Came across this this morning and I am not sure how to report it mostly because I have not encountered it before.
The meter is a fairly recent installation. The panel below has no main disconnect within the panel, and the dual pole 50 Amp breaker above is labelled as the main disconnect and the connections are set up as such (from the meter, to the 50A, to the main lugs in the panel. a) Is this set up kosher? I cannot immediately find any reason it would not be, but I also do not know the NEC inside and out. b) Is the 50A breaker large enough? It doesn't seem to be, but I am also looking for some source to cite to support that assessment. |
|
#2
|
||||
|
||||
|
Really can't tell much from that picture, but the visible breaker does not appear to be a service disconnect as the feed comes from the panel on the left.
The entire set-up looks pretty Mickey Mouse. IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ® Jeff PopeJPI Home Inspection Service Santa Clarita CA (661) 212-0738 Santa Clarita Home Inspection http://www.MyInspector.net |
|
#3
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Joe:
Panelboards inside of cabinets that are mounted sideways present a defect related to the "ON" and "OFF" position where one row will be incorrect. Suggest that this looks like a "bootlegged" job by someone who was unaware of the correct methods for this type of installation. When a Meter Socket Enclosure is used like this one was, it too is required to be inspected, from the looks of this an inspection probably didn't take place. |
|
#4
|
||||
|
||||
|
Please Note:
jmichalski is a non-member guest and is in no way affiliated with InterNACHI or its members.
Thanks guys. The visible breaker is labeled as a main service disconnect, and is fed from a socket that connects directly to the side of the box surrounding the meter (hard to see). The feed I think you are referring to Jeff, is what I saw as the connection to the main lugs in the panel.
Evaluation was recommended. Thank you both! |
|
#5
|
||||
|
||||
|
Quote:
Quote:
An electrical professional can perform a service capacity calculation to check if the service is inadequate (e.g. using NEC 220.31), but it may be a no-brainer depending on the type of house and typical electrical equipment. P.S. Is that photo of the service equipment sideways? If not JT has a good point about the likelyhood of the panel breakers on one side (e.g. the top row) incorrectly having up as the "off" position. JMO and 2-nickels ... Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... Last edited by roconnor; 1/29/06 at 4:32 PM.. |
|
#6
|
|||
|
|||
|
Please Note:
Dean Call is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| question on electrical service | Coral Chesney | Electrical Inspections | 6 | 2/24/07 9:35 AM |
| Adequate service size....oh, and a GFCI question | ksherstobetoff | Electrical Inspections | 13 | 2/8/07 1:18 PM |
| Metal Rigid or PVC Rigid what is code | bpotts | Electrical Inspections | 5 | 12/4/06 2:40 PM |
| PIC of State Rep and sponsor of new NACHI H.I. Bill in NH. | gromicko | Miscellaneous Discussion for Inspectors | 53 | 8/30/06 5:58 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |