It's likely that the yellow cord cap is not listed for connection to AC cable, MC cable or a metallic flexible raceway.
|
|
#3
|
||||
|
||||
|
Should have a junction box there with a wall plate preferably.
|
|
#4
|
||||
|
||||
|
Putting a plug (female) on the end of permanent wiring basically turns it into an extension cord which is not to be used for permanent wiring in the home. As stated, should have terminated in a J box with an approved receptacle. So, Yes, I have a problem with it.
"War is an ugly thing, but not the ugliest of things; the decayed and degraded state of moral and patriotic feeling which thinks nothing is worth a war, is worse. A man who has nothing which he cares more about than he does about his personal safety is a miserable creature who has no chance at being free, unless made and kept so by the exertions of better men than himself." - John Stuart Mill |
|
#5
|
||||
|
||||
|
Quote:
|
|
#6
|
||||
|
||||
|
Since that type of socket end even comes loose when attached to a extension cord.BX or armored cable is double trouble.
1st The attachment cannot be secured properly 2nd It will never be used by electrician in this application. 3rd If it does not have a good tight connection it will not trip the breaker first and is a fire hazard. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#7
|
||||
|
||||
|
Quote:
I think it's a stretch to call it an extension cord as Doug mentioned, unless of course the end we cannot see has a similar arrangement. 774 Manor Road Staten Island, NY 10314 718-514-3393 |
|
#8
|
||||
|
||||
|
It is not an extension cord. It is either a BX armored cable or a BX protected sheaving.
THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#9
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
Quote:
Judging from the photo I am guessing that it is any one of the three wiring methods (AC cable, MC cable or FMC) that I mentioned. Unless that's a special cord cap it's not listed to be terminated as shown in the photo. Normally we would just use a surface Wiremold box and receptacle for this application. |
|
#10
|
||||
|
||||
|
OPPS! I meant sheathing.
A note about it being BX it will not have a ground wire so if it does it might be new AC or MC armored cable. THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#11
|
||||
|
||||
|
Some BX runs a ground wire through it.
|
|
#12
|
||||
|
||||
|
[Correct] only the original 1960s BX has no ground.
THE RIGHT TRAK CIAQP, IAC2 Certified Master Inspector kwoodinspections@hotmail.com www.kwood.inspectorpages.com www.homegauge.com/shgi/THERIGHTTRAKIAQ www.linkedin.com/in/kevinwoodiaq OOVOO account kwoodinspections Cell: 705-971-2096 Ph : 705-946-2676 |
|
#13
|
||||
|
||||
|
Please Note:
Robert Meier is a non-member guest and is in no way affiliated with InterNACHI or its members.
Are you referring to the thin aluminum bonding strip within AC cable? |
| Need a home inspection in Oklahoma? Check out InterNACHI's listing of Oklahoma certified home inspectors. Or, find a home inspector anywhere in the world with our inspection search engine. |
|
#14
|
||||
|
||||
|
Quote:
774 Manor Road Staten Island, NY 10314 718-514-3393 |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| Help. What is the correct way to report a breaker that is too big. | gromicko | Electrical Inspections | 77 | 5/10/12 6:13 PM |
| Microwave oven testing? | badair | Miscellaneous Discussion for Inspectors | 26 | 3/11/09 7:53 PM |
| Microwave receptacle | jwardenski | Electrical Inspections | 17 | 9/9/07 7:18 PM |
| Romex connected to male plug... OK? | ghawley | Electrical Inspections | 20 | 3/4/07 6:05 PM |