Default Main wire verification

Panel has 100 amp main but the main service wires appear to be 60 Amp.

Can you tell from the pics if the service wires are 60 amps?

House was built in 1955. Those are the original and appears that the electrician didnt update the main wires.

I attached the sub panel just for your viewing pleasure. It took my 10 minutes to remove the rusted screw. Harry home owner special.

Thanks

Dave

Last edited by dmacy; 10/17/07 at 8:05 AM..
Reply With Quote
  #2  
Old 1/28/06, 5:23 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Main wire verification

The cloth and rubber (if that's what it is) covered wires should be replaced regardless of their capacity. It's difficult to tell what size they actually are.

The third picture is a Federal Pacific panel board. Enough said there.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #3  
Old 1/29/06, 5:09 PM
Robert J. OConnor's Avatar
Robert J. OConnor Robert J. OConnor is offline
InterNACHI Member
 
Join Date: Jul 2003
Location: Long Island, NY
Posts: 1,288
Default Re: Main wire verification

For a 100A service, #4 Cu service feeder wires would be required (may be close). However, the condition of the service feeders does seem to be questionable, but may be functional.

There also needs to be retainer clips on that 100A main breaker/disconnect as it's a "backfed" service panel, so the main breaker can't come out of the panel still live (don't really see that retainer clip, but maybe I need glasses ... lol).

JMO & 2-nickels ...



Robert O'Connor, PE
Consulting Engineer & Inspector
LIU CW Post Adjunct Professor
NACHI Education Committee
www.reporthost.com/-rjo

I am absolutely amazed sometimes by how much thought goes into doing things wrong ...

Last edited by roconnor; 1/29/06 at 5:14 PM..
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Nice Report on AL Wire Terminations - Enjoy pabernathy Electrical Inspections 0 7/2/07 12:35 PM
Proper Marr Connectors for Aluminum Pigtails jskrypka Canadian Inspectors 5 3/25/07 10:41 PM
Main Electrical Shut-off? jpassailaigue General Inspection Discussion 10 3/24/06 2:19 PM
Bad electrical problem Pest Guy Electrical Inspections 4 1/20/06 9:26 PM


All times are GMT -4. The time now is 4:55 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts