There is a 100 amp breaker and a 50 amp breaker, is the fifty amp not in use anymore? just does not seem right, any help would be great
|
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
The fitting entering the back of the panel appears to be missing a locknut.
The 100 amp feeder to the indoor panel appears to only have an EGC, and lacks a neutral. Unless the indoor panel only has 240 volt loads, I suspect very much that they are using that EGC as a neutral, and have that subpanel set up as a 3-wire feed. Not only is this improper for a subpanel, but that #6 copper EGC is undersized for use as a neutral, even if you could use it that way. The 50 amp breaker must have went to a packaged outdoor hot tub that is no longer in use. |
|
#3
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
I have never seen load side feeders re enter the service side like that. Shouldn't the service side be sealed and reserved for the POCO?
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 7:28 PM |
| Subpanel wired as main panel. | jlybolt | Electrical Inspections | 15 | 5/23/07 4:10 PM |
| Main disconnect at meter instead of main panel. OK? | kshepard | Electrical Inspections | 14 | 11/8/06 6:24 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 9:02 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |