Can someone tell me what the MINIMUM size breaker is to supply a fairly large and full sub panel, (17 breakers, 2 of the 30 amp and the rest 15 and 20 amp breakers). I had one that the Main is not labeled, of course and can not tell what breaker the sub is being fed by. I do know that the supply wire to the sub is only a number 6, which is good for up to a 60 amp breaker. 60 amps does not seem to be big enough, to me.
Thanks, Rick |
|
#2
|
|||
|
|||
|
Please Note:
Speedy Petey is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
What if one 30 is feeding A/C and the other is feeding electric heat? What if the rest are feeding simple general receptacles and lighting? See what I am getting at? If you've ever done a load calc on a home you'd see the actual demand load is not usually what you would think. It is very typical to have a fully loaded 40 space 200 amp panel with a demand load of under 150 amps. |
|
#3
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
|
|
#4
|
||||
|
||||
|
Please Note:
rmoewe is a non-member guest and is in no way affiliated with InterNACHI or its members.
The panel in not labled.
|
|
#5
|
||||
|
||||
|
Please Note:
pdoane is a non-member guest and is in no way affiliated with InterNACHI or its members.
Beyond your SOP. You need to do an actual load calc. as speedy and Marc have said. The sum of the breakers (amp potential) in a panel has nothing to due with the sizing of the main breaker. (i.e. the potential that ALL the circuits are on at one given time at their maximum load is not realistic as Speedy has also hinted to.) Manufacturers set their own panel ratings and can usually be found on their name plate. But I'm no expert and may be corrected as well.
|
|
#6
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Even if the feeder to that panel is undersized, that feeder is protected by a breaker in the main panel. As long as the feeder size jives with that feeder breaker size, no hazard exists. The breaker will trip if the feeder is ever overloaded. Might be a nuisance to someone in the future, if it were to happen, but certainly not a hazard. I don't know much about home inspection SOP, but I'd recommend that you concentrate you effort on making sure the feeder breaker matches the feeder gauge, and worry less about the actual connected load in the subpanel, unless you know how to do those calculations.
|
|
#7
|
|||
|
|||
|
Quote:
____________________________________________ "An Education, not just an Inspection" Larry Kage Lake Ann (Traverse City), Michigan 49650 231 929 3525 Professional Inspector and Infrared Thermographer serving the Traverse City, Michigan area and beyond. ITC/FLIR CERTIFIED BUILDING SCIENCES THERMOGRAPHER ITC/FLIR CERTIFIED LEVEL 1 THERMOGRAPHER
|
|
#8
|
||||
|
||||
|
Quote:
Yes. it is beyond scope and your efforts to care for your client is very noted and I totally understand but without the proper information it is hard to come up with the answers for you....we can hazard a guess if you can provide us with the dwelling square footage being served by this panel, the identified breakers within this panel ( if not labeled defer anyway and let the electrician handle it )...a # 6 to a remote distribution panel with lets see...(2) double poles and (13 ) single poles may appear as alot but without knowing exactly what is being supported by this remote distribution panel...it is a hard call. As I believe peter stated.....you would be amazed the variety of calcs you can get using standard or optional methods and so on....so it is just not something you are gonna want to dabble in.....if you have other issues in this dwelling...defer the issues, make note of your concerns and let the electricians determine the rest. Paul W. Abernathy,CMI,CEI,CEPE NECŪ Consultant/Columnist www.twitter.com/ElectricalGuru - ICC & IAEI Certified Electrical Inspector - ICC & IAEI Certified Electrical Plans Examiner - Look for my article in the Nov/Dec 2009 IAEI Magazine - 2007 "Top Gun" Winner - Mike Holt Enterprises " visit www.TheElectricalGuru.com Today !" |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical | 44 | 4/18/08 12:43 AM |
| Help. What is the correct way to report a breaker that is too big. | gromicko | Electrical | 72 | 3/12/08 12:19 AM |
| Service wire size to breaker panel | sfalvey | Electrical | 12 | 10/31/06 5:28 PM |
| Panel Inspection Safety | roconnor | Electrical | 10 | 9/24/06 10:02 PM |
| Bad electrical problem | Pest Guy | Electrical | 4 | 1/20/06 10:26 PM |