Default How many EGC under one screw?

Is there a limit? Or can you like the picture shows, stuff as many as you can get in..........Cutler Hammer 100 amp panel.
Attached Thumbnails
many-equipment-grounding-conductor-under-one-screw-505-pleasant-st-198-small-.jpg.jpg
Views:	141
Size:	49.1 KB
ID:	30509  

Last edited by gwilcox; 8/2/09 at 9:50 AM.. Reason: Added more info
Reply With Quote
Find an InterNACHI certified Oregon Home Inspector (and anywhere else in North America)
  #2  
Old 8/2/09, 8:47 AM
Bobby Hamilton's Avatar
Bobby Hamilton Bobby Hamilton is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Austintown, OH
Posts: 1,246
Default Re: How many EGC under one screw?

The panel will tell you how many and of what size can go underneath one of the screws. Just looking at the pic, I would say there are too many.



Bobby Hamilton
Bloodhound Home Inspection Services
Youngstown Home Inspection
Austintown Ohio Home Inspection


Providing home inspections, state licensed termite inspections and radon testing in Youngstown, Boardman, Canfield, Poland, Howland, Warren and surrounding Northeast Ohio areas.
Reply With Quote
  #3  
Old 8/2/09, 2:01 PM
Gerald C. Wilcox's Avatar
Gerald C. Wilcox Gerald C. Wilcox is offline
InterNACHI Member
 
Join Date: Jan 2007
Location: Harvey, ND
Posts: 333
Default Re: How many EGC under one screw?

bump
Reply With Quote
  #4  
Old 8/2/09, 2:32 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: How many EGC under one screw?

Usually no more than 3.

"The product standard(UL 67-Clause 17.2.6) allows multiple equipment grounding conductors, but not more than 3 No.10 AWG or smaller in a single opening in a wire terminal."



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #5  
Old 8/6/09, 2:31 AM
rbibler rbibler is offline
Active Poster
 
Join Date: Nov 2008
Location: Healdsburg Ca
Posts: 1,114
Please Note: rbibler is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many EGC under one screw?

I will call it if there is more then one.

Best

Ron

Last edited by rbibler; 8/6/09 at 3:00 AM..
Reply With Quote
  #6  
Old 8/6/09, 7:06 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: How many EGC under one screw?

Quote:
Originally Posted by ccurrins View Post
Usually no more than 3.

"The product standard(UL 67-Clause 17.2.6) allows multiple equipment grounding conductors, but not more than 3 No.10 AWG or smaller in a single opening in a wire terminal."
A agree.
Reply With Quote
  #7  
Old 8/6/09, 7:07 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,681
Default Re: How many EGC under one screw?

Quote:
Originally Posted by rbibler View Post
I will call it if there is more then one.

Best

Ron
Ron, I believe you are referring to neutrals. 3 grounds can be placed under one screw.
Reply With Quote
  #8  
Old 8/6/09, 12:41 PM
Mark Thorman Mark Thorman is offline
Unmoderated Guest
 
Join Date: Mar 2008
Posts: 392
Please Note: Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many EGC under one screw?

I would call out the black wire also.

www.MauiHomeInspections.com
Reply With Quote
  #9  
Old 8/6/09, 1:09 PM
Jim Port Jim Port is offline
Unmoderated Guest
 
Join Date: Jul 2007
Location: Maryland
Posts: 805
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many EGC under one screw?

Quote:
Originally Posted by dvalley View Post
Ron, I believe you are referring to neutrals. 3 grounds can be placed under one screw.
This is not always the case for grounding wires. The label would really need to be checked for the quantity and size ranges acceptable.

Neutrals, 1 wire per hole.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Bonding Screw kmalone Electrical Inspections 25 4/6/08 6:16 PM
Screw Jacks Advice- Log Home thance Structural Inspections 18 3/31/08 10:48 PM
Subpanel Bonding Screw away Electrical Inspections 24 1/9/08 2:46 PM
Screw jack support? sfalvey Structural Inspections 5 6/12/06 6:09 PM
Panel screw hits a live wire rwand1 Electrical Inspections 23 4/3/06 5:50 PM


All times are GMT -4. The time now is 7:42 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts