Today's house had the main panels/breaker and directly on the other side of the wall in the garage were the breaker panels. These breaker panels are sub panels (the neutral is separated from the ground and box and the ground is bonded to the panel.
Aren't these sub panels required to have a disconnect or do the exterior ones suffice?
Where there is a Will there is a Way! Will Misegades TREC# 10465 RedFish Home Inspections www.redfishinspections.com |
| Need a home inspection in Connecticut? Check out InterNACHI's listing of Connecticut certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
No disconnect is required for those sub panels. I don't see any grounding electrode conductors in the two service disconnects.
|
|
#3
|
||||
|
||||
|
Ground is bonded to the neutral because of electrical conduit.
THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#4
|
|||
|
|||
|
I was about to right it up as no grounding electrode. So, are you saying this installation is correct?
Where there is a Will there is a Way! Will Misegades TREC# 10465 RedFish Home Inspections www.redfishinspections.com |
|
#5
|
||||
|
||||
|
Quote:
The GES should be verified or established. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#6
|
|||
|
|||
|
Yes the remote panels are compliant. They do not need a main breaker for the panel as the service disconnect will turn the remote panel off.
As to the grounding electrode, it could be installed in the enclosure that is below the two service disconnects. Mike Whitt Contractor/Instructor |
|
#7
|
||||
|
||||
|
Correct and I also agree with Jeffrey P. If you cannot confirm the GEC don't guess.