I usually find the microwave plug coming through a hole in the cabinets and plugged into a receptacle in the cabinet above. I thought it was required. I just finished an inspection and no plug was found. It was obviously installed behind the microwave.

Does a receptacle for a built in microwave (non-vent hood type) have to be accessible?

Thanks in advance!
Reply With Quote
  #2  
Old 9/8/07, 1:39 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Microwave receptacle

ABSOLUTELY!

What you describe sounds odd. There is literally no room behind one of those things for a receptacle. And the cord MUST come out the top.
Reply With Quote
  #3  
Old 9/8/07, 2:15 PM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Microwave receptacle

Jerry,

It's always great to know all the answers, but I try to make my inspection life easy.

If I find something in a home that is questionable or appears unsafe, defective, odd or out of place in any way, I simply note it in the report. I don't burden myself with code compliances. That way you can finish the report without a lot of research.
Reply With Quote
  #4  
Old 9/8/07, 9:30 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Microwave receptacle

There's a home inspector in my area that finds these "missing" microwave cords pretty regularly. I get to remediate some of them. What I normally find is that the microwave/hood replaced a regular exhaust hood at some point in time. The installers would either cut the plug off the microwave and wire nut it to the old hood romex cable, or they'd put a cord cap on the end of the romex cable, plug the microwave into that, and stuff the whole works back in a large hole in the drywall behind the microwave. There's often about a 1/2" recess in the cabinet bottom above; just enough to get the cord to lay flat and go into the hole in the drywall. I suspect very much that this is what you're dealing with there. A non-compliant, handyman type micro-hood installation.
Reply With Quote
  #5  
Old 9/9/07, 12:12 AM
jwardenski jwardenski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Houston, TX
Posts: 4
Default Re: Microwave receptacle

The microwave is mounted inside a cabinet that houses the microwave and a built-in oven below it. There is cabinet space above and below the two units. Five feet away is the cooktop and vent hood. It is new construction.
Reply With Quote
  #6  
Old 9/9/07, 2:08 AM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Microwave receptacle

Without actually pulling the microwave out, I am not sure you know if you have a violation. As far as I know the plug of a cord and plug connected appliance only has to be "accessible", it doesn't need to "readily accessible"
Reply With Quote
  #7  
Old 9/9/07, 3:29 AM
jwardenski jwardenski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Houston, TX
Posts: 4
Default Re: Microwave receptacle

Anyone know what code covers this...IRC...NEC?
Reply With Quote
  #8  
Old 9/9/07, 6:47 AM
Brian A. MacNeish Brian A. MacNeish is offline
Active Poster
 
Join Date: Apr 2007
Posts: 2,382
Please Note: Brian A. MacNeish is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Microwave receptacle

Quote:
Originally Posted by Greg Fretwell
Without actually pulling the microwave out, I am not sure you know if you have a violation. As far as I know the plug of a cord and plug connected appliance only has to be "accessible", it doesn't need to "readily accessible"
Our Canadian Electrical Code has this as a requirement with only the single microwave outlet allowed on the circuit. Seems reasonable.
Reply With Quote
  #9  
Old 9/9/07, 7:37 AM
David P. Valley's Avatar
David P. Valley David P. Valley is offline
InterNACHI Member
 
Join Date: Jun 2003
Location: METHUEN, MA
Posts: 8,020
Default Re: Microwave receptacle

The 2002 NEC states...

422.16 Flexible Cords (A) General. Flexible cord shall be permitted (1) for the connection of appliances to facilitate their frequent interchange or to prevent the transmission of noise or vibration or (2) to facilitate the removal or disconnection of appliances that are fastened in place, where the fastening means and mechanical connections are specifically designed to permit ready removal for maintenance or repair and the appliance is intended or identified for flexible cord connection.”

It should be understood that a cord-connected appliance is required to be specifically designed, mechanically and electrically, to be readily removable for maintenance and repair.
Reply With Quote
  #10  
Old 9/9/07, 9:22 AM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,355
Default Re: Microwave receptacle

I believe it should look somewhat like this.

Attachment 14381

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/

Last edited by mcyr; 2/2/08 at 9:12 PM..
Reply With Quote
  #11  
Old 9/9/07, 9:46 AM
Leonard E. Ungar's Avatar
Leonard E. Ungar Leonard E. Ungar is offline
InterNACHI Member
 
Join Date: Oct 2003
Location: Bayport, NY
Posts: 348
Default Re: Microwave receptacle

David;
I like your #3 post short & sweet. That's the way I also do it if possible.
Len
Reply With Quote
  #12  
Old 9/9/07, 1:06 PM
Greg Fretwell Greg Fretwell is offline
Active Poster
 
Join Date: Jul 2004
Location: Estero Florida
Posts: 1,798
Please Note: Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Microwave receptacle

David, 422.16 refers to when you are allowed to "cord and plug" an appliance that would normally be hardwired. It still does not address the issue of whether the cord cap itself shall remain "readily" accessible.
As long as you can unplug this as a normal part of removing the microwave I don't see the issue. You will need to pull it out before you can work on it anyway. We have a similar situation with "built in" dishwashers where the cord and plug are behind the dishwasher. For that matter the receptacle behind the fridge is not readily accessible either.
Wasn't that the basis for allowing the "no GFCI" exception for washing machines, garage door openers and freezers in basements and garages?
Quote:
210.8(A)(4) 2002NEC Exception No. 1: Receptacles that are not readily accessible.
Reply With Quote
  #13  
Old 9/9/07, 1:15 PM
jwardenski jwardenski is offline
InterNACHI Member
 
Join Date: Apr 2007
Location: Houston, TX
Posts: 4
Default Re: Microwave receptacle

Thanks David! That's the information I was looking for. I realize I cannot know it all but when I have a question about something I believe to be true, I like to be able to confirm or deny it. Research makes me a better inspector. Otherwise it is only CYA.

The picture in Marcel's post #10 is what I usually see and what I believed it should be, now I'm sure.

Thanks to all the others who replied as well!
Reply With Quote
  #14  
Old 9/9/07, 3:07 PM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Microwave receptacle

Quote:
Originally Posted by jwardenski
The picture in Marcel's post #10 is what I usually see and what I believed it should be, now I'm sure.
Actually not!
I misunderstood the original description. I see now that it is NOT a typical OTR micro.
In your case it very well MAY be right behind the micro and is perfectly fine. "Built-in", as in sitting on a dedicated shelf is a TOTALLY different thing than a built-in OTR micro/hood.

I bet the installation in question is perfectly fine.
Reply With Quote
  #15  
Old 9/9/07, 3:29 PM
Marcel R. Cyr's Avatar
Marcel R. Cyr Marcel R. Cyr is online now
InterNACHI Member
 
Join Date: Jul 2004
Location: Winslow, ME
Posts: 12,355
Default Re: Microwave receptacle

Maybe this is what you are talking about, and the receptacle is behind the unit.

http://www.kitchenaid.com/assets/pdf...LL/8205303.pdf
http://www.sharpusa.com/files/hso_dow_builderguide.pdf

Marcel




Cyr Home and Commercial Property Inspections

IAC2 Certified
NACHI04070211
http://co.nachi.org/inachiawards


Commercial Builder
CertainTeed
Master Shingle Applicator
Shingle Technology
Ouellet Associaties Inc.
http://www.oaconstruction.com/
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
What's This Receptacle For? cmettel Electrical 7 5/25/07 8:35 AM
Bedroom receptacle dnasser Electrical 9 4/16/07 11:33 AM
Amprobe Microwave Leak Detector rgant Interior 15 2/22/07 6:41 PM
Receptacle for a microwave dmacy Electrical 12 1/31/07 1:02 PM
Online Code Check- Reference pabernathy Electrical 31 11/9/06 4:39 PM


All times are GMT -4. The time now is 9:25 PM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts