How would you report the following pertaing to the main SEC?
(See Photo) Secondly, The microwave is wired to the junction box in the cabinet. Again how would you report on the wiring. |
|
#2
|
||||
|
||||
|
I see broken strands in the second photo. So you might want to defer this for further analysis, and repair as necessary, by a qualified electrician.
As for the microwave, it appears the appliance cord has been 'modified' which is once again beyond your HI's ability to verify. Electrician time. IMHO, tom |
|
#3
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Why is there a SER running (4 wire) to the service disconnect? Is this a load side panel (upstream disconnect)? If so there may be bigger issues than the improper lug. Maybe a "defer" is in order
|
|
#4
|
|||
|
|||
|
Please Note:
jkogel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Evidence of unprofessional or unconventional workmanship, which may be unsafe or a fire hazard. Call for repair not just evaluation. We don't need to analyze it any more than that.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Neutral bus bar failed inspection | Greg Moritz | Electrical Inspections | 18 | 1/19/08 1:53 PM |
| Main disconnect at meter instead of main panel. OK? | kshepard | Electrical Inspections | 14 | 11/8/06 6:24 PM |
| Main Electrical Shut-off? | jpassailaigue | General Inspection Discussion | 10 | 3/24/06 2:19 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |