Default Manufactured home main pull

Hi all
I did another manufactured home today and the power was off. The main panel in the home was OFF. There was a large box with just one switch outside that said main 200 and that was still ON visibly. Does that mean there was power still on between the outside main and the inside panel main?
Thanks
I don't have pic of the outside.
Attached Thumbnails
manufactured-home-main-pull-kenny-cottage-048-small-.jpg.jpg
Views:	84
Size:	42.9 KB
ID:	3034  
Reply With Quote
  #2  
Old 4/21/06, 8:40 PM
Andy T. Bishop Andy T. Bishop is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Allegan, MI
Posts: 321
Default Re: Manufactured home main pull

Sorry wrong pic
Here
Attached Thumbnails
manufactured-home-main-pull-clark-048-small-.jpg.jpg
Views:	114
Size:	62.6 KB
ID:	3035  
Reply With Quote
  #3  
Old 4/21/06, 8:47 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Manufactured home main pull

If the exterior was in the "on" position there was power to the lugs on the breaker indoors. unless the meter was off. Mobile homes are required to have an outdoor disconnect like you described.
Reply With Quote
  #4  
Old 4/21/06, 9:02 PM
Andy T. Bishop Andy T. Bishop is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Allegan, MI
Posts: 321
Default Re: Manufactured home main pull

That is what i thought. I just wanted to hear someone else say it.
Thanks
Reply With Quote
  #5  
Old 4/21/06, 10:59 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Manufactured home main pull

Hmmm. No EGC from the service panel?



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #6  
Old 4/22/06, 12:21 AM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 713
Default Re: Manufactured home main pull

Quote:
Originally Posted by jpope
Hmmm. No EGC from the service panel?
The ground and the neutral are seperated (floating) and it appears that grounding conductor is sheathed (THHN?) which will run throught conduit to the main service disconnect panel on the exterior at pole. That panel has the EGC that connects to the rods.

The wire is stealth like as it blends in with the other hot conductors.....hmmm should have been green....at least some green tape identifying it.

Harold
Miller Home Inspection
Reply With Quote
  #7  
Old 4/22/06, 12:18 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Manufactured home main pull

That conductor looks too small for the equipment grounding conductor (EGC) which should be sized according to 250.122. It should be 6 AWG copper, and as you said, green or bare copper.

The conductor connected to "the rods" is the grounding electrode conductor (GEC), and as you said, it is located at the service disconnect.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #8  
Old 4/24/06, 10:56 PM
Harold E. Miller's Avatar
Harold E. Miller Harold E. Miller is offline
InterNACHI Member
 
Join Date: Feb 2006
Location: Camano Island, WA
Posts: 713
Default Re: Manufactured home main pull

Jeff,
Ya, it is hard to tell from the picture, but I think you are right. It is probably only 8 guage. Little too small for the application.
Reply With Quote
  #9  
Old 4/24/06, 11:39 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Manufactured home main pull

Andy, what is the rating of the interior panel?
Reply With Quote
  #10  
Old 4/25/06, 10:02 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Manufactured home main pull

My point is the feeders look like 100 amp feeders, the panel looks like a 100 amp panel. So the EGC is sized properly, however the main disconnect should be only 100 amps.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
American Home Inspection Service Area jmckenna1 Miscellaneous Discussion for Inspectors 3 9/4/06 7:23 PM
Common Defects List by Age of House trausch Inspection Education & Training 10 6/12/06 4:52 AM