Correct size wire(s) for 200 amp breaker? Anyone have wire sizing chart? Thanks in advance.
Attached Thumbnails
main-wire-size-900-n.-lane-defiance-055.jpg   main-wire-size-900-n.-lane-defiance-056.jpg   main-wire-size-900-n.-lane-defiance-057.jpg  
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #2  
Old 7/12/11, 6:09 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main wire size

Quote:
Originally Posted by jfrederick View Post
Correct size wire(s) for 200 amp breaker? Anyone have wire sizing chart? Thanks in advance.
3/0 in Canada
Reply With Quote
  #3  
Old 7/12/11, 7:01 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main wire size

NEC, 200 amps=#2/0 Copper or #4/0 Aluminum, #2 cu=125 amps, all with some restrictions. Table 310.15(B)(6)-2008 NEC.
Reply With Quote
  #4  
Old 7/12/11, 7:06 AM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Main wire size

Quote:
Originally Posted by Robert Meier View Post
NEC, 200 amps=#2/0 Copper or #4/0 Aluminum, #2 cu=125 amps, all with some restrictions. Table 310.15(B)(6)-2008 NEC.
So to answer my first question?? Is this 2/0 in the picture(s)?
Reply With Quote
  #5  
Old 7/12/11, 7:14 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main wire size

Looks like #2 Copper, from photo {2 AWG}.

Reply With Quote
  #6  
Old 7/12/11, 7:21 AM
Joshua L. Frederick Joshua L. Frederick is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Defiance, OH
Posts: 832
Send a message via AIM to jfrederick
Default Re: Main wire size

Quote:
Originally Posted by Robert Meier View Post
Looks like #2 Copper, from photo {2 AWG}.
Again I ask, Is this the correct wire size for 200 amp breaker and/or what is the difference between #2 and 2/0?? Thanks.
Reply With Quote
  #7  
Old 7/12/11, 7:41 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main wire size

Quote:
Originally Posted by jfrederick View Post
Again I ask, Is this the correct wire size for 200 amp breaker and/or what is the difference between #2 and 2/0?? Thanks.
Did you read post #3? The answer is no for 200 amps.
Reply With Quote
  #8  
Old 7/12/11, 7:48 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main wire size

Quote:
Originally Posted by jfrederick View Post
Again I ask, Is this the correct wire size for 200 amp breaker and/or what is the difference between #2 and 2/0?? Thanks.
2/0 (two naught) pronounced "two not" is a larger wire and will carry the 200 amps by your codes. #2 is good for up to 125 A depending its installation, configuration e.g. in open air, in a raceway, in a 3 wire cable, etc.
Reply With Quote
  #9  
Old 7/12/11, 7:58 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main wire size

Quote:
Originally Posted by Brian A. MacNeish View Post
2/0 (two naught) pronounced "two not" is a larger wire and will carry the 200 amps by your codes. #2 is good for up to 125 A depending its installation, configuration e.g. in open air, in a raceway, in a 3 wire cable, etc.
In the US wire sizes bigger than #1 go by zero's or aught (pronounced ought) a derivative of naught.

#1/0=0
#2/0=00
#3/0=000
#4/0=0000

After #4/0 the wire sizes start with their circular mil area in thousands.
Reply With Quote
  #10  
Old 7/12/11, 10:00 AM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main wire size

Quote:
Originally Posted by Robert Meier View Post
In the US wire sizes bigger than #1 go by zero's or aught (pronounced ought) a derivative of naught.

#1/0=0
#2/0=00
#3/0=000
#4/0=0000

After #4/0 the wire sizes start with their circular mil area in thousands.
I still say "naught" .........we keep dropping letters/words. Pretty soon we'll all be writing like our kids text language.....R U OK w/ that?

naught

   /nɔt/ Show Spelled[nawt] Show IPA
–noun 1. nothing.

2. a cipher (0); zero

Last edited by Brian A. MacNeish; 7/12/11 at 10:13 AM..
Reply With Quote
  #11  
Old 7/12/11, 10:13 AM
Robert Meier's Avatar
Robert Meier Robert Meier is online now
Active Poster
 
Join Date: Feb 2010
Location: New Jersey
Posts: 1,250
Please Note: Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main wire size

Quote:
Originally Posted by Brian A. MacNeish View Post
I still say "naught" .........we keep dropping letters/words. Pretty soon we'll all be talking like our kids text language.....R U OK w/ that?

naught

   /nɔt/ Show Spelled[nawt] Show IPA
–noun 1. nothing.

2. a cipher (0); zero

It's all good.

Go to the electrical supply house here and say "I need some three naught". First they look at you really funny then they say "you must be Canadian".
Reply With Quote
  #12  
Old 7/12/11, 12:25 PM
Robert Ernst Robert Ernst is offline
InterNACHI Member
 
Join Date: Sep 2010
Location: Sparks,NV
Posts: 654
Default Re: Main wire size

Wow and the whole time I thought it was "Ought".
aught or ought 2 (ɔːt) n a less common word for nought
Reply With Quote
  #13  
Old 7/12/11, 2:02 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Main wire size

Quote:
Originally Posted by Robert Meier View Post
Go to the electrical supply house here and say "I need some three naught".
That would be like asking for "three goose egg" wire ... ... but maybe they would look at us just as funny if we went into a canuck supply house and asked for "three ought" wire ... they might say "dont ya mean ya want some three naught wire ... ehhhh" ... .

Quote:
Originally Posted by jfrederick View Post
Correct size wire(s) for 200 amp breaker? Anyone have wire sizing chart? Thanks in advance.
Get yourself a copy of Code Check, which has the attached table and a bunch of other usefull basic code info for HI's. With that table keep in mind that you can get more out of wires in conduit, and it doesn't necessarily apply to AC condenser circuits (check the nameplate for that).

.
Attached Thumbnails
main-wire-size-wire-sizing-table-code-check.jpg  



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...
Reply With Quote
Need a home inspection in South Dakota? Check out InterNACHI's listing of South Dakota certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine.
  #14  
Old 7/12/11, 2:23 PM
Brian A. MacNeish Brian A. MacNeish is offline
Banned
 
Join Date: Apr 2007
Location: CANADA
Posts: 4,638
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Main wire size

Quote:
Originally Posted by rernst1 View Post
Wow and the whole time I thought it was "Ought".
aught or ought 2 (ɔːt) n a less common word for nought
It probably is but I used 3 naught!
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
What wire size and breaker for heater??? Dan Bolton Inspecting HVAC Systems 3 12/17/10 7:51 PM
4 wire for main panel? mnahrgang Electrical Inspections 2 8/24/09 5:54 PM
Wire size? nbhi Electrical Inspections 50 3/4/08 1:10 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 7:41 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts