Default to many amps

200 amp panel with 760 total amps in breakers. Seimens panel with worn label. how many amps is to much for a 200amp/240v panel.
Reply With Quote
  #2  
Old 7/13/08, 11:20 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: to many amps

No limit but that (760)does not sound right.

Did you add up all double pole 240V breaker using the printed amps on each half of the breaker? ie count up 60 for a 30 amp 240V breaker?

List SF of house and equipment present.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 7/14/08, 6:27 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: to many amps

Adding up the breakers is ABSOLUTELY meaningless.

It is not uncommon to have 600-800 amps worth of breakers in a 200 amp panel.
This means they ran all 20A circuits, or a mix and several larger. Again, this means nothing.
Reply With Quote
  #4  
Old 7/14/08, 6:53 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: to many amps

Seth,

How long have you adding the sum of breakers in a SE?

As Speedy states....it's meaningless.
Reply With Quote
  #5  
Old 7/14/08, 8:20 AM
Seth Hegert's Avatar
Seth Hegert Seth Hegert is offline
InterNACHI Member
 
Join Date: Jun 2006
Location: Ellijay, GA
Posts: 17
Default Re: to many amps

I do not usually add them up. this house is a 2/2 with a garage. It just seemed to high to me for this particular house. Thanks for the posts and back up.
seth
Reply With Quote
  #6  
Old 7/17/08, 9:34 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: to many amps

Assuming none of the breakers (main or branch) have been tripping regularly, the sum of the breaker ratings is of no consequence. Usually it is just the sign of a very conservative installation. As an extreme example, for all we know each of those 20 amp breakers is serving only one duplex outlet. That is approximately the case in some areas of my house.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #7  
Old 7/19/08, 10:30 PM
George P. Wells, CMI's Avatar
George P. Wells, CMI George P. Wells, CMI is offline
InterNACHI Member
 
Join Date: Oct 2004
Location: Michigan
Posts: 554
Send a message via Skype™ to gwells
Default Re: to many amps

Quote:
Originally Posted by shegert
200 amp panel with 760 total amps in breakers. Seimens panel with worn label. how many amps is to much for a 200amp/240v panel.
Seth,

That's not unusual. There is a difference between connected load and demand load. The demand load takes many factors into consideration. For example, if you have both a heating load and a cooling load, they are are not both included in the demand at the same time. They are called "non-coincident" loads because you would not typically run both at the same time.

We have a Residential Electrical Service Size Calculator that is in the Free Stuff section of our website. If you subscribe to the free Tips for Success newsletter, you will automatically get access to the Free Stuff section.

The calculator is in the form of a Excel file. You do not need to have any knowledge of electrical systems or electrical codes to use it. I created the calculator mainly for home inspectors and others who are interested in knowing how to size a residential electrical service.

The calculator will tell you the demand load, the closest standard service size, conductor sizes for Cu and Al, and conduit size. The NEC does not use the same table for service conductor ampere ratings as for feeder and branch circuit conductors.

There are also some other electrical teaching calculators in the Free Stuff section.



BestInspectors.Net
& Real Estate Training Academy

Inspection Report Software for
Windows - iOS - Mac - Android

Continuing Education
Home and Commercial Building Inspection - Skilled Trades – Real Estate – Appraisal – NFPA 921

http://www.bestinspectors.net

est. 1992
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Updated panel 200 amps most outlets two pronged? Jay Nel Electrical Inspections 8 7/13/08 10:24 PM
What size Amps is this panel smcintire Electrical Inspections 4 5/22/08 4:33 PM
Sub Panel Amps mtimpani Electrical Inspections 7 10/1/06 9:47 AM
How many Amps??? psmothers Electrical Inspections 7 8/9/06 2:01 PM
Another Service Entrance Amps Question pdickerson Electrical Inspections 2 8/7/06 3:39 PM


All times are GMT -4. The time now is 4:55 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts