InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > Electrical

Electrical Contains discussions about electrical systems. This includes outlets, panels, wiring, et cetera.

Reply
 
LinkBack Thread Tools Display Modes
  #1  
Old 10/14/08, 7:02 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 454
Bruce Thompson is often very helpful Bruce Thompson is often very helpful Bruce Thompson is often very helpful
Default Meter base being used as workbox

Surely this is a no-no (making a junction in or passing through the meter base). That is an AC disconnect box on the left. I assume the rule would come from the electric company b/c I've not been able to find anything in the IRC.

Any help would be appreciated.

thanks,
Bruce
Attached Images
File Type: jpg meter base.jpg (57.5 KB, 104 views)



Bruce Thompson
NACHI 06081394
Tyler, Texas
Reply With Quote
  #2  
Old 10/14/08, 8:22 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,888
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Meter base being used as workbox

It's permitted, by the NEC, as long as the gutter fill in the meter base is not exceeded (I seriously doubt it's even remotely close to that limit). The power company, however, will very much frown on that. In fact, they wouldn't hook up a service if I was to build something like that new today. If that homeowner ever has any problems with his service to the extent that the PoCo is ever involved, it's quite likely he'll get a 30 day notice to correct that to their rules (aka get a "red tag") or face disconnection of utility power.
Reply With Quote
Old 10/14/08, 8:30 PM
jtedesco1
This message has been deleted by jtedesco1.
  #3  
Old 10/14/08, 8:38 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Location: NY State
Posts: 1,273
Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Meter base being used as workbox

Is that the only meter on the house? It looks as if this could be a demand meter for the A/C.

Is the service entrance coming out of the back of the meter box? Or is that the only load on the meter?

If this is the only meter on the house then yes, this is a BIG no-no.
Reply With Quote
  #4  
Old 10/14/08, 9:18 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 454
Bruce Thompson is often very helpful Bruce Thompson is often very helpful Bruce Thompson is often very helpful
Default Re: Meter base being used as workbox

Thanks to everyone!

Marc, what is gutter fill?

Mr. Tedesco, thanks for the information. I've watched all 3 of your videos. Very good stuff for guys like me.

Speedy, it is the only meter and not a demand meter.

very humbly,
Bruce



Bruce Thompson
NACHI 06081394
Tyler, Texas

Last edited by bthompson1; 10/14/08 at 9:18 PM. Reason: misspelled Marc's name
Reply With Quote
  #5  
Old 10/14/08, 9:34 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 9,665
Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute Marcel R. Cyr has a reputation beyond repute
Default Re: Meter base being used as workbox

Hey, while you guys were busy with the Electrical, did you notice the lousy Brick Job. ha. ha.



Cyr Home Inspections
IAC2 Certified
NACHI04070211

http://co.nachi.org/inachiawards/inachiawards551.html
http://co.nachi.org/inachiawards


Commercial Builder
Ouellet Associaties Inc.
Reply With Quote
  #6  
Old 10/14/08, 9:44 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 454
Bruce Thompson is often very helpful Bruce Thompson is often very helpful Bruce Thompson is often very helpful
Default Re: Meter base being used as workbox

Quote:
Originally Posted by mcyr View Post
Hey, while you guys were busy with the Electrical, did you notice the lousy Brick Job. ha. ha.
come on...that's 1966 art!!!



Bruce Thompson
NACHI 06081394
Tyler, Texas
Reply With Quote
  #7  
Old 10/14/08, 9:49 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,888
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Meter base being used as workbox

That Greenfield change is pretty much brand spanking new. For all of history, until the 2008 NEC, Greenfield was allowed outdoors. Why it was ever permitted in the first place is anyone's guess. It was a stupid wiring method for outside.
Reply With Quote
  #8  
Old 10/14/08, 9:54 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Location: NY State
Posts: 1,273
Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information Speedy Petey is very trusted source of information
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Meter base being used as workbox

Quote:
Originally Posted by Marc D. Shunk View Post
That Greenfield change is pretty much brand spanking new. For all of history, until the 2008 NEC, Greenfield was allowed outdoors. Why it was ever permitted in the first place is anyone's guess. It was a stupid wiring method for outside.
I agree entirely.

I will say though. That looks to me to be older than (at most) 10 months.
Reply With Quote
Old 10/14/08, 10:08 PM
jtedesco1
This message has been deleted by jtedesco1.
  #9  
Old 10/14/08, 11:05 PM
Joe Farsetta's Avatar
Joe Farsetta Joe Farsetta is offline
ESOP Committee Member
 
Join Date: Oct 2002
Location: Pearl River, NY
Posts: 2,886
Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute Joe Farsetta has a reputation beyond repute
Default Re: Meter base being used as workbox

Hey Sparkies, including Joltin' Joe Tedesco...

The installation pre-exists any changes to the NEC, and is therefore likely grandfathered.

To my knowledge, Marc is correct, though I havent ever seen it done this way.

Is it an AC disco, or the main disco?

By the way... that's a DIGITAL meter. It is likely that the utility is fully aware of this installation and has blessed it, as the meter looks newer than the adjacent box. Since the utility is typically the ultiumate AHJ, this is likely a non-issue in their eyes.

Last edited by jfarsetta; 10/14/08 at 11:09 PM.
Reply With Quote
  #10  
Old 10/14/08, 11:17 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,888
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Meter base being used as workbox

Quote:
Originally Posted by jfarsetta View Post
By the way... that's a DIGITAL meter. It is likely that the utility is fully aware of this installation and has blessed it, as the meter looks newer than the adjacent box. Since the utility is typically the ultiumate AHJ, this is likely a non-issue in their eyes.
Don't bet money on it. The lion's share of the digital and AMR meter change outs are historically being done by subcontractors.
Reply With Quote
  #11  
Old 10/14/08, 11:22 PM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 454
Bruce Thompson is often very helpful Bruce Thompson is often very helpful Bruce Thompson is often very helpful
Default Re: Meter base being used as workbox

It is an HVAC disconnect. I did think about the newer meter, but was still bumfuzzled.

FYI, my meter was actually changed by the PoCo.



Bruce Thompson
NACHI 06081394
Tyler, Texas
Reply With Quote
  #12  
Old 10/14/08, 11:28 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,888
Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information Marc D. Shunk is very trusted source of information
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Meter base being used as workbox

Quote:
Originally Posted by bthompson1 View Post
FYI, my meter was actually changed by the PoCo.
You're still going to put text in your report, addressing this as a potential problem, from an administrative standpoint, I guess? Just for my own curiosity's sake, do you happen to know the name of the power company that serves the meter in your picture? I'm going to see if I can scare up a link to their rules book.
Reply With Quote
  #13  
Old 10/15/08, 12:07 AM
Bruce Thompson's Avatar
Bruce Thompson Bruce Thompson is offline
InterNACHI Member
 
Join Date: Sep 2006
Location: Tyler, TX
Posts: 454
Bruce Thompson is often very helpful Bruce Thompson is often very helpful Bruce Thompson is often very helpful
Default Re: Meter base being used as workbox

Quote:
Originally Posted by Marc D. Shunk View Post
You're still going to put text in your report, addressing this as a potential problem, from an administrative standpoint, I guess? Just for my own curiosity's sake, do you happen to know the name of the power company that serves the meter in your picture? I'm going to see if I can scare up a link to their rules book.
I did. I addressed the fact that the poco will not like it and Mr. Tedesco's comment about the FMC.

http://www.txu.com/

so what is gutter fill?



Bruce Thompson
NACHI 06081394
Tyler, Texas
Reply With Quote
Old 10/15/08, 4:46 AM
jtedesco1
This message has been deleted by jtedesco1.
  #14  
Old 10/15/08, 7:26 AM
Joseph M. Whitt Joseph M. Whitt is offline
InterNACHI Member
 
Join Date: Oct 2008
Location: NC
Posts: 42
Joseph M. Whitt is generally well trusted
Default Re: Meter base being used as workbox

I think that there are far worse problems than the worry of the flex. Gosh with all these experts posting one would think that at least one of them would address the real issues.

First is that is one of the first disconnects from the point of delivery which means the disconnect MUST be service rated.

Second if there is more than that one disconnect then all the other disconnect supplied from that meter are REQUIRED to be grouped.

I would not even mention the use of the flex in my report but instead I would mention the two items above that need immediate attention and are a far more safety hazard than the flex.
Reply With Quote
  #15  
Old 10/15/08, 7:35 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 6,358
David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute David P. Valley has a reputation beyond repute
Default Re: Meter base being used as workbox

Quote:
Originally Posted by bthompson1 View Post
so what is gutter fill?
Brian,

Take a look at the image below. See all the wires crammed into the sides of the electrical panel (which caused an arc)? Well, that tight area (where the wires are sitting) is "the gutter fill".