InterNACHI


Go Back   InterNACHI Message Board > Specific Inspection Topics > Electrical

Notices

Electrical Contains discussions about electrical systems. This includes outlets, panels, wiring, et cetera.

Reply
 
LinkBack Thread Tools
  #1  
Old 6/29/09, 5:02 PM
Billy J. Clark's Avatar
Billy J. Clark Billy J. Clark is offline
InterNACHI Member
 
Join Date: Jan 2004
Location: Mustang, OK
Posts: 67
Default Meter load

I did an inspection for an individual back in March. She called me today because over the weekend she smelled smoke and said her house almost caught fire. She filed an emergency work order through her warranty company and that sent an electrician right over. He said what happened is the meter is overloaded and that she should contact the home inspector that he should have caught this. My understanding is we are not required to inspect the inside load of the meter. All meters are tagged shut and sometimes locked and only accessible by the electric companies and electricians.
Where do I stand on this and what should I tell the lady. I am going to visit with her today @ 5 central time.
Thanks, for all your help guys.



Thanks Billy,
President, CORE Home Inspections, LLC
"Committed to Excellence"
Visit: www.corehomeinspections.com
Reply With Quote
Find an InterNACHI certified Tennessee Home Inspector (and anywhere else in North America)
  #2  
Old 6/29/09, 5:08 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,730
Default Re: Meter load

Quote:
Originally Posted by bclark View Post
I did an inspection for an individual back in March. She called me today because over the weekend she smelled smoke and said her house almost caught fire. She filed an emergency work order through her warranty company and that sent an electrician right over. He said what happened is the meter is overloaded and that she should contact the home inspector that he should have caught this. My understanding is we are not required to inspect the inside load of the meter. All meters are tagged shut and sometimes locked and only accessible by the electric companies and electricians.
Where do I stand on this and what should I tell the lady. I am going to visit with her today @ 5 central time.
Thanks, for all your help guys.

It is hard to believe that warranty company's electrician wants to pass liability to the home inspector.

We don't pull the meter around here.

Still, I'd go over and listen to the lady and do what I could to help her be safe.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #3  
Old 6/29/09, 5:29 PM
Rick Maday's Avatar
Rick Maday Rick Maday is offline
InterNACHI Member
 
Join Date: Jan 2008
Location: Itasca, IL
Posts: 4,591
Default Re: Meter load

Quote:
Originally Posted by lkage View Post
It is hard to believe that warranty company's electrician wants to pass liability to the home inspector.

We don't pull the meter around here.

Still, I'd go over and listen to the lady and do what I could to help her be safe.
Agreed. What did your report say about the electrical conditions?



Owl Home Inspections
Rick Maday
Itasca, IL


Home Inspector Serving all Chicago Suburbs

Schaumburg Home Inspector
Naperville Home Inspector
Lake County Home Inspector
Reply With Quote
  #4  
Old 6/30/09, 11:34 AM
Darren Spencer Darren Spencer is offline
InterNACHI Member
 
Join Date: Nov 2007
Location: Bellevue, WA
Posts: 509
Default Re: Meter load

Cutting meter tag is tampering and not permitted. What does a Warranty Company know about inspections anyway? ...sorry Ben.




Need a Link Exchange? Inspector Links


Seattle,WA Commercial Inspectors

Reply With Quote
  #5  
Old 6/30/09, 7:41 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Libertyville, Il
Posts: 448
Default Re: Meter load

you don't need to open up the can to look at the rating of the meter. It'll state right on the meter itself

Jeff



Jeff Wicklander
Corwick Home Services
224-715-0457
Reply With Quote
  #6  
Old 6/30/09, 8:21 PM
William E. Siegel William E. Siegel is online now
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: Meter load

I. The inspector shall inspect:
A. the service drop/lateral;
B. the meter socket enclosures;


This is all it says about insepecting the meter in the standards. No mention of not pulling the meter. I agree that we should not be doing this, but, if you say you follow the SOP, a problem could arise. Perhaps there needs to be a change to the standards.




Bill Siegel
Florida Home Inspection Team Inc.
Reply With Quote
  #7  
Old 6/30/09, 8:30 PM
Jeffrey R. Wicklander's Avatar
Jeffrey R. Wicklander Jeffrey R. Wicklander is offline
InterNACHI Member
 
Join Date: Mar 2008
Location: Libertyville, Il
Posts: 448
Default Re: Meter load

If you want to measure the amperage across the meter, just throw a clamp on the SE cables on the line side of the main panel. We don't throw the main disconnect on our inspections, why would we pull the meter??

Jeff



Jeff Wicklander
Corwick Home Services
224-715-0457
Reply With Quote
  #8  
Old 7/6/09, 2:13 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Meter load

Quote:
Originally Posted by jwicklander View Post
If you want to measure the amperage across the meter, just throw a clamp on the SE cables on the line side of the main panel. We don't throw the main disconnect on our inspections, why would we pull the meter??

Jeff
I guess they could but it would be subjective to the load being drawn at the time of the "clamping". I do not believe an HI need's to venture down that path as it is beyond the scope of the typical home inspection. When looking at a meter you will see many things on but for one usually you will see something like CL 200. Typically that is the Class 200 model but as we have talked about before it should not be relied on to determine anything in the service sizing...just as additional confirmation to what the other factors have told us in our examination of the service.

If the meter socket looked fine, no signs of corrosion or damage and the service was sized based on the given factors and you reported all this properly then you are fine, You have done what the SOP has allowed.

FYI- I am a licensed master electrician and well I know a little about electricity and I would never venture into a "LIVE" meter socket enclosure.....I prefer not to BANG on my CHEST like some other electricians do to "get the job done". I do not work on things "LIVE"....period. Now, I have to when doing diagnostic work but we are talking about cutting a tag off a meter and so on....you wont catch me doing it.....simply not worth the possibilities.

BTW- Most all of that was not directed at your response Jeff...I was simply rambling on for those electricians out thier who like to pull meter sockets...."Just to get the job done"....no job is worth a life.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"


Last edited by pabernathy; 7/6/09 at 2:18 PM..
Reply With Quote
  #9  
Old 7/9/09, 7:09 PM
Frank P. Newman Frank P. Newman is offline
InterNACHI Member
 
Join Date: Aug 2007
Location: Dublin, GA
Posts: 505
Default Re: Meter load

This situation is part of the reason our AHJ requires a main disconnect outside the home, usually next to the meter. Nearly all home built in many years can be easily disconnected in an emergency without touching the meter. Besides, many larger homes have 400 amp service (usually dual 200 amp lugs). Pulling that meter would only disconnect the CTs.



Frank P. Newman
Emerald City Inspections, LLC
Dublin, GA
Reply With Quote
  #10  
Old 7/9/09, 10:06 PM
Wayne B. Wilson's Avatar
Wayne B. Wilson Wayne B. Wilson is offline
InterNACHI Member
 
Join Date: Aug 2008
Location: Powell, Tn
Posts: 2,442
Default Re: Meter load

LOL i had one last night call said all the wires where burnt, I ran over and the utility company was there , He had already told the lady there was no way the home inspector could have seen this , the clips came loose in the meter base.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
cut floor joice John E. Gibson, #2 General Inspection Discussion 16 9/25/08 10:45 PM
Where do I put the Aquarium? mcyr Structural 3 11/6/07 4:05 PM


All times are GMT -4. The time now is 9:53 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts