Is there a limit? Or can you like the picture shows, stuff as many as you can get in..........Cutler Hammer 100 amp panel.
"He is no fool who gives what he cannot keep to gain that which he cannot lose." Jim Elliot 1949 Gerald Wilcox Harvey, ND CMIA, RMT www.housecheckhomeinspections.com www.homeinspectorinnorthdakota.com 701.324.4075 Minot, ND Home Inspections Devil's Lake, ND Home Inspections Bismarck, ND Home Inspections Jamestown, ND Home Inspections Home Inspector in North Dakota North Dakota Home Inspection Last edited by gwilcox; 8/2/09 at 9:50 AM.. Reason: Added more info |
| Find an InterNACHI certified Oregon Home Inspector (and anywhere else in North America) |
|
#2
|
||||
|
||||
|
The panel will tell you how many and of what size can go underneath one of the screws. Just looking at the pic, I would say there are too many.
Bobby Hamilton Bloodhound Home Inspection Services Youngstown Home Inspection Austintown Ohio Home Inspection Providing home inspections, state licensed termite inspections and radon testing in Youngstown, Boardman, Canfield, Poland, Howland, Warren and surrounding Northeast Ohio areas.
|
|
#3
|
||||
|
||||
|
bump
"He is no fool who gives what he cannot keep to gain that which he cannot lose." Jim Elliot 1949 Gerald Wilcox Harvey, ND CMIA, RMT www.housecheckhomeinspections.com www.homeinspectorinnorthdakota.com 701.324.4075 Minot, ND Home Inspections Devil's Lake, ND Home Inspections Bismarck, ND Home Inspections Jamestown, ND Home Inspections Home Inspector in North Dakota North Dakota Home Inspection |
|
#4
|
||||
|
||||
|
Usually no more than 3.
"The product standard(UL 67-Clause 17.2.6) allows multiple equipment grounding conductors, but not more than 3 No.10 AWG or smaller in a single opening in a wire terminal." Christopher Currins Certified, Licensed Proudly serving the St.Louis Metro St. Charles, St. Peters, Maryland Heights, O'Fallon, Florrisant, MO Home Inspector BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
|
|
#5
|
|||
|
|||
|
Please Note:
rbibler is a non-member guest and is in no way affiliated with InterNACHI or its members.
I will call it if there is more then one.
Best Ron Last edited by rbibler; 8/6/09 at 3:00 AM.. |
|
#6
|
||||
|
||||
|
A agree.
|
|
#7
|
||||
|
||||
|
Ron, I believe you are referring to neutrals. 3 grounds can be placed under one screw.
|
|
#8
|
|||
|
|||
|
Please Note:
Mark Thorman is a non-member guest and is in no way affiliated with InterNACHI or its members.
|
|
#9
|
|||
|
|||
|
Please Note:
Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Neutrals, 1 wire per hole. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Bonding Screw | kmalone | Electrical Inspections | 25 | 4/6/08 6:16 PM |
| Screw Jacks Advice- Log Home | thance | Structural Inspections | 18 | 3/31/08 10:48 PM |
| Subpanel Bonding Screw | away | Electrical Inspections | 24 | 1/9/08 2:46 PM |
| Screw jack support? | sfalvey | Structural Inspections | 5 | 6/12/06 6:09 PM |
| Panel screw hits a live wire | rwand1 | Electrical Inspections | 23 | 4/3/06 5:50 PM |