Correct size wire(s) for 200 amp breaker? Anyone have wire sizing chart? Thanks in advance.
|
| Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#2
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
3/0 in Canada
|
|
#3
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
NEC, 200 amps=#2/0 Copper or #4/0 Aluminum, #2 cu=125 amps, all with some restrictions. Table 310.15(B)(6)-2008 NEC.
|
|
#4
|
|||
|
|||
|
So to answer my first question?? Is this 2/0 in the picture(s)?
|
|
#5
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Looks like #2 Copper, from photo {2 AWG}.
|
|
#6
|
|||
|
|||
|
Again I ask, Is this the correct wire size for 200 amp breaker and/or what is the difference between #2 and 2/0?? Thanks.
|
|
#7
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Did you read post #3? The answer is no for 200 amps.
|
|
#8
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
2/0 (two naught) pronounced "two not" is a larger wire and will carry the 200 amps by your codes. #2 is good for up to 125 A depending its installation, configuration e.g. in open air, in a raceway, in a 3 wire cable, etc.
|
|
#9
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
#1/0=0 #2/0=00 #3/0=000 #4/0=0000 After #4/0 the wire sizes start with their circular mil area in thousands. |
|
#10
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
naught /nɔt/ Show Spelled[nawt] Show IPA –noun 1. nothing. 2. a cipher (0); zero Last edited by Brian A. MacNeish; 7/12/11 at 10:13 AM.. |
|
#11
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Go to the electrical supply house here and say "I need some three naught". First they look at you really funny then they say "you must be Canadian". |
|
#13
|
||||
|
||||
|
Quote:
Quote:
. Robert O'Connor, PE Consulting Engineer & Inspector LIU CW Post Adjunct Professor NACHI Education Committee www.reporthost.com/-rjo I am absolutely amazed sometimes by how much thought goes into doing things wrong ... |
| Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
|||
|
|||
|
Please Note:
Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| What wire size and breaker for heater??? | Dan Bolton | Inspecting HVAC Systems | 3 | 12/17/10 7:51 PM |
| 4 wire for main panel? | mnahrgang | Electrical Inspections | 2 | 8/24/09 5:54 PM |
| Wire size? | nbhi | Electrical Inspections | 50 | 3/4/08 1:10 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 9:26 PM |