Default This metal garage door was alive!

This metal garage door was alive!

http://www.youtube.com/v/yiZFjRA_Gs4&rel=1

Are they checked by the inspector during a home inspection?

PS: What do I have to do to get the actual picture of the start up video posted?
Reply With Quote
  #2  
Old 11/20/07, 8:05 AM
msylvester's Avatar
msylvester msylvester is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Batavia, IL
Posts: 672
Send a message via AIM to msylvester
Default Re: This metal garage door was alive!

How sad...



Mark Sylvester
P.I. Home Inspection Services
www.pihomeinspection.com
mark@pihomeinspection.com
Reply With Quote
  #3  
Old 11/20/07, 8:45 AM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: This metal garage door was alive!

Joe,
I cant see the video because i am in a airport heading to a seminar ( Motorola Q)..but i will say home inspectors are probably not check garage doors for voltage because testing would generally require them to use a voltage meter....and it is usually not in there arsenal.....some may but the majority wont.....sad thing is the resistance to learning about suretests is only matched by the resistance to use of a good volt meter. ;(



Paul W. Abernathy
Reply With Quote
  #4  
Old 11/20/07, 8:57 AM
msylvester's Avatar
msylvester msylvester is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Batavia, IL
Posts: 672
Send a message via AIM to msylvester
Default Re: This metal garage door was alive!

I check aluminum siding but have never checked the garage door.

I will now!



Mark Sylvester
P.I. Home Inspection Services
www.pihomeinspection.com
mark@pihomeinspection.com
Reply With Quote
  #5  
Old 11/20/07, 9:41 AM
mthomas2 mthomas2 is offline
Active Poster
 
Join Date: Oct 2005
Location: Evanston, IL
Posts: 703
Please Note: mthomas2 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This metal garage door was alive!

Would a non-contact (Tic-Tracker) detector likely have found this?
Reply With Quote
  #6  
Old 11/20/07, 9:48 AM
msylvester's Avatar
msylvester msylvester is offline
InterNACHI Member
 
Join Date: Feb 2005
Location: Batavia, IL
Posts: 672
Send a message via AIM to msylvester
Default Re: This metal garage door was alive!

It should.



Mark Sylvester
P.I. Home Inspection Services
www.pihomeinspection.com
mark@pihomeinspection.com
Reply With Quote
  #7  
Old 11/20/07, 9:49 AM
Michael W. Gault's Avatar
Michael W. Gault Michael W. Gault is offline
InterNACHI Member
 
Join Date: Apr 2005
Location: Mount Pleasant, SC
Posts: 1,091
Default Re: This metal garage door was alive!

Quote:
Originally Posted by mthomas2
Would a non-contact (Tic-Tracker) detector likely have found this?
It should...

Tragic story all around.



- Mike

Michael W. Gault, SC RBI 1728
A to Z Home Inspections
Charleston, Dorchester & Berkeley Counties in S.C.
NACHI05040682
www.atozinspector.com

(843) 442-9755
Charleston Home Inspector
Reply With Quote
  #8  
Old 11/20/07, 11:30 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This metal garage door was alive!

There had to be several violations for this to happen. The ungrounded switch loop was only one of them. How was the garage door opener wired? (where did that power come from) Why didn't that EGC clear the fault?

I agree the bottom line is they should have had permits and inspections but I am not convinced a lot of muni inspectors actually inspect anything. The EC is ultimately responsible and I imagine he will simply be bankrupted in a wrongful death suit. The wireman who actually killed this kid will probably get away scot free.
Reply With Quote
  #9  
Old 11/20/07, 12:40 PM
William J. Decker's Avatar
William J. Decker William J. Decker is offline
InterNACHI Member
 
Join Date: Nov 2004
Location: Skokie, IL
Posts: 7,785
Default Re: This metal garage door was alive!

Quote:
Originally Posted by jtedesco1
This metal garage door was alive!

http://www.youtube.com/v/yiZFjRA_Gs4&rel=1

Are they checked by the inspector during a home inspection?

PS: What do I have to do to get the actual picture of the start up video posted?
Please note these facts in the video:

1) The electrician believed he, and the others in that area, new better than the law. A permit was "technically" required (as in, "Legally required") but not obtained. Yeah, the law says we have to, but we have decided that we don't and we are electricians and we know better than the law".)

2) Because of the above, the code guys didn't find the problem. This is clearly a case where the contractor messes up, but everyone wants to blame the codies.

3) Note that the electrician chose to not use the correct and required wire. Question? If the installation have been in EMT instead of romex, whould the outcome have been different (because, properly installed, the EMT is always grounded?)

4) This is why most of the good electricians that I know install GFCI receptacles for garage door openers. If the current came from a ground fault in the garage door opener, a GFCI would have stopped it.

5) In short, the negligence of the "professionals" killed this kid. Sure, it's beyind the SOP, but I always check every exterior metal piece with a ticker.

Hope this helps;



Will Decker, CMI
ILL License # 450.0002240
Board Certified Master Inspector
Decker Home Services, LLC
Chicago and Northern Suburban Home Inspections
Office: (847) 676-8393
Cell: (847) 609-2345
Home: (847) 673-2702

wjd@DeckerHomeServices.com
www.DeckerHomeServices.com

Learn, Educate, Serve and have fun doing it!
Reply With Quote
  #10  
Old 11/20/07, 3:39 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This metal garage door was alive!

William,


1) This is NOT always the fault of the electrician. Most times when a GC does not open a building permit the electrician does not get electrical permits so as not to expose the GC's unpermitted job.
No, I do not "know better than the law". This is just simple facts of real life in our world.

2) Not blamin the "codies", but WHY if a building permit WAS issued, were electrical inspections not required??? In most places a building permit will not be closed without proper inspections all around.

3) EMT? For a residential garage wire??? Maybe in Chicago, not in the real world.
"properly installed, the EMT is always grounded"...Oh yeah. You've not seen some of the installs I have. What if the feed end is not made up or the fitting is loose or does not exist? What then? You know what...NO ground.
What if the conduit rusts away? No ground.
What if the conduit gets hit and the fitting breaks? No ground.
EMT without a separate grounding conductor pulled is far worse IMO than any cable wiring method.

4) Most "good electricans"? I am a very good electrican and I have never installed a GFI for an opener. I never even considered it. I see no reason for it. Rather I make sure my installations are up to code and safe. A properly grounded garage door/opener would have prevented this and any other tradgedies.

5) Here I do NOT disagree. The one guy who wired a 3-way switch using "2-wire" instead of "3-wire", in turn using a bare ground to carry current, killed this kid. NO ONE else.
Reply With Quote
  #11  
Old 11/20/07, 3:46 PM
Ian Gills Ian Gills is offline
Active Poster
 
Join Date: Jan 2007
Posts: 199
Please Note: Ian Gills is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This metal garage door was alive!

A tragic illustration of Abernathy's powerpoint that shows ground will not trip the breaker. I think it's time to switch to three wire on the range.

I'll do that.

Last edited by Ian Gills; 11/20/07 at 3:50 PM..
Reply With Quote
  #12  
Old 11/20/07, 3:51 PM
cbuell's Avatar
cbuell cbuell is offline
Active Poster
 
Join Date: Feb 2004
Location: Shorline, WA
Posts: 380
Please Note: cbuell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This metal garage door was alive!

3) EMT? For a residential garage wire??? Maybe in Chicago, not in the real world.
"properly installed, the EMT is always grounded"...Oh yeah. You've not seen some of the installs I have. What if the feed end is not made up or the fitting is loose or does not exist? What then? You know what...NO ground.
What if the conduit rusts away? No ground.
What if the conduit gets hit and the fitting breaks? No ground.
EMT without a separate grounding conductor pulled is far worse IMO than any cable wiring method.

This picture re-inforces the problems that can arise when the conduit is used to provide a ground path to a remote distribution panel.
Attached Thumbnails
metal-garage-door-alive-dulitz-116.jpg  
Reply With Quote
  #13  
Old 11/20/07, 4:10 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: This metal garage door was alive!

... and when the rust sets in this is the result!

Reply With Quote
  #14  
Old 11/20/07, 4:57 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: This metal garage door was alive!

All the examples above point out vividly the importance of installing a grounding conductor for all circuits. The additional cost is negligable when compared to the potential consequences.

Maybe I missed it, but in all the information presented, did anyone say exactly why and how the door itself became energized?



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #15  
Old 11/20/07, 5:29 PM
Richard L. Bennett Richard L. Bennett is offline
InterNACHI Member
 
Join Date: Mar 2005
Location: Frostproof, Fl
Posts: 2,304
Default Re: This metal garage door was alive!

Poor reporting of a cause of death

I do not understand how the wrong wire caused the door to be hot

The building code in my area would have never picked up on the 14-2 14-3 problem

Some one draw me a pix of how a mis wired 3 way light made the door hot

This is a case where money will not solve the problem

rlb
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Evaporative cooler in garage chellickson Inspecting HVAC Systems 9 7/23/07 12:08 AM
Light Bulbs- All Ya Wanna Know pabernathy Electrical Inspections 9 4/18/07 7:22 PM
Garage ceiling & door header Al Barb Interior Inspections 7 3/27/07 12:07 PM
Garage Door Safety...No Reverse...Advice Please gliebig Exterior Inspections 33 3/17/07 7:28 PM


All times are GMT -4. The time now is 7:42 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts