Default How many wires did you say were allowed?

Hint: How many did you say?



With five different wiring methods installed in this box, including two electrical metallic tubings, two rigid nonmetallic conduits, one nonmetallic sheathed cable (Type NM-B), two surface metal raceways, and two Type AC cables, there is just not enough free space in this 4 inch x 1 1/4 inch square box. If we considered conductors sized at 12 AWG for each circuit, with two wires in each raceway, and cable, including an equipment grounding conductor in the RNMC and NM-B cable, we would end up with a total of 18 of the 12 AWG conductors, plus one additional for the three equipment grounding conductors, for a grand total of 19 conductors. As per Table 314.16(A), the maximum number of 12 AWG conductors allowed in this size metal box is only eight!

Reply With Quote
  #2  
Old 6/7/06, 3:10 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,207
Default Re: How many wires did you say were allowed?

It takes a lot of talent to get all those wires and connections in that box!
Too bad they didn't have more talent.....

was the cover bulging out?
Reply With Quote
  #3  
Old 6/7/06, 4:25 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Cool Re: How many wires did you say were allowed?

Quote:
Originally Posted by bking
It takes a lot of talent to get all those wires and connections in that box!
Too bad they didn't have more talent.....

was the cover bulging out?
Nay, they probably will add more wires, or add some extension rings. If they do, then the problem gets worse because of the 3 inch rule that calls for all wires to capable of extending from the edge of the last ring or rings with no splices.

2005 NEC Reference:

"300.14 Length of Free Conductors at Outlets, Junctions, and Switch Points
At least 150 mm (6 in.) of free conductor, measured from the point in the box where it emerges from its raceway or cable sheath, shall be left at each outlet, junction, and switch point for splices or the connection of luminaires (fixtures) or devices. Where the opening to an outlet, junction, or switch point is less than 200 mm (8 in.) in any dimension, each conductor shall be
long enough to extend at least 75 mm (3 in.) outside the opening.

Exception: Conductors that are not spliced or terminated at the outlet, junction, or switch point shall not be required to comply with 300.14."

Reply With Quote
  #4  
Old 6/7/06, 4:37 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: How many wires did you say were allowed?

Heck, there's three unused knock-outs...that means three more wires can fit in there...



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #5  
Old 6/7/06, 4:40 PM
Jae Williams Jae Williams is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Sharonville, OH
Posts: 5,482
Default Re: How many wires did you say were allowed?

...and if the knock-outs are 3/4 inch, let's run a couple of 8/3 NM into it as well...



"not just an inspection, but an education"

www.homesweethomecincinnati.com

Democracy is two wolves and a lamb.
Liberty is a well-armed lamb. B. Franklin
Reply With Quote
  #6  
Old 6/7/06, 4:58 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many wires did you say were allowed?

Call the Posse out! I think this is a job for the NACHI Electrical Posse!

Where's that Sheriff when you need him?

http://www.nachi.org/forum/users/pabernathy/
Reply With Quote
  #7  
Old 6/7/06, 5:08 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: How many wires did you say were allowed?

lol....Joe YOU just HATE when I use my little tag lines....lol......You dont need the POSSE on this one....heck an Apprentice could get this one right...



Paul W. Abernathy
Reply With Quote
  #8  
Old 6/7/06, 5:48 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: How many wires did you say were allowed?

Oh my -- I took the cover off and found a box full of cat #3 phone wire and they had used old runs because it was easy. I am in real trouble now because I flagged it as a problem and it was not

Oh well live and learn - Next time I pull the cover plate - Crap I will probably get in trouble because that is probably invasive like taking the screws out of an attic hatch or the screws off of the panel on an electrical box. -- Just can't win

Is it invasive because we walked into the home??

rlb
Reply With Quote
  #9  
Old 6/7/06, 7:15 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: How many wires did you say were allowed?

"...plus one additional for the three equipment grounding conductors..."

If you run EMT and/or rigid there is no need for grounding conductors. The conduit is the ground conductor.

Guess we can get more wires in the box in the Chicago area .

BTW: What is the NEC's rule on number of hots / neutrals in a given conduit (by size of conduit, I would presume).



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #10  
Old 6/7/06, 10:17 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many wires did you say were allowed?

Joe, they could add a box extension to ease things up, or maybe two.
Reply With Quote
  #11  
Old 6/7/06, 10:27 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many wires did you say were allowed?

Quote:
Originally Posted by brian winkle
Joe, they could add a box extension to ease things up, or maybe two.
See this: http://www.nachi.org/forum/showpost....30&postcount=3

I included this scenario.
Reply With Quote
  #12  
Old 6/7/06, 10:34 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many wires did you say were allowed?

Quote:
Originally Posted by wdecker
"...plus one additional for the three equipment grounding conductors..."

If you run EMT and/or rigid there is no need for grounding conductors. The conduit is the ground conductor.

Guess we can get more wires in the box in the Chicago area .

BTW: What is the NEC's rule on number of hots / neutrals in a given conduit (by size of conduit, I would presume).
True, but the EGC's were not in the EMT.

Last edited by jtedesco1; 6/15/06 at 12:35 AM..
Reply With Quote
  #13  
Old 6/7/06, 10:38 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: How many wires did you say were allowed?

Hey Sheriff Paul, come on play along, I was referring to this installation.

http://www.nachi.org/forum/showpost....35&postcount=5
Reply With Quote
  #14  
Old 6/7/06, 10:58 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: How many wires did you say were allowed?

lol.....you lost me Fella......I am not part of the Sheriff's Posse....I am a FOUNDING follower of the "INSANE" clown POSSE' on my brothers side....



Paul W. Abernathy
Reply With Quote
  #15  
Old 6/7/06, 11:13 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: How many wires did you say were allowed?

Are you looking for what I would advise the person to do.....honestly...I would tell them to take that freakin blank off.....add a 4" x 2 1/8" square extention ring and HOPE the wires meet the requirement...or they can wirenut and pigtail to get the length...they wont count in the calculation anyway... and replace the cover and be happy........about all I would tell them.



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wires ran from lugs to auxilary panels Kevin Luce Electrical Inspections 7 9/20/07 9:24 AM
grounding wires tvanvranken Electrical Inspections 14 3/16/07 7:24 AM
Wires and Junction at tub mlong Electrical Inspections 8 11/18/06 12:29 PM
Ground Wires Inside a Panel mveitenhans Electrical Inspections 13 10/29/06 11:39 AM
Painted service wires hcavin Electrical Inspections 1 9/27/06 12:47 PM


All times are GMT -4. The time now is 7:42 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts