Default Melted Neutral SE. What's the cause?

Saw a panel, the other day.

Everything looked fine. One exception.

The Neutral SE, where connected to the Service Equipment, displayed some green corrosion (copper conductor) but there was evidence of old melting of the insulation.



Any Ideas? I know there is a reason for just the neutral to display this.

There was no clear ground on this SE panel.

Thanks;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!

Last edited by wdecker; 4/7/06 at 8:17 PM..
Reply With Quote
  #2  
Old 3/23/06, 10:49 PM
Jay Moge's Avatar
Jay Moge Jay Moge is offline
Active Poster
 
Join Date: Aug 2005
Location: Derry New Hampshire
Posts: 761
Please Note: Jay Moge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Melted Neutral SE. What's the cause?

currosion = resistance. resistance = heat?
Reply With Quote
  #3  
Old 3/23/06, 10:50 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Melted Neutral SE. What's the cause?

Loose connection.
Reply With Quote
  #4  
Old 3/23/06, 10:54 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: Melted Neutral SE. What's the cause?

Additional point

1) There rest of the panel was neat and clean and no problems.

2) The panel face screws were ALL pointed wood screws and 2 (or 4) were rusted at the ends.


I just know that I had seen an explaination on this board somewhere!

Reletated to grounding, somehow.



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #5  
Old 3/23/06, 10:59 PM
bkelly1's Avatar
bkelly1 bkelly1 is offline
Active Poster
 
Join Date: Jan 2004
Location: Rives, TN
Posts: 1,738
Please Note: bkelly1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Melted Neutral SE. What's the cause?

It appears from the melting on the insulation it once got hot from a loose connection. Or could be loose now. Have seen it several times. Could be other though..........
Reply With Quote
  #6  
Old 3/24/06, 3:02 AM
rmoore's Avatar
rmoore rmoore is offline
Active Poster
 
Join Date: Feb 2004
Location: Seattle, WA
Posts: 113
Please Note: rmoore is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Melted Neutral SE. What's the cause?

If the "melting" is just around the lug, then I too would suspect a poor connection from corrosion and the subsequent arcing. If more of the conductor (at the drip loop etc) was in similar condition, then I'd guess a lightening strike on the utility's grounded conductor or some other type of short or surge.

Whatever the cause, I'd say it's now in a condition that warrants repair.
Reply With Quote
  #7  
Old 3/24/06, 11:47 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Melted Neutral SE. What's the cause?

Lets not also forget guys that the neutral could also be undersized.....without knowing the AMPS, the Grounded Conductros Size....and all the factors...yers it can be loose connection....or it could be undersized....with the advent of so many linear and non-linear issues and harmonics and so on in new homes........could just be a poor electrical design.

A good mind will not block out all the options to consider.....



Paul W. Abernathy
Reply With Quote
  #8  
Old 3/24/06, 2:37 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Melted Neutral SE. What's the cause?

Loose connection to cause that...

A missing GEC will not cause that.
I have found 20 and 30 year old homes with no GEC at all with no problems.



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #9  
Old 3/24/06, 3:22 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Melted Neutral SE. What's the cause?

Dude.....Said NOTHING about a loose GEC.......Loose Neutral Connection.....Please read the post...!



Paul W. Abernathy
Reply With Quote
  #10  
Old 3/24/06, 3:52 PM
Patrick Bolliger's Avatar
Patrick Bolliger Patrick Bolliger is offline
InterNACHI Member
 
Join Date: Aug 2005
Location: Chicago, IL
Posts: 890
Send a message via Skype™ to pbolliger
Talking Re: Melted Neutral SE. What's the cause?

What kinda bothers me about the picture is the fact that the other wires don't show any signs of heat damage.. You know the conductors in very close proximity at the connection point. hmmm Any comments..

On a different note:

Last night attended a open house at ITA.. Had a little spiel about GFCI / AFCI.. Had some input to give regarding bogus UL listed testers and the fact that a new release was made that all AFCI testers are NOT verifiable methods of properly testing a AFCI device.. per UL Hmmm Sure-test and all... WOW

Also heard but can not confirm ...hear that GFCI / AFCI could be a whole house issue (pushing to start in 2008... that will be the day $$$$$$

Feed back from the board sparkies...
Reply With Quote
  #11  
Old 3/24/06, 4:21 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Melted Neutral SE. What's the cause?

I believe all testing of GFCI's and AFCI's should take place at the Receptacle and Breaker itself as the only real approved method by the manufacturer. While a SureTest will trip most all GFCI situations.....it relies on 2nd party perspective.....the manufactures prefer it to be internal tested from the reset buttons.

As for the whole house deal........Thats going to be a tough one...might require it on all 15A and 20A branch circuits....but not the whole panel because it would have to be intergrated.....otherwise explain when a 20A AFCI trips the entire panel.....I can hear the whining now.......and its only 2006....

The day a whole panel becomes AFCI and GFCI protected will be the day the systems get SMART and all 42 breakers are intergrated, switchable between 120V and 240V and totally customizable.......otherwise a main breaker will never be AFCI and GFCI protected in my opinion....something that needs to be controlled on a Branch Circuit level....

Now I am off to FIX a smoking Electrical Panel........Love those after hours calls....



Paul W. Abernathy
Reply With Quote
  #12  
Old 3/24/06, 9:38 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Melted Neutral SE. What's the cause?

I am not sure the world will be ready for an integrated panel anytime soon. There is too much invested in the molded case circuit breaker business
Reply With Quote
  #13  
Old 3/24/06, 9:50 PM
A Dan Leleika A Dan Leleika is offline
InterNACHI Member
 
Join Date: Jun 2005
Location: Aurora, IL
Posts: 402
Default Re: Melted Neutral SE. What's the cause?

Quote:
Originally Posted by pabernathy
Now I am off to FIX a smoking Electrical Panel........Love those after hours calls....
Pictures, pictures....we want to see pics tomorrow Paul.
Reply With Quote
  #14  
Old 3/24/06, 11:50 PM
Bruce A. King's Avatar
Bruce A. King Bruce A. King is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: York, SC
Posts: 3,206
Default Re: Melted Neutral SE. What's the cause?

Quote:
Originally Posted by pabernathy
Dude.....Said NOTHING about a loose GEC.......Loose Neutral Connection.....Please read the post...!

Paul, your not the only poster here, it was mentioned earlier ok



B.A. King Home Inspections, LLC
www.BAKingHomeInspections.com
Serving Charlotte NC area and Rock Hill SC areas.
CMI Certified Master Inspector and Independent
License NC2449 and SC1597
704 301-3207



"Discovery consists in seeing what everyone else has seen and thinking what no one else has thought."
- Albert Szent-Gyvrgyi, Nobel Prize for Medicine 1937
Reply With Quote
  #15  
Old 3/25/06, 3:10 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Melted Neutral SE. What's the cause?

lol........Hmmmmm I did not see anything about a GEC being loose causing it....Hell I know I am not the only poster here bruce...how boring would that be...thehehehe



Paul W. Abernathy
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
"UFER" Ground? see last paragraph. jtedesco1 Electrical Inspections 19 8/23/11 3:56 PM
Metal Rigid or PVC Rigid what is code bpotts Electrical Inspections 5 12/4/06 2:40 PM
Ground wire in neutral bar, neutral to breaker, hot to ground? rmc3inspection Electrical Inspections 4 8/1/06 9:44 AM
Proposed Definition of Neutral Conductor and Point jtedesco1 Electrical Inspections 1 4/22/06 10:19 AM


All times are GMT -4. The time now is 4:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts