Default Main Panel with splices...see pic

Can you have splices in a main panel ?

Reply With Quote
Find an InterNACHI certified South Dakota Home Inspector (and anywhere else in North America)
  #2  
Old 6/7/09, 8:20 PM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 8,342
Send a message via Yahoo to jfunderburk
Default Re: Main Panel with splices...see pic

Yes, but that one looks a little weird. Were the wire sizes appropriate for the amperage?



“The things that will destroy America are peace at any price,
prosperity at any cost, safety first instead of duty first,
the love of soft living, and the get-rich-quick theory of life.”
Theodore Roosevelt


Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #3  
Old 6/7/09, 8:20 PM
arook arook is offline
Active Poster
 
Join Date: Jan 2006
Location: Hamilton, NJ
Posts: 256
Please Note: arook is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Panel with splices...see pic

Yes - as long as they use the correct wire nut for the wire sizes and all the wires connected together are all the same or greater wire sizes than the breaker.

Other problems:
1. Wire should not go across the panel like that, they should go around
2. Missing wire grommets (protectors)

I'm sure others will chime in.
Reply With Quote
  #4  
Old 6/7/09, 8:57 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Main Panel with splices...see pic

Is that panel listed for those Tandom Breakers?. Check the panel legend to see. One of them appears to be doubled up as well on the tandom. As someone mentioned those NM Cables need to be secured at the enclosure as well. I also can't tell but it appears one of the splices is for the grounded conductor which promptly changed back over to a black conductor.....which is a No-No as well.
Also it appears to be different types of manufacturer breakers in this enclosure. Are the breakers Classified to be in this panel or simply a hodge-podge of breakers being used. And ofcourse see which breaker those larger conductors spliced to the small conductors actually terminates on....could be undersized conductors ( probably the case ).....Also verify the main bonding jumper is installed ( as we can't see all that due to the clutter ) which brings me to the splice question....

Yes, you can have spliced in a panel as long as their is space provided for such splices and as long as the panel is not being used as simply a pass through junction box. The NEC tells us no splices in a panel but then goes on to allow it provided the space is provided.....and I wont get into the math associated with that.

Check out these little dandies.....

312.7 Space in Enclosures.
Cabinets and cutout boxes
shall have sufficient space to accommodate all conductors
installed in them without crowding.

312.8 Enclosures for Switches or Overcurrent Devices.
Enclosures for switches or overcurrent devices shall not be
used as junction boxes, auxiliary gutters, or raceways for conductors
feeding through or tapping off to other switches or
overcurrent devices, unless adequate space for this purpose is
provided. The conductors shall not fill the wiring space at any
cross section to more than 40 percent of the cross-sectional
area of the space, and the conductors, splices, and taps shall
not fill the wiring space at any cross section to more than
75 percent of the cross-sectional area of that space.



Paul W. Abernathy
Reply With Quote
  #5  
Old 6/7/09, 10:30 PM
David Nasser's Avatar
David Nasser David Nasser is offline
InterNACHI Member
 
Join Date: Mar 2006
Location: Moreno Valley, CA
Posts: 771
Default Re: Main Panel with splices...see pic

Thanks everybody
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric Panel dmozzillo Electrical Inspections 26 1/26/09 1:18 PM
Panel Questions - main, mid, sub lfoster Electrical Inspections 6 11/11/08 9:42 PM
Subpanel wired as main panel. jlybolt Electrical Inspections 15 5/23/07 4:10 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 4:54 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts