Default Messy work, but is it wrong?

This was in a garage yesterday. The wiring is not being covered with dry wall, it just stays like this. This type of workmanship just kills me. It was all over.
Keeping in mind that in Az. romex can be bare above 7 feet, is there anything wrong with this? I would like to call it out but what do I say other than it looks like crap ?
Attached Thumbnails
messy-work-but-wrong-100_8052-medium-small-.jpg (Small).JPG
Views:	163
Size:	39.7 KB
ID:	5490  




"Be Proud of Your Home, Go With Pride!"
'Not just a Home Inspection, but an Education'

Pride Property Inspections provides professional Home Inspections throughout Tucson and Southern Arizona including Pima, Cochise, Pinal, Santa Cruz, Graham counties.

Reply With Quote
  #2  
Old 9/9/06, 11:47 AM
lagudo lagudo is offline
Active Poster
 
Join Date: Nov 2005
Location: Roswell, GA
Posts: 156
Please Note: lagudo is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Messy work, but is it wrong?

Work appears to be done by homeowner or handyman and looks unprofessional. If this is what you can see, who knows whats hidden. I'm interested in what others have to say.
Reply With Quote
  #3  
Old 9/9/06, 11:53 AM
Roy D. Cooke, Sr's Avatar
Roy D. Cooke, Sr Roy D. Cooke, Sr is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Brighton, ON
Posts: 14,612
Default Re: Messy work, but is it wrong?

Quote:
Originally Posted by mtimpani
This was in a garage yesterday. The wiring is not being covered with dry wall, it just stays like this. This type of workmanship just kills me. It was all over.
Keeping in mind that in Az. romex can be bare above 7 feet, is there anything wrong with this? I would like to call it out but what do I say other than it looks like crap ?
The wiring for the Garage door is less then professionally done .
Wires under the joist make it impossible to finish the ceiling .
Garage doors should be on their own circuit and not have other cords plugged in to them.
Recommend immediate repair by qualified person.
Roy Cooke .... Royshomeinstection.com
Reply With Quote
  #4  
Old 9/9/06, 12:29 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Messy work, but is it wrong?

If it's "messy," it's "wrong" (IMHO). It certainly warrants repair or correction.



IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #5  
Old 9/9/06, 12:33 PM
dspencer's Avatar
dspencer dspencer is offline
Active Poster
 
Join Date: Dec 2004
Location: Marengo, Oh
Posts: 178
Please Note: dspencer is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Messy work, but is it wrong?

Any code to support the need for correction? What would the local Licensed contractor say about the placment of the wiring? Maybe a comment of dangling cords would be a safty issue....

Also you usally can tell how good a homeowner is when you see how they tied it in the main panel.
Reply With Quote
  #6  
Old 9/9/06, 1:06 PM
Jeffrey R. Pope's Avatar
Jeffrey R. Pope Jeffrey R. Pope is offline
InterNACHI Member
 
Join Date: Aug 2003
Location: Santa Clarita, CA
Posts: 8,047
Default Re: Messy work, but is it wrong?

NEC 110.12 Mechanical Execution of Work.
Electrical equipment shall be installed in a neat and workmanlike manner.




IF YOUR INSPECTOR IS NOT USING THERMAL IMAGING, YOU'RE NOT GETTING THE WHOLE PICTURE ®
Jeff Pope
JPI Home Inspection Service
Santa Clarita CA
(661) 212-0738
Santa Clarita Home Inspection
http://www.MyInspector.net


Reply With Quote
  #7  
Old 9/9/06, 7:29 PM
Pierre Belarge Pierre Belarge is offline
Active Poster
 
Join Date: Apr 2006
Posts: 202
Please Note: Pierre Belarge is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Messy work, but is it wrong?

314.17(C) exception
(C) Nonmetallic Boxes and Conduit Bodies.
Nonmetallic
boxes and conduit bodies shall be suitable for the lowest
temperature-rated conductor entering the box. Where nonmetallic
boxes and conduit bodies are used with open wiring
or concealed knob-and-tube wiring, the conductors
shall enter the box through individual holes. Where
flexible
tubing is used to enclose the conductors, the tubing shall
extend from the last insulating support to not less than
6 mm (
14 in.) inside the box and beyond any cable clamp.
Where nonmetallic-sheathed cable or multiconductor Type
UF cable is used, the sheath shall extend not less than
6 mm (
14 in.) inside the box and beyond any cable clamp.
In all instances, all permitted wiring methods shall be secured
to the boxes.

Exception: Where nonmetallic-sheathed cable or multiconductor
Type UF cable is used with single gang boxes not
larger than a nominal size 57 mm
× 100 mm (214 in.

×
4 in.) mounted in walls or ceilings, and where the cable
is fastened within 200 mm (8 in.) of the box measured along
the sheath and where the sheath extends through a cable
knockout not less than 6 mm (
14 in.), securing the cable to
the box shall not be required. Multiple cable entries shall
be permitted in a single cable knockout opening.



300.4(D)

(D) Cables and Raceways Parallel to Framing
Members.
In both exposed and concealed locations, where
a cable- or raceway-type wiring method is installed parallel
to framing members, such as joists, rafters, or studs, the
cable or raceway shall be installed and supported so that the
nearest outside surface of the cable or raceway is not less
than 32 mm (1
14 in.) from the nearest edge of the framing
member where nails or screws are likely to penetrate.

Reply With Quote
  #8  
Old 9/9/06, 9:52 PM
Peter Doane's Avatar
Peter Doane Peter Doane is offline
InterNACHI Member
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,055
Default Re: Messy work, but is it wrong?

Cables in basements and garage walls are often found exposed to damage. Cables should not be exposed on the surface of unfinished wall/ ceiling studs, and should have been borred and run in-through the joist at least 1 1/4" inches from the bottom end of the joist or at least 7' above the floor surface. Cables should also be secured within 12" of boxes, fixtures, or panels. To simplify this, I would call it out as:
"sub-standard electrical work noted in the garage. There are a few exposed electrical wires that are subject to damage. It is noted for buyer information that a qualified electrician should review further for repair options for occupant safety."



Peter Doane
Realty Check Inspection Service
NACHI ID# 05120681
Reply With Quote
  #9  
Old 9/9/06, 9:56 PM
Joseph Hagarty,  CMI's Avatar
Joseph Hagarty, CMI Joseph Hagarty,  CMI is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Parkesburg, PA
Posts: 5,636
Default Re: Messy work, but is it wrong?

Quote:
Originally Posted by jpope
NEC 110.12 Mechanical Execution of Work.
Electrical equipment shall be installed in a neat and workmanlike manner.

One of my favorite notations as well....



Joseph P. Hagarty
joseph.hagarty@comcast.net
Main Line Inspections, Inc.
Phone: 610-399-3675
Email: MainLineHI@comcast.net

http://pa.nachi.org/mainlinepa/about.html
http://www.householdinspector.com

National President / NACHI (2003-2004)
NACHI Education Committee Member
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Basement Work Done In Past Nick Scibetta Structural Inspections 18 10/31/06 4:21 PM


All times are GMT -4. The time now is 4:56 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts