo.com

(210) 347-1023
TREC #7654
InterNACHI #06032691

Reply With Quote
  #6  
Old 7/13/08, 3:17 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main at meter pole, distribution in home

I have heard this debated a lot at inspector meetings.
230(A)(1) Readily Accessible Location. The service disconnecting means shall be installed at a readily accessible location either outside of a building or structure or inside nearest the point of entrance of the service conductors.

It does not specify a distance inside or outside the building.
In Linda's case I would raise the "readily available" flag due to the fence.
There is also the question, is a pole a structure? making the house the second structure.
Reply With Quote
  #7  
Old 7/17/08, 10:30 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 506
Default Re: Main at meter pole, distribution in home

Except for possibly the distance between the two locations, this arrangement is pretty common in our area. However, the inside panel is almost always treated as a subpanel fed with a 4 wire circuit.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #8  
Old 7/17/08, 11:31 PM
Doug Edwards,  CMI's Avatar
Doug Edwards, CMI Doug Edwards,  CMI is offline
InterNACHI Member
 
Join Date: Apr 2004
Posts: 3,516
Default Re: Main at meter pole, distribution in home

and remove the bird's nest
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Got a letter from ASHI's President today. gromicko General Inspection Discussion 36 2/24/08 1:30 AM


All times are GMT -4. The time now is 12:08 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts