Default Main Panel vs Sub-Panel and main disconnect?

I am filling out an inspection report on a 1979 condo. The main disconnect is at the meter in a central utility room which also contains the meters and disconnects for the other 8 condos in the building. The meter room is 100 feet from the subject condo. Is the panel inside the condo considered the main panel or a sub-panel? There is no main disconnect in the condo's panel so it would take more than 6 hand motions to turn off the power from inside the condo. Can the remote disconnect in the utility room satisfy the less than 6 hand motions rule to disconnect the power for the condo?

Also there are 2 double taps in the panel which I plan to write-up, however I'm not sure if I should write-up the drywall finish overspray which could also be on the non-visible busbar under the breakers and cause heatup due to a poor contact. I just say an educational video which said this could be a problem, though it's probably been that way since 1979 and not caused a problem yet. What do you think? Note: Panel photo attached.
Attached Thumbnails
main-panel-vs-sub-panel-and-main-disconnect-img_1182-compressed.jpg  
Reply With Quote
Find an InterNACHI certified Massachusetts Home Inspector (and anywhere else in North America)
  #2  
Old 10/18/09, 10:36 PM
rbrady's Avatar
rbrady rbrady is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Eureka, CA
Posts: 619
Please Note: rbrady is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Panel vs Sub-Panel and main disconnect?

I state where the main disconnect breaker/panel is located and I refer to the other one as the main distribution panel.
Reply With Quote
  #3  
Old 10/18/09, 11:48 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Main Panel vs Sub-Panel and main disconnect?

Normally, the panel containing the disconnect (even if that is the only breaker) is the considered to be the main panel and any downstream are sub-panels (some call them remote distribution panels), subject to the rules governing them.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA

Last edited by fnewman; 10/18/09 at 11:55 PM..
Reply With Quote
  #4  
Old 10/18/09, 11:57 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is online now
InterNACHI Member
 
Join Date: Mar 2008
Location: Lake Forest, Il
Posts: 1,117
Default Re: Main Panel vs Sub-Panel and main disconnect?

http://www.nachi.org/forum/f13/no-ma...connect-40939/

More discussion on past thread.

Jeff



Jeff Wicklander
Corwick Home Services

Join my business on Facebook
Reply With Quote
  #5  
Old 10/19/09, 1:15 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 7,760
Default Re: Main Panel vs Sub-Panel and main disconnect?

If we lose the word "main," it becomes much less confusing.

There is "service" equipment, and there is "other" equipment. The service equipment contains the service disconnect, which also disconnects power from other equipment. A service disconnect (six or less throws) is required only at the service equipment. Other equipment does not fall under the "six throw rule" (exceptions do apply).



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 10/19/09 at 1:20 PM..
Reply With Quote
  #6  
Old 10/19/09, 4:17 PM
wh349055 wh349055 is offline
New User
 
Join Date: Feb 2006
Posts: 2
Please Note: wh349055 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main Panel vs Sub-Panel and main disconnect?

There also appear to be some low voltage wires (those orange wire nuts) at the top of the panel. Thats a violation worth mentioning
Reply With Quote
  #7  
Old 10/20/09, 4:55 PM
Tim Larsen Tim Larsen is offline
InterNACHI Member
 
Join Date: Mar 2009
Location: Central Vermont
Posts: 139
Default Re: Main Panel vs Sub-Panel and main disconnect?

I don't see any ground conductors...?

Tim
Reply With Quote
  #8  
Old 10/20/09, 5:20 PM
Richard Mangold's Avatar
Richard Mangold Richard Mangold is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Niles, IL
Posts: 111
Default Re: Main Panel vs Sub-Panel and main disconnect?

Tim,
If metal conduit is used, the metal conduit serves as the ground conductors. This is common in the Chicago area



Rich Mangold
RCM Home Inspections, LLC
www.RCMHomeInspections.com
Email: Rich@RCMHomeInspections.com
Phone: 847-698-5993
Reply With Quote
  #9  
Old 10/20/09, 6:33 PM
Tim Larsen Tim Larsen is offline
InterNACHI Member
 
Join Date: Mar 2009
Location: Central Vermont
Posts: 139
Default Re: Main Panel vs Sub-Panel and main disconnect?

Thanks Richard. I thought of that, but couldn't see how the conduits/panel were bonded.

Tim
Reply With Quote
  #10  
Old 10/20/09, 6:35 PM
Tim Larsen Tim Larsen is offline
InterNACHI Member
 
Join Date: Mar 2009
Location: Central Vermont
Posts: 139
Default Re: Main Panel vs Sub-Panel and main disconnect?

Scratch that - bonded at meter. I'm a little slow today...

Tim
Reply With Quote
  #11  
Old 10/20/09, 10:54 PM
Robert L. Bassett Robert L. Bassett is offline
InterNACHI Member
 
Join Date: Oct 2009
Posts: 13
Default Re: Main Panel vs Sub-Panel and main disconnect?

Thanks to all for your comments. They have been very useful!
Bob Bassett
Reply With Quote
  #12  
Old 10/24/09, 7:16 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Default Re: Main Panel vs Sub-Panel and main disconnect?

Check the breaker brands, They may not be the allowable ones for that panel brand
I see some "color" wire on the neutral buss... too

Just my .05 cents..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Electric Panel dmozzillo Electrical Inspections 26 1/26/09 2:18 PM
Main disconnect at meter instead of main panel. OK? kshepard Electrical Inspections 14 11/8/06 7:24 PM
Disconnect and Main panel srowe Electrical Inspections 10 6/13/06 8:49 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 6:31 PM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts