#1
|
||||
|
||||
|
I did an inspection for an individual back in March. She called me today because over the weekend she smelled smoke and said her house almost caught fire. She filed an emergency work order through her warranty company and that sent an electrician right over. He said what happened is the meter is overloaded and that she should contact the home inspector that he should have caught this. My understanding is we are not required to inspect the inside load of the meter. All meters are tagged shut and sometimes locked and only accessible by the electric companies and electricians.
Where do I stand on this and what should I tell the lady. I am going to visit with her today @ 5 central time. Thanks, for all your help guys. Thanks Billy, President, CORE Home Inspections, LLC "Committed to Excellence" Visit: www.corehomeinspections.com |
| Find an InterNACHI certified Tennessee Home Inspector (and anywhere else in North America) |
|
#2
|
|||
|
|||
|
Quote:
It is hard to believe that warranty company's electrician wants to pass liability to the home inspector. We don't pull the meter around here. Still, I'd go over and listen to the lady and do what I could to help her be safe. ____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#3
|
||||
|
||||
|
Agreed. What did your report say about the electrical conditions?
Owl Home Inspections Rick Maday Itasca, IL Home Inspector Serving all Chicago Suburbs Schaumburg Home Inspector Naperville Home Inspector Lake County Home Inspector
|
|
#4
|
|||
|
|||
|
Cutting meter tag is tampering and not permitted. What does a Warranty Company know about inspections anyway? ...sorry Ben.
![]() |
|
#5
|
||||
|
||||
|
you don't need to open up the can to look at the rating of the meter. It'll state right on the meter itself
Jeff |
|
#6
|
|||
|
|||
|
I. The inspector shall inspect:
A. the service drop/lateral; Bill Siegel Florida Home Inspection Team Inc. |
|
#7
|
||||
|
||||
|
If you want to measure the amperage across the meter, just throw a clamp on the SE cables on the line side of the main panel. We don't throw the main disconnect on our inspections, why would we pull the meter??
Jeff |
|
#8
|
||||
|
||||
|
Quote:
If the meter socket looked fine, no signs of corrosion or damage and the service was sized based on the given factors and you reported all this properly then you are fine, You have done what the SOP has allowed. FYI- I am a licensed master electrician and well I know a little about electricity and I would never venture into a "LIVE" meter socket enclosure.....I prefer not to BANG on my CHEST like some other electricians do to "get the job done". I do not work on things "LIVE"....period. Now, I have to when doing diagnostic work but we are talking about cutting a tag off a meter and so on....you wont catch me doing it.....simply not worth the possibilities. BTW- Most all of that was not directed at your response Jeff...I was simply rambling on for those electricians out thier who like to pull meter sockets...."Just to get the job done"....no job is worth a life. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" Last edited by pabernathy; 7/6/09 at 2:18 PM.. |
|
#9
|
|||
|
|||
|
This situation is part of the reason our AHJ requires a main disconnect outside the home, usually next to the meter. Nearly all home built in many years can be easily disconnected in an emergency without touching the meter. Besides, many larger homes have 400 amp service (usually dual 200 amp lugs). Pulling that meter would only disconnect the CTs.
Frank P. Newman Emerald City Inspections, LLC Dublin, GA |
|
#10
|
||||
|
||||
|
LOL i had one last night call said all the wires where burnt, I ran over and the utility company was there , He had already told the lady there was no way the home inspector could have seen this , the clips came loose in the meter base.
|
![]() |