Default Main panel grounds & neutrals

Today's inspection had this 200 amp panel. The left side is the neutral bus bar which is bonded. The bus bar on the right was not bonded and/or floating with both neutrals and grounds connected. At the bottom right, is a grounding bus bar, with grounds only, which was bonded. Now, all neutrals & grounds, at the main panel, need to be connected/on the same bus bar which is bonded to the enclosure, right? (or all grounds & neutrals need to connected and bonded to the enclosure) I realize the pic is a little difficult to see, but that's all I have. Any help would be appreciated.

Thanks,
Josh
Attached Thumbnails
main-panel-grounds-and-neutrals-20429-kiser-rd.-defiance-033.jpg  
Reply With Quote
  #2  
Old 2/23/09, 4:29 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Main panel grounds & neutrals

Yes, all grounded and grounding conductors are required to be bonded to the enclosure and the grounding electrode at the service equipment.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 2/23/09 at 4:35 PM..
Reply With Quote
  #3  
Old 2/23/09, 4:34 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,847
Default Re: Main panel grounds & neutrals

Quote:
Originally Posted by jpope View Post
Yes, all grounded and ungrounded conductors are required to be bonded to the enclosure and the grounding electrode at the service equipment.
Jeff, I think you wanted to say "all grounded and grounding conductors are required to be bonded to the enclosure..."



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
  #4  
Old 2/23/09, 4:36 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Main panel grounds & neutrals

Quote:
Originally Posted by lkage View Post
Jeff, I think you wanted to say "all grounded and grounding conductors are required to be bonded to the enclosure..."
Woops! Thanks for the catch



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 2/23/09, 8:02 PM
grusk grusk is offline
Active Poster
 
Join Date: Feb 2006
Location: FT. JENNINGS, OH
Posts: 191
Please Note: grusk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main panel grounds & neutrals

Josh; is this a manufactured home?

Gary

HSS Property Inspection
Reply With Quote
  #6  
Old 2/23/09, 8:59 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Main panel grounds & neutrals

Quote:
Originally Posted by grusk View Post
Josh; is this a manufactured home?

Gary

HSS Property Inspection
Yes it was. An All American. Does that make a difference? I've never it quite seen a panel set up like this (even in other All Americans). I know they have to follow codes, so this is why I was kind of confused.
Reply With Quote
  #7  
Old 2/23/09, 9:15 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Main panel grounds & neutrals

Often, in MFH's, the service panel is separate from the home, making your panel a "sub" panel.

In such a case, only the grounding conductors (grounds) can be bonded to the panel. The grounded conductors (neutrals) must be isolated from the enclosure.

Where were the service entrance and meter?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 2/23/09 at 9:26 PM..
Reply With Quote
  #8  
Old 2/23/09, 9:20 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Main panel grounds & neutrals

Meter & underground service were outside directly behind this panel. This was no doubt the main disconnect/panel.
Reply With Quote
  #9  
Old 2/23/09, 9:26 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Main panel grounds & neutrals

Attached to the structure?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #10  
Old 2/23/09, 9:28 PM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Main panel grounds & neutrals

Yes.
Reply With Quote
  #11  
Old 2/23/09, 9:32 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Main panel grounds & neutrals

Then, as stated before, all grounded and grounding conductors are required to be bonded to the enclosure and the grounding electrode.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #12  
Old 2/23/09, 9:55 PM
grusk grusk is offline
Active Poster
 
Join Date: Feb 2006
Location: FT. JENNINGS, OH
Posts: 191
Please Note: grusk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main panel grounds & neutrals

Josh; All Americans are modular homes (not a mobile home) they follow the same electrical codes as if building a custom home, the main panel/load center should be bonded as Jeff posted.

Gary

HSS Property Inspection
Reply With Quote
  #13  
Old 2/23/09, 9:58 PM
tmcsweeney tmcsweeney is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Buffalo, NY
Posts: 28
Default Re: Main panel grounds & neutrals

It's hard to determine by the picture but if it is the main panel I wouldn't be surprised if at a closer look the neutral and grounding bars are connected by a bus going from left to right. If this is not the case then the bar on the right should not have had both neutrals and grounds attached. This is a common panel configuration.
Reply With Quote
  #14  
Old 2/24/09, 2:14 AM
Michael Thellend's Avatar
Michael Thellend Michael Thellend is offline
New User
 
Join Date: Feb 2009
Location: Cardinal, ON, Canada
Posts: 30
Please Note: Michael Thellend is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main panel grounds & neutrals

Hi,

I see a few problems.

If this is the main disconnecting means of the house then the main grounding conductor should be attached to the main neutral bar lug, I don't see it. From this point there should be a bonding screw or jumper that goes to the panels enclosure. The neutral bars appear to be connected with a bar running behind the main breaker, they should be isolated from the enclosure and be connected by the bonding jumper only. Grounding conductors and grounded conductors can be either together on the neutral bar or the grounding conductors can go on the enclosure grounding bar. The neutrals or grounded conductors go on the neutral bars on either side of course.

There seems to be missing plastic bushings on the large conduits entering the panel.

Mike
Reply With Quote
  #15  
Old 2/26/09, 8:57 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Main panel grounds & neutrals

Might want to suggest they IDENTIFY the grounded conductor properly as well. Last i checked it was to be White, Grey, Any Color other than green with (3) white stripes and you get where I am going.

Just remember at a Service Disconnection Means Panel Location = Neutrals ( Grounded ) and Grounding ( usually bare or green conductors ) bonded together.

Just remember at a Remote Distribution Panel ( Sub-Panel ) Location = Neutrals (Grounded) and Grounding ( usually bare or green conductors ) seperated. Grounding conductors bond to enclosure while the Grounded is isolated from the connection to the metal enclosure.

Any case to neutral connection in the panel system other than at the main service panel is considered a violation of the NEC. (In General ) since we do currently have a few places in the NEC we do allow this with still with some specific requirements but why go there...right....



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric Panel dmozzillo Electrical Inspections 26 1/26/09 1:18 PM
Panel Questions - main, mid, sub lfoster Electrical Inspections 6 11/11/08 9:42 PM
Subpanel wired as main panel. jlybolt Electrical Inspections 15 5/23/07 4:10 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 4:54 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts