Default Minimum Size Breaker for Sub Panel

Can someone tell me what the MINIMUM size breaker is to supply a fairly large and full sub panel, (17 breakers, 2 of the 30 amp and the rest 15 and 20 amp breakers). I had one that the Main is not labeled, of course and can not tell what breaker the sub is being fed by. I do know that the supply wire to the sub is only a number 6, which is good for up to a 60 amp breaker. 60 amps does not seem to be big enough, to me.
Thanks, Rick
Reply With Quote
  #2  
Old 5/19/07, 10:53 AM
Speedy Petey Speedy Petey is offline
Active Poster
 
Join Date: Jul 2006
Posts: 1,294
Please Note: Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Minimum Size Breaker for Sub Panel

Quote:
Originally Posted by rmoewe
60 amps does not seem to be big enough, to me.
What do you base this on? Have you done a load calculation? Do you know what loads are served by this panel?
What if one 30 is feeding A/C and the other is feeding electric heat? What if the rest are feeding simple general receptacles and lighting?

See what I am getting at? If you've ever done a load calc on a home you'd see the actual demand load is not usually what you would think. It is very typical to have a fully loaded 40 space 200 amp panel with a demand load of under 150 amps.
Reply With Quote
  #3  
Old 5/19/07, 11:26 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Minimum Size Breaker for Sub Panel

Quote:
Originally Posted by rmoewe
Can someone tell me what the MINIMUM size breaker is to supply a fairly large and full sub panel,
Yes, I'd be glad to do that load calc for you, but I'd need a ton more information. Counting breakers is a really goofy way to determine whether the feeder is properly sized or not. Square footage, connected load data plate information, and kilowatts of heat, etc are some of the types of information that would be needed. Really hard to say without that information. Do you at least have the panel schedule labeling for each of those breakers, and we can maybe hazard a guess as to whether it's definitely not okay?
Reply With Quote
  #4  
Old 5/19/07, 3:25 PM
rmoewe's Avatar
rmoewe rmoewe is offline
Active Poster
 
Join Date: Nov 2003
Location: Brentwood, TN
Posts: 134
Please Note: rmoewe is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Minimum Size Breaker for Sub Panel

The panel in not labled.
Reply With Quote
  #5  
Old 5/20/07, 7:15 PM
pdoane's Avatar
pdoane pdoane is offline
Active Poster
 
Join Date: Dec 2005
Location: Olympia, WA
Posts: 2,040
Please Note: pdoane is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Minimum Size Breaker for Sub Panel

Beyond your SOP. You need to do an actual load calc. as speedy and Marc have said. The sum of the breakers (amp potential) in a panel has nothing to due with the sizing of the main breaker. (i.e. the potential that ALL the circuits are on at one given time at their maximum load is not realistic as Speedy has also hinted to.) Manufacturers set their own panel ratings and can usually be found on their name plate. But I'm no expert and may be corrected as well.
Reply With Quote
  #6  
Old 5/20/07, 9:07 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Minimum Size Breaker for Sub Panel

Even if the feeder to that panel is undersized, that feeder is protected by a breaker in the main panel. As long as the feeder size jives with that feeder breaker size, no hazard exists. The breaker will trip if the feeder is ever overloaded. Might be a nuisance to someone in the future, if it were to happen, but certainly not a hazard. I don't know much about home inspection SOP, but I'd recommend that you concentrate you effort on making sure the feeder breaker matches the feeder gauge, and worry less about the actual connected load in the subpanel, unless you know how to do those calculations.
Reply With Quote
  #7  
Old 5/20/07, 9:16 PM
Larry D. Kage Larry D. Kage is offline
InterNACHI Member
 
Join Date: Jul 2004
Location: Lake Ann (Traverse City), MI
Posts: 5,744
Default Re: Minimum Size Breaker for Sub Panel

Quote:
Originally Posted by Marc D. Shunk
Even if the feeder to that panel is undersized, that feeder is protected by a breaker in the main panel. As long as the feeder size jives with that feeder breaker size, no hazard exists. The breaker will trip if the feeder is ever overloaded. Might be a nuisance to someone in the future, if it were to happen, but certainly not a hazard. I don't know much about home inspection SOP, but I'd recommend that you concentrate you effort on making sure the feeder breaker matches the feeder gauge, and worry less about the actual connected load in the subpanel, unless you know how to do those calculations.
Even if you do know how to do the calcs, it's is way beyond the SOP but looking for the hazard, as Marc explains it, is appropriate.



____________________________________________
"An Education, not just an Inspection"

Larry Kage
Lake Ann (Traverse City), Michigan 49650
231 929 3525


Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond.


ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER

ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
Reply With Quote
  #8  
Old 5/21/07, 7:24 PM
Paul W. Abernathy's Avatar
Paul W. Abernathy Paul W. Abernathy is offline
InterNACHI Member
 
Join Date: Sep 2005
Location: Harrisonburg, VA
Posts: 7,539
Send a message via AIM to pabernathy Send a message via MSN to pabernathy
Default Re: Minimum Size Breaker for Sub Panel

Quote:
Originally Posted by rmoewe
Can someone tell me what the MINIMUM size breaker is to supply a fairly large and full sub panel, (17 breakers, 2 of the 30 amp and the rest 15 and 20 amp breakers). I had one that the Main is not labeled, of course and can not tell what breaker the sub is being fed by. I do know that the supply wire to the sub is only a number 6, which is good for up to a 60 amp breaker. 60 amps does not seem to be big enough, to me.
Thanks, Rick
Speedy and Marc are very right here ....See the calculation is needed to determine the demand for this remote distribution panel and you simply have not given enough information for these gentlemen to assist you.

Yes. it is beyond scope and your efforts to care for your client is very noted and I totally understand but without the proper information it is hard to come up with the answers for you....we can hazard a guess if you can provide us with the dwelling square footage being served by this panel, the identified breakers within this panel ( if not labeled defer anyway and let the electrician handle it )...a # 6 to a remote distribution panel with lets see...(2) double poles and (13 ) single poles may appear as alot but without knowing exactly what is being supported by this remote distribution panel...it is a hard call.

As I believe peter stated.....you would be amazed the variety of calcs you can get using standard or optional methods and so on....so it is just not something you are gonna want to dabble in.....if you have other issues in this dwelling...defer the issues, make note of your concerns and let the electricians determine the rest.



Paul W. Abernathy,CMI,CEI,CEPE
NECŪ Consultant/Columnist
www.twitter.com/ElectricalGuru

- ICC & IAEI Certified Electrical Inspector
- ICC & IAEI Certified Electrical Plans Examiner
- Look for my article in the Nov/Dec 2009 IAEI Magazine
- 2007 "Top Gun" Winner - Mike Holt Enterprises
" visit www.TheElectricalGuru.com Today !"

Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
National Electrical Code Information and Discussion jtedesco1 Electrical 44 4/18/08 12:43 AM
Help. What is the correct way to report a breaker that is too big. gromicko Electrical 72 3/12/08 12:19 AM
Service wire size to breaker panel sfalvey Electrical 12 10/31/06 5:28 PM
Panel Inspection Safety roconnor Electrical 10 9/24/06 10:02 PM
Bad electrical problem Pest Guy Electrical 4 1/20/06 10:26 PM


All times are GMT -4. The time now is 8:09 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts