Default Main Panel Jumper

I'm taking the required 25 Standards Every Inspector Should Know course. In it, it states that bonding bushings and jumpers are required for metal conduit entering the main panel through concentric or eccentric knockouts. Unfortunately, I'm pretty weak in electricity and I don't completely understand that statement. Anyone want to clarify?
Reply With Quote
Need a home inspection in Hawaii? Check out InterNACHI's listing of Hawaii certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 8/20/10, 10:23 AM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Main Panel Jumper

I'll try. The panels used in most residential work are pre-punched with knockouts that allow for easy creation of openings of various sizes. The holes can be concentric (all holes have the same center point) or eccentric (holes centered toward one side). All that doesn't really matter. The point is that because of the prepunched holes there is a concern that proper bonding may not be present. Therefore, a bushing has to be installed on the conduit that that permits a jumper to be installed between the condiut and panel thus insuring continuity.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #3  
Old 8/20/10, 1:45 PM
Justin R. Ake Justin R. Ake is offline
InterNACHI Member
 
Join Date: Aug 2010
Posts: 14
Default Re: Main Panel Jumper

Mr. Newman,

Thanks for getting back to me. That does help. I'm pretty weak in electricity and need to get smart on it before I start inspecting homes. I was curious as to the reasoning behind the needed bonding but that makes sense now. Thank again.

Justin
Reply With Quote
  #4  
Old 8/20/10, 3:07 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Main Panel Jumper

For those without an electical background, that area is almost always the weakest for a new inspector. For your own safety and knowledge, I would suggest taking every course you can find on the subject, then see if you can find someone who is willing to let you go around with them specifically to look at the electrical side of the business. Any other questions, please ask here - there are many who will be glad to help.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #5  
Old 8/20/10, 9:18 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,249
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Panel Jumper

The use of a metallic service raceway requires that the raceway be bonded by means other than standard locknuts. That means a bonding bushing, bonding locknut, hub or bonding wedge is required to bond that raceway. When no concentric or eccentric KO's are encountered a bonding locknut is permitted to bond the raceway. If concentric, eccentric KO's are encountered then a bonding bushing with the proper sized bonding jumper (NEC Table 250.66) is required. One other note, the bonding bushing, locknut, wedge or hub is only required on one end of the metallic service raceway.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Sub panel main tripping? crichiii Electrical Inspections 6 12/28/06 10:08 AM
Main Panel location dmacy Electrical Inspections 5 12/6/06 6:32 PM
Main disconnect at meter instead of main panel. OK? kshepard Electrical Inspections 14 11/8/06 6:24 PM
Panel Inspection Safety roconnor Electrical Inspections 10 9/24/06 9:02 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 4:54 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts