Default Max overcurrent protection for AC units

Did an inspection where home had 2 AC units. Data plates on units indicate max. overcurrent protection of 20 and 30 amps. Breaker in panel labeled for AC's was one 50 amp? Does'nt each unit need its own dedicated circuit?
Reply With Quote
Find an InterNACHI certified Oklahoma Home Inspector (and anywhere else in North America)
  #2  
Old 5/25/09, 10:50 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,403
Default Re: Max overcurrent protection for AC units

Did you look inside the subpanel next to the units? This is where you will typically find the individual breakers.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207

"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #3  
Old 5/25/09, 10:58 AM
Joe Funderburk, CMI's Avatar
Joe Funderburk, CMI Joe Funderburk, CMI is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Hickory Grove, SC
Posts: 4,410
Send a message via Yahoo to jfunderburk
Default Re: Max overcurrent protection for AC units

Bruce is correct. However, once you identify the breakers for the AC condensers, you should carefully match them to the data plates. About 40% of every condenser I see has an inappropriately sized breaker. Seems most HVAC guys only carry the 30 amps on the truck. No matter what the condenser requires, it gets a 30 amp.



Joe Funderburk, CMI
Alpha & Omega Home Inspections, LLC
Inspecting Upstate SC & Charlotte Metro, NC
NACHI ID: NACHI05120170
www.aohomeinspection.com


Reply With Quote
  #4  
Old 5/25/09, 11:20 AM
nrichards nrichards is offline
InterNACHI Member
 
Join Date: Feb 2009
Posts: 16
Default Re: Max overcurrent protection for AC units

It was my understanding that the breakers at the units are disconnects only and do not act as overcurrent devices? Does not matter size of disconnect I thought...
Reply With Quote
  #5  
Old 5/25/09, 11:25 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,403
Default Re: Max overcurrent protection for AC units

You have to confirm what they are, when a subpanel is used like you descibed they should be breakers with the amps indicated on them. If the subpanel has disconnects only it is wrong, If the panel breakers are the right size the exterior can have a straight disconnect or any size breaker (but larger than the panel one).

In summary, you can have the properly sized breaker inside the main panel or at the disconnect location.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207

"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #6  
Old 5/25/09, 11:40 AM
nrichards nrichards is offline
InterNACHI Member
 
Join Date: Feb 2009
Posts: 16
Default Re: Max overcurrent protection for AC units

Thanks for your replies, let me clarify my original question. Each unit has a single breaker disconnect next to the compressor. The main panel is located in the garage with one 50 amp breaker that appears to be for both units.
Reply With Quote
  #7  
Old 5/25/09, 11:50 AM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 2,403
Default Re: Max overcurrent protection for AC units

If the disconnects do not have any amps marked on them then its wrong.

So there is no subpanel? Just two disconnect boxes? That means there is a splice or double tap somewhere.

I have never seen a subpanel with disconnects inside with no overcurrent protection but its possible.

Proper terms would be:
double pole disconnect (not a breaker)
double pole breaker (also functions as a disconnect)



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
704 301-3207

"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What do you think? Can this work for you? jtedesco1 Electrical 13 2/9/09 10:58 PM
Where is it written.... bgromicko General Inspection Discussion 18 1/19/08 9:02 PM
Article 240 : Overcurrent Protection Article pabernathy Electrical 0 5/23/07 11:40 AM
AFCI Questions and Answers - Mike Holt pabernathy Electrical 0 7/7/06 12:24 PM
When were panels not allowed in clothes closets? jtedesco1 Electrical 43 3/2/06 1:37 AM


All times are GMT -4. The time now is 12:03 AM.


Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts