Default How many splices in Panel

I was at a new home today and saw this crappy installation of the branch wiring (17 to 20 splices all crammed at the top of the panel). Is this something that you would write up? What would be the wording you would use if so? I tried to attach the picture but it was to big of a J-peg. If you know how to condense a j-peg file let me know and I will add it.

Thanks,

Spencer
Reply With Quote
  #2  
Old 4/3/08, 12:03 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: How many splices in Panel

Nothing wrong with splices in a panel.

Send me the pic and I'll post it inspectorjeff@sbcglobal.net



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #3  
Old 4/3/08, 12:08 AM
relliott's Avatar
relliott relliott is offline
Active Poster
 
Join Date: Aug 2006
Location: HARWOOD HTS, il
Posts: 8,570
Please Note: relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many splices in Panel

Download software for pic reduction after that , by downloading any one of a number of free graphic programs.
PM me if you want help.
Reply With Quote
  #4  
Old 4/3/08, 12:31 AM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 5,038
Default Re: How many splices in Panel

Here's the picture. Talk about an abortion. . .
Attached Thumbnails
many-splices-panel-img_0771.jpg  



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net
Reply With Quote
  #5  
Old 4/3/08, 1:01 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many splices in Panel

It is not filling a significant part of the wiring space so it is "legal". That sure looks like a screw up to me. They either left the wires short or had a copper theft and that was as high as the crack heads could reach.
Reply With Quote
  #6  
Old 4/3/08, 4:23 AM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many splices in Panel

"..... splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space."

What is happening to the industry, and why are people accepting this lousy crap and poor method of bootleg jobs done by hacks and hop heads!
Reply With Quote
  #7  
Old 4/3/08, 8:30 AM
Scott A. Figert Scott A. Figert is offline
InterNACHI Member
 
Join Date: Apr 2006
Location: Cecil, Oh
Posts: 163
Default Re: How many splices in Panel

Notice the main breaker at the "top" of the panel? Me either, did they install the panel upside down as well?



Scott A. Figert
www.sfigert.com
www.nachi.org NACHI #06042595
Figert Building Inspection, Ltd.
(419) 399-4472 Office & Home Sweet Home
Reply With Quote
  #8  
Old 4/3/08, 8:51 AM
Barry Adair's Avatar
Barry Adair Barry Adair is offline
InterNACHI Member
 
Join Date: Aug 2004
Location: TEXAS
Posts: 3,479
Default Re: How many splices in Panel

Not all MAIN are at the top of the panel here's a Square D from the other day



badair
ADAIR INSPECTION
972-487-5634

Residential-Commercial-Construction-EIFS-Infrared Thermography
TREC # 4563
EDI: EIFS-MA TX # 39

2008 US Member of the Year

life is the random lottery of events followed by numerous narrow escapes...accept the good

Last edited by badair; 6/2/09 at 1:56 AM..
Reply With Quote
  #9  
Old 4/3/08, 9:52 AM
Jim Port Jim Port is offline
Active Poster
 
Join Date: Jul 2007
Location: Maryland
Posts: 285
Please Note: Jim Port is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many splices in Panel

Quote:
Originally Posted by sfigert
Notice the main breaker at the "top" of the panel? Me either, did they install the panel upside down as well?
Since most mains operate in a horizontal orientation there is no right side up or upside down.

If the feed enters below the panel it would make sense to install it main down. Less wire to purchase and less gutter space is used.
Reply With Quote
  #10  
Old 4/3/08, 10:00 AM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 18,489
Default Re: How many splices in Panel

Here is a Cutler Hammer from a couple of weeks ago.
Attached Thumbnails
many-splices-panel-img_3983-small-.jpg.jpg
Views:	61
Size:	117.0 KB
ID:	20065  



"Never underestimate the difficulty of changing false beliefs by facts."
Henry Rosovsky-Harvard

Michael Larson
Hudson, WI

Services provided in East MN and West WI
InspectraPro
or
Minnesota Home Inspector

Reply With Quote
  #11  
Old 4/3/08, 10:47 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many splices in Panel

Quote:
Originally Posted by jtedesco1
"..... splices, and taps shall not fill the wiring space at any cross section to more than 75 percent of the cross-sectional area of that space."

What is happening to the industry, and why are people accepting this lousy crap and poor method of bootleg jobs done by hacks and hop heads!
What about the conductor fill of the plastic conduit...looks more than 75%?
Reply With Quote
  #12  
Old 4/3/08, 12:06 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many splices in Panel

We would be concerned that the fill was greater than 40% and would have to show that Table 4 in the NEC Chapter 9 was complied with along with Table 5. This mess should be referred to a qualified electrician
Reply With Quote
  #13  
Old 4/3/08, 12:30 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many splices in Panel

What is the fill allowance for a splice?
Reply With Quote
  #14  
Old 4/3/08, 1:35 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,908
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many splices in Panel

Greg: The 40% fill in the pipe was where we were with this question, not the splice.

Last edited by jtedesco1; 6/12/08 at 5:38 PM..
Reply With Quote
  #15  
Old 4/3/08, 2:11 PM
Mike Whitt's Avatar
Mike Whitt Mike Whitt is offline
Active Poster
 
Join Date: Sep 2005
Location: North Carolina
Posts: 474
Please Note: Mike Whitt is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many splices in Panel

Is that even an electrical conduit?

If it is a water pipe then all this other is for nill cause the pipe must be replaced which would mean that the complete installation would be addressed.

Also there should be a bushing on the end of the pipe which again would address the splices.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 11:18 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts