Default Meter base size

Meter base is not square, is this a 200 amp base?
Service panel is rated at 125, conductor to service panel is rated 125, main breaker is 125. Service to meter is not visible.
Thanks.
Attached Thumbnails
meter-base-size-img_9930-small-.jpg.jpg
Views:	334
Size:	30.1 KB
ID:	17180  
Reply With Quote
  #2  
Old 1/3/08, 10:57 PM
brian winkle brian winkle is offline
Active Poster
 
Join Date: Sep 2005
Location: Arizona
Posts: 454
Please Note: brian winkle is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Meter base size

The only way to know for sure is to look inside the meter can, which is pretty much a non option for most.
Reply With Quote
  #3  
Old 1/3/08, 11:06 PM
Al D. Bolt Al D. Bolt is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Twin Falls, ID
Posts: 97
Default Re: Meter base size

According to the NACHI Electrical Course, which says a square meter base is 100 amp and a rectangular meter base is 200 amp, this should be a 200 amp base. Any refutations?
Reply With Quote
  #4  
Old 1/3/08, 11:10 PM
James E. Braun, CMI's Avatar
James E. Braun, CMI James E. Braun, CMI is offline
InterNACHI Member
 
Join Date: Jan 2005
Location: Jefferson City, MO
Posts: 6,945
Default Re: Meter base size

It does not matter. The system is only as big as the smallest component.
Reply With Quote
  #5  
Old 1/4/08, 7:07 AM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Meter base size

Quote:
Originally Posted by abolt
According to the NACHI Electrical Course, which says a square meter base is 100 amp and a rectangular meter base is 200 amp, this should be a 200 amp base. Any refutations?
Yes, this assertion is absolutely false.
That IS a 100A meter pan. I only know this from experience. Others may not know just from looking at it.

James is 100% correct. It would not matter a lick if that were a 200A meter pan. While everything is "rated" at 125 amps I bet the main breaker still says 100A.
It's a 100A service.
Reply With Quote
  #6  
Old 1/4/08, 12:09 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Meter base size

Pepco (DC/Md/Va) installed a 200a service in that type of meter base in the 70s.
Reply With Quote
  #7  
Old 1/4/08, 12:46 PM
Al D. Bolt Al D. Bolt is offline
InterNACHI Member
 
Join Date: Dec 2006
Location: Twin Falls, ID
Posts: 97
Default Re: Meter base size

I agree the system is only as big as the smallest component. The original post states everything else including the main breaker is 125. My concern is the meter. If it is only 100, then the system is 100. If it is 200, the system is 125.
According to the NACHI course it is 200. Some don't agree with this. I'm seeking input regarding the meter size to size the system.
Thanks.
Reply With Quote
  #8  
Old 1/4/08, 2:05 PM
jtedesco1 jtedesco1 is offline
Account Suspended Due to Excessive Complaints
 
Join Date: Dec 2005
Posts: 1,891
Please Note: jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Meter base size

Quote:
Originally Posted by abolt
Meter base is not square, is this a 200 amp base?
Service panel is rated at 125, conductor to service panel is rated 125, main breaker is 125. Service to meter is not visible.
Thanks.
Al:

I like to look at the local utility rules, here is a file in you area I found that may be of help:

Meter Base

More here too: Milbank

You can find information here as well: www.themeterguy.com

Last edited by jtedesco1; 1/4/08 at 2:54 PM..
Reply With Quote
  #9  
Old 1/4/08, 2:15 PM
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Spotsylvania, VA
Posts: 8,072
Send a message via AIM to pabernathy Send a message via MSN to pabernathy Send a message via Skype™ to pabernathy
Default Re: Meter base size

I would say watch my online video regarding it. You can't assue anything based on the meter can....plus its a POCO thing....so exclude it and go with what is known......Panel Rating, Conductors Size and OCPD size.......those factors based on the weakest link theory is the method to use......remember the meter can is part of the analysis.....and may lead to confirmation of the other 3 items.....but alone never rely on the meter can........

The online course helps you understand concepts and general sizes but is only a stepping stone to the entire process.



Paul W. Abernathy
Reply With Quote
  #10  
Old 1/4/08, 5:31 PM
Speedy Petey Speedy Petey is offline
Unmoderated Guest
 
Join Date: Jul 2006
Posts: 1,297
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Meter base size

Quote:
Originally Posted by pabernathy
I would say watch my online video regarding it. You can't assue anything based on the meter can....plus its a POCO thing....so exclude it and go with what is known......Panel Rating, Conductors Size and OCPD size.......those factors based on the weakest link theory is the method to use......remember the meter can is part of the analysis.....and may lead to confirmation of the other 3 items.....but alone never rely on the meter can........
This is excellent advice.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
meter base size bthompson1 Electrical Inspections 5 1/30/07 10:14 PM
Metal Rigid or PVC Rigid what is code bpotts Electrical Inspections 5 12/4/06 2:40 PM