Default Max Fuse

Data plate on A/C unit call for a max fuse of 25 Amps. Main Panel has (2) 20 Amp breakers together. Is this OK? (3rd and 4th breakers on right side in off position)
Attached Thumbnails
max-fuse-ac-panel.jpg  
Reply With Quote
  #2  
Old 3/31/07, 4:06 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Max Fuse

Yes, 20 is less than 25, so you're okay if it permits breakers.

Last edited by Marc D. Shunk; 3/31/07 at 4:10 PM..
Reply With Quote
  #3  
Old 3/31/07, 4:08 PM
Michael Larson's Avatar
Michael Larson Michael Larson is offline
InterNACHI Member
 
Join Date: May 2006
Location: Hudson, WI including the Twin Cities of MN
Posts: 32,049
Default Re: Max Fuse

Check mfg. site for AC model number.
Many have both a max. fuse size and max. Circuit Breaker rating.
Reply With Quote
  #4  
Old 3/31/07, 4:48 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,514
Default Re: Max Fuse

We're good. Thanks!
Reply With Quote
  #5  
Old 4/1/07, 2:32 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Max Fuse

The only down side of that might be a nuisance trip. Maybe a PITA but not a safety issue
Reply With Quote
  #6  
Old 4/1/07, 11:56 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Max Fuse

Is this new construction......if so have them re-identify the white conductor going to the breaker.

And just remember..( and I think Marc touched on it )...if by chance you are ever dealing with an older AC unit outside and it says Maximum Fuse Size and says nothing about breakers...it MUST have a fused OCPD somewhere in the setup.



Paul W. Abernathy
Reply With Quote
  #7  
Old 4/1/07, 4:51 PM
Richard W. Washington's Avatar
Richard W. Washington Richard W. Washington is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Katy, TX
Posts: 1,184
Default Re: Max Fuse

Quote:
Originally Posted by pabernathy
Is this new construction......if so have them re-identify the white conductor going to the breaker.

And just remember..( and I think Marc touched on it )...if by chance you are ever dealing with an older AC unit outside and it says Maximum Fuse Size and says nothing about breakers...it MUST have a fused OCPD somewhere in the setup.
fused OCPD?



Richard W. Washington, owner
RW Home Inspections, Inc.
www.RWHOMEINSPECTIONS.com
Texas Real Estate Commission (TREC)
Professional Inspector License #7238
Texas Professional Real Estate Inspectors Member (TPREIA)-Greater Houston Chapter
InterNACHI member since 2004
Based in Katy, serving Houston and all surrounding communities
Reply With Quote
  #8  
Old 4/1/07, 6:16 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Banned
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,980
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Max Fuse

Quote:
Originally Posted by rwashington
fused OCPD?
Fused overcurrent protective device. In a home with breakers, this would normally be accomplished by providing a weatherproof fused disconnect at the unit where a normal weatherproof unfused safety switch would normally be found.
Reply With Quote
  #9  
Old 4/1/07, 6:56 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Max Fuse

The only reason they would say "fuse" is if the number they came up with was a non-standard breaker size. You can get fuses just about any size. Most inspectors would take the next smaller breaker. (a few overly generous ones might even let you round up)
Reply With Quote
  #10  
Old 4/3/07, 9:23 PM
ROBERT W. NEWLAND, JR.'s Avatar
ROBERT W. NEWLAND, JR. ROBERT W. NEWLAND, JR. is offline
InterNACHI Member
 
Join Date: Oct 2005
Location: TYRONE, GA
Posts: 2,514
Default Re: Max Fuse

Ooops, My bad. I meant Max BREAKER in my original post. I'm feeling "old school"
Reply With Quote
  #11  
Old 4/4/07, 8:44 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Max Fuse

lol...well robert if you mean 25A Max Breaker.....just make sure it is not protected by a breaker larger than 25A.....

Just remember most nameplates will say Minimum Circuit Ampacity and Maximum ( in your case breaker ) OCPD size......this is where you see many times smaller sized conductors on larger breakers...make it simply for yourself...just verify the items on the nameplate and let er ride....



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Fuse box puzzle (with photos) abolt Electrical Inspections 2 8/5/07 3:28 PM
Fuse box puzzle abolt Electrical Inspections 0 8/5/07 2:34 PM
Fuse Panel Questions pdoane Electrical Inspections 8 9/21/06 8:37 AM
FPE Fuse Panel rarmstrong1 Electrical Inspections 2 6/3/06 5:22 PM
Max fuse ratings dmacy Inspecting HVAC Systems 15 1/19/06 11:35 PM


All times are GMT -4. The time now is 4:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts