Hint: How many did you say?
With five different wiring methods installed in this box, including two electrical metallic tubings, two rigid nonmetallic conduits, one nonmetallic sheathed cable (Type NM-B), two surface metal raceways, and two Type AC cables, there is just not enough free space in this 4 inch x 1 1/4 inch square box. If we considered conductors sized at 12 AWG for each circuit, with two wires in each raceway, and cable, including an equipment grounding conductor in the RNMC and NM-B cable, we would end up with a total of 18 of the 12 AWG conductors, plus one additional for the three equipment grounding conductors, for a grand total of 19 conductors. As per Table 314.16(A), the maximum number of 12 AWG conductors allowed in this size metal box is only eight!
|
|
#2
|
||||
|
||||
|
It takes a lot of talent to get all those wires and connections in that box!
Too bad they didn't have more talent..... was the cover bulging out? |
|
#3
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
2005 NEC Reference: "300.14 Length of Free Conductors at Outlets, Junctions, and Switch Points At least 150 mm (6 in.) of free conductor, measured from the point in the box where it emerges from its raceway or cable sheath, shall be left at each outlet, junction, and switch point for splices or the connection of luminaires (fixtures) or devices. Where the opening to an outlet, junction, or switch point is less than 200 mm (8 in.) in any dimension, each conductor shall be long enough to extend at least 75 mm (3 in.) outside the opening. Exception: Conductors that are not spliced or terminated at the outlet, junction, or switch point shall not be required to comply with 300.14." |
|
#4
|
|||
|
|||
|
Heck, there's three unused knock-outs...that means three more wires can fit in there...
"not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#5
|
|||
|
|||
|
...and if the knock-outs are 3/4 inch, let's run a couple of 8/3 NM into it as well...
"not just an inspection, but an education" www.homesweethomecincinnati.com Democracy is two wolves and a lamb. Liberty is a well-armed lamb. B. Franklin |
|
#6
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Call the Posse out! I think this is a job for the NACHI Electrical Posse!
Where's that Sheriff when you need him? http://www.nachi.org/forum/users/pabernathy/ |
|
#7
|
|||
|
|||
|
lol....Joe YOU just HATE when I use my little tag lines....lol......You dont need the POSSE on this one....heck an Apprentice could get this one right...
Paul W. Abernathy |
|
#8
|
|||
|
|||
|
Oh my -- I took the cover off and found a box full of cat #3 phone wire and they had used old runs because it was easy. I am in real trouble now because I flagged it as a problem and it was not
Oh well live and learn - Next time I pull the cover plate - Crap I will probably get in trouble because that is probably invasive like taking the screws out of an attic hatch or the screws off of the panel on an electrical box. -- Just can't win Is it invasive because we walked into the home?? rlb |
|
#9
|
||||
|
||||
|
"...plus one additional for the three equipment grounding conductors..."
If you run EMT and/or rigid there is no need for grounding conductors. The conduit is the ground conductor. Guess we can get more wires in the box in the Chicago area BTW: What is the NEC's rule on number of hots / neutrals in a given conduit (by size of conduit, I would presume). Will Decker, CMI ILL License # 450.0002240 Board Certified Master Inspector Decker Home Services, LLC Chicago and Northern Suburban Home Inspections Office: (847) 676-8393 Cell: (847) 609-2345 Home: (847) 673-2702 wjd@DeckerHomeServices.com www.DeckerHomeServices.com Learn, Educate, Serve and have fun doing it! |
|
#10
|
|||
|
|||
|
Please Note:
brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Joe, they could add a box extension to ease things up, or maybe two.
|
|
#11
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
I included this scenario. |
|
#12
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Last edited by jtedesco1; 6/15/06 at 12:35 AM.. |
|
#13
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Hey Sheriff Paul, come on play along, I was referring to this installation.
http://www.nachi.org/forum/showpost....35&postcount=5 |
|
#14
|
|||
|
|||
|
lol.....you lost me Fella......I am not part of the Sheriff's Posse....I am a FOUNDING follower of the "INSANE" clown POSSE' on my brothers side....
Paul W. Abernathy |
|
#15
|
|||
|
|||
|
Are you looking for what I would advise the person to do.....honestly...I would tell them to take that freakin blank off.....add a 4" x 2 1/8" square extention ring and HOPE the wires meet the requirement...or they can wirenut and pigtail to get the length...they wont count in the calculation anyway... and replace the cover and be happy........about all I would tell them.
Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Wires ran from lugs to auxilary panels | Kevin Luce | Electrical Inspections | 7 | 9/20/07 9:24 AM |
| grounding wires | tvanvranken | Electrical Inspections | 14 | 3/16/07 7:24 AM |
| Wires and Junction at tub | mlong | Electrical Inspections | 8 | 11/18/06 12:29 PM |
| Ground Wires Inside a Panel | mveitenhans | Electrical Inspections | 13 | 10/29/06 11:39 AM |
| Painted service wires | hcavin | Electrical Inspections | 1 | 9/27/06 12:47 PM |