Default Main service disonnect question

Came across this this morning and I am not sure how to report it mostly because I have not encountered it before.

The meter is a fairly recent installation. The panel below has no main disconnect within the panel, and the dual pole 50 Amp breaker above is labelled as the main disconnect and the connections are set up as such (from the meter, to the 50A, to the main lugs in the panel.

a) Is this set up kosher? I cannot immediately find any reason it would not be, but I also do not know the NEC inside and out.

b) Is the 50A breaker large enough? It doesn't seem to be, but I am also looking for some source to cite to support that assessment.
Attached Thumbnails
main-service-disonnect-question-dscn0430.jpg  
Reply With Quote
  #2  
Old 1/28/06, 5:28 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Main service disonnect question

Really can't tell much from that picture, but the visible breaker does not appear to be a service disconnect as the feed comes from the panel on the left.

The entire set-up looks pretty Mickey Mouse.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 1/28/06, 8:59 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main service disonnect question

Joe:

Panelboards inside of cabinets that are mounted sideways present a defect related to the "ON" and "OFF" position where one row will be incorrect.

Suggest that this looks like a "bootlegged" job by someone who was unaware of the correct methods for this type of installation.

When a Meter Socket Enclosure is used like this one was, it too is required to be inspected, from the looks of this an inspection probably didn't take place.
Reply With Quote
  #4  
Old 1/28/06, 10:39 PM
jmichalski's Avatar
jmichalski jmichalski is offline
Active Poster
 
Join Date: Aug 2004
Location: Souderton, PA
Posts: 2,532
Please Note: jmichalski is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main service disonnect question

Thanks guys. The visible breaker is labeled as a main service disconnect, and is fed from a socket that connects directly to the side of the box surrounding the meter (hard to see). The feed I think you are referring to Jeff, is what I saw as the connection to the main lugs in the panel.

Evaluation was recommended.

Thank you both!
Reply With Quote
  #5  
Old 1/29/06, 3:51 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Main service disconnect question

Quote:
Originally Posted by jmichalski
a) Is this set up kosher? I cannot immediately find any reason it would not be, but I also do not know the NEC inside and out.
Actually it's okay to have a separate main disconnect switch and distribution panel. But the main disconnect would need to be rated for service equipment, which appears to be questionable. Needs to be looked at more closely to see if it's rated for that.

Quote:
Originally Posted by jmichalski
b) Is the 50A breaker large enough? It doesn't seem to be, but I am also looking for some source to cite to support that assessment.
The 50A service capacity is probably totally inadequate for anything other than a small seasonal bungalow. An electrical service for a smaller house should be at least 100A (which is also the minimum service required by IRC E3502.1 or NEC 230.79.C for all houses). For larger homes or those with significant electrical equipment (e.g. stoves, dryers, HVAC systems) it should be 150A to 200A.

An electrical professional can perform a service capacity calculation to check if the service is inadequate (e.g. using NEC 220.31), but it may be a no-brainer depending on the type of house and typical electrical equipment.

P.S. Is that photo of the service equipment sideways? If not JT has a good point about the likelyhood of the panel breakers on one side (e.g. the top row) incorrectly having up as the "off" position.

JMO and 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 1/29/06 at 4:32 PM..
Reply With Quote
  #6  
Old 1/29/06, 4:32 PM
Dean Call Dean Call is offline
New User
 
Join Date: Jan 2005
Posts: 23
Please Note: Dean Call is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main service disconnect question

Quote:
Originally Posted by roconnor
.............
P.S. Is that photo of the service equipment sideways?...................
I'm thinking the picture needs to be rotated because of the words "below" and "above" stated.

Quote:
Originally Posted by jmichalski
The panel below has no main disconnect within the panel, and the dual pole 50 Amp breaker above is labelled...................."
Attached Thumbnails
main-service-disonnect-question-rotated.jpg  
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
question on electrical service Coral Chesney Electrical Inspections 6 2/24/07 9:35 AM
Adequate service size....oh, and a GFCI question ksherstobetoff Electrical Inspections 13 2/8/07 1:18 PM
Metal Rigid or PVC Rigid what is code bpotts Electrical Inspections 5 12/4/06 2:40 PM
PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. gromicko Miscellaneous Discussion for Inspectors 53 8/30/06 5:58 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 4:55 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts