  #1  
Old 3/4/09, 4:34 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Meter Box

Was this type of meter base ever approved for 100 amp?



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!

Last edited by ccurrins; 4/20/09 at 12:47 AM..
Reply With Quote
  #2  
Old 3/4/09, 8:49 PM
gbeaumont's Avatar
gbeaumont gbeaumont is offline
InterNACHI Member
 
Join Date: Jan 2003
Location: Clearwater, FL
Posts: 6,261
Send a message via AIM to gbeaumont Send a message via MSN to gbeaumont Send a message via Yahoo to gbeaumont
Default Re: Meter Box

Quote:
Originally Posted by ccurrins View Post
Was this type of meter base ever approved for 100 amp?
Yes, that is a typical 100amp base and some were rated at 125 amp

Regards

Gerry



"To realize our true destiny, we must be guided not by a myth from our past, but by a vision of our future."
(Mark B Adams)

Commercial property Inspection Tampa, Orlando, Sarasota, Jacksonville, Ft Launderdale, Miami, Florida.
NACHI cell 484-429-5466
NACHI02121106

Reply With Quote
  #3  
Old 3/4/09, 9:01 PM
wsiegel wsiegel is offline
Active Poster
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 2,649
Please Note: wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Meter Box

It could be rated for more, but most likely not.
Reply With Quote
  #4  
Old 3/4/09, 9:10 PM
Christopher Currins's Avatar
Christopher Currins Christopher Currins is offline
InterNACHI Member
 
Join Date: Feb 2007
Location: Godfrey, IL
Posts: 7,626
Default Re: Meter Box

Quote:
Originally Posted by gbeaumont View Post
Yes, that is a typical 100amp base and some were rated at 125 amp

Regards

Gerry
Thanks Gerry and William for reassuring me. I agree and didn't mention it in my report as a defect.
But the local AHJ says the base must be replaced before they'll issue an occupancy permit.

Nothing else, only the meter base. He said the rounded box was not approved for 100 amp.



Christopher Currins
Certified, Licensed

Proudly serving the St.Louis Metro

St. Charles, St. Peters, Maryland Heights,
O'Fallon, Florrisant, MO Home Inspector




BLESSED ARE THE CRACKED, FOR THEY ARE THE ONES WHO LET IN THE "LIGHT"!
Reply With Quote
  #5  
Old 3/8/09, 9:22 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 668
Default Re: Meter Box

The AHJ always has the final word, so if he says it must be replaced, it must, regardless of 'code' or other basis. Of course, you could try to apply reason and logic, but that probably would not work either. Around here, the PoCo furnishes the meter base, so whatever they choose to furnish is generally ok with the AHJ.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Rectangular Box, 100CL Meter nwagner Electrical Inspections 2 3/25/08 5:51 PM
City electrical inspector says move the meter and panel cbottger Electrical Inspections 9 4/4/07 8:59 PM
Panel and Meter jwilliams7 Electrical Inspections 10 6/21/06 5:49 PM


All times are GMT -4. The time now is 7:43 AM.


Popular Sections

:

All Sections

Inspection News

InterNACHI Membership

Inspection Standards

Inspection Education

InterNACHI Inspectors

Inspection Links

 

 

 

NACHI.ORG Statistics

 

 

no new posts