Data plate on A/C unit call for a max fuse of 25 Amps. Main Panel has (2) 20 Amp breakers together. Is this OK? (3rd and 4th breakers on right side in off position)
|
|
#2
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yes, 20 is less than 25, so you're okay if it permits breakers.
Last edited by Marc D. Shunk; 3/31/07 at 4:10 PM.. |
|
#3
|
||||
|
||||
|
Check mfg. site for AC model number.
Many have both a max. fuse size and max. Circuit Breaker rating. |
|
#4
|
||||
|
||||
|
We're good. Thanks!
|
|
#5
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The only down side of that might be a nuisance trip. Maybe a PITA but not a safety issue
|
|
#6
|
|||
|
|||
|
Is this new construction......if so have them re-identify the white conductor going to the breaker.
And just remember..( and I think Marc touched on it )...if by chance you are ever dealing with an older AC unit outside and it says Maximum Fuse Size and says nothing about breakers...it MUST have a fused OCPD somewhere in the setup. Paul W. Abernathy |
|
#7
|
||||
|
||||
|
Quote:
Richard W. Washington, owner RW Home Inspections, Inc. www.RWHOMEINSPECTIONS.com Texas Real Estate Commission (TREC) Professional Inspector License #7238 Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter InterNACHI member since 2004 Based in Katy, serving Houston and all surrounding communities |
|
#8
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#9
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
The only reason they would say "fuse" is if the number they came up with was a non-standard breaker size. You can get fuses just about any size. Most inspectors would take the next smaller breaker. (a few overly generous ones might even let you round up)
|
|
#10
|
||||
|
||||
|
Ooops, My bad. I meant Max BREAKER in my original post. I'm feeling "old school"
|
|
#11
|
|||
|
|||
|
lol...well robert if you mean 25A Max Breaker.....just make sure it is not protected by a breaker larger than 25A.....
Just remember most nameplates will say Minimum Circuit Ampacity and Maximum ( in your case breaker ) OCPD size......this is where you see many times smaller sized conductors on larger breakers...make it simply for yourself...just verify the items on the nameplate and let er ride.... Paul W. Abernathy |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Fuse box puzzle (with photos) | abolt | Electrical Inspections | 2 | 8/5/07 3:28 PM |
| Fuse box puzzle | abolt | Electrical Inspections | 0 | 8/5/07 2:34 PM |
| Fuse Panel Questions | pdoane | Electrical Inspections | 8 | 9/21/06 8:37 AM |
| FPE Fuse Panel | rarmstrong1 | Electrical Inspections | 2 | 6/3/06 5:22 PM |
| Max fuse ratings | dmacy | Inspecting HVAC Systems | 15 | 1/19/06 11:35 PM |