Default Main service disconnect/panel question

Having a hard time posting pic, but anyway... Do the grounds & neutrals need to be tied together at the main service disconnect? or on the same neutral bus bar?
The neutrals were separated on the main panel neutral bus bars (which were bonded w/green screw) and the grounds were on separate bus bars (which were also bonded to the panel) attached to the panel.

Thanks in advance.
Reply With Quote
Need a home inspection in Pennsylvania? Check out InterNACHI's listing of Pennsylvania certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/27/11, 10:25 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,057
Default Re: Main service disconnect/panel question

As long as both are bonded to the enclosure at the service panel, it has been done properly. When they are both bonded to the enclosure, they ARE tied together.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net



Last edited by jpope; 7/27/11 at 10:59 AM..
Reply With Quote
  #3  
Old 7/27/11, 10:36 AM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Main service disconnect/panel question

Thanks for the confirmation, Jeff.
Reply With Quote
  #4  
Old 7/27/11, 12:41 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main service disconnect/panel question

They don't need to be on the same bar in a service panel. Typically in a service panel they will be because it would cost extra to add an auxillary ground buss.

Any panel besides a service panel would require the grounded and grounding to be isolated from each other.
Reply With Quote
  #5  
Old 7/27/11, 4:51 PM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main service disconnect/panel question

Quote:
Originally Posted by jfrederick View Post
Having a hard time posting pic, but anyway... Do the grounds & neutrals need to be tied together at the main service disconnect? or on the same neutral bus bar?
The neutrals were separated on the main panel neutral bus bars (which were bonded w/green screw) and the grounds were on separate bus bars (which were also bonded to the panel) attached to the panel.

Thanks in advance.

Your installation is fine as long as the panel contains the service disconnecting means and that there are no neutrals connected to the equipment grounding bus which would cause neutral current to flow on the enclosure.
Reply With Quote
  #6  
Old 7/27/11, 10:22 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 8,848
Default Re: Main service disconnect/panel question

Quote:
Originally Posted by Robert Meier View Post
Your installation is fine as long as the panel contains the service disconnecting means and that there are no neutrals connected to the equipment grounding bus which would cause neutral current to flow on the enclosure.

I think we're talking service equipment with the service disconnect...



InterNachi Awards Portal: http://co.nachi.org/inachiawards/

____________________________________________
"An Education, not just an Inspection"

Larry Kage, CMI
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector serving the Traverse City, Michigan area and beyond.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Home Inspector Listings jbowman Miscellaneous Discussion for Inspectors 230 3/21/12 9:35 PM
Mold Inspectors in Coeur d’Alene, ID 83815 rspriggs Ancillary Inspection Services & Additional Topics 15 1/3/12 1:14 PM
Adequate service size....oh, and a GFCI question ksherstobetoff Electrical Inspections 13 2/8/07 1:18 PM
Main service disonnect question jmichalski Electrical Inspections 5 1/29/06 4:32 PM


All times are GMT -4. The time now is 7:41 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts