#1
|
|||
|
|||
|
I inspected a house that had a main panel that looked OK, except that a few of the circuit breakers (indicated) appeared that they may have been of the wrong type of the panel -- though they were well seated, and appeared to fit very well in it.
Is there any problem with this, and if so, what is it? |
|
#2
|
||||
|
||||
|
Panel make/model?
Breakers make/model? tom |
|
#3
|
|||
|
|||
|
Yeah, I forgot to mention that the panel is a common Siemens panel, for which QP breakers are recommended. The pertinent info on the different looking circuit breakers was unreadable, but they did appear to have been installed with the original job.
|
|
#4
|
|||
|
|||
|
And the photo quality is limited by sizing constraints for posting. I could get it a little better, but that would not add anything to the value of the pic.
|
|
#5
|
|||
|
|||
|
The breakers installed in the panel should be the ones listed by the manufacturer, otherwise it is incorrect in most instances.
Don't interfere with anything in the Constitution. That must be maintained, for it is the only safeguard of our liberties. Abraham Lincoln www.qualityhomeinspectionsfl.com |
|
#6
|
|||
|
|||
|
unless of course they are " Classified " breakers made by Eaton.....they have UL Approved replacement breakers for many panels on the market today...be aware guys that you will see alot more of the " Classified " versions and they meet UL for the enclosures to which they are in......they are 3rd party tested and approved by UL......and no they do not void any manufactures warranty...Magnesson -Moss Act prohibits manufactures from making that claim about warranty being voided......
Paul W. Abernathy |
|
#7
|
|||
|
|||
|
However...in the case of the ones in your photo...which I can't see....it would be a problem unless the enclosure lists them....otherwise just because they fit does not make them approved....
Thats the difference with " Classified " breakers....they have been formally approved for many older styles like ITE, Gould, Crouse-Hinds, T & B, Square D ( both QO and Hom )....and a few others.... Those in the picture are not classifieds......... Paul W. Abernathy |
|
#8
|
|||
|
|||
|
Bye Bye......just got back from Jacksonville, FL doing a seminar...and I am off to Danville for another one.....later guys...see ya Monday.
Paul W. Abernathy |
|
#9
|
||||
|
||||
|
Here's what I often say: "The panel is equipped with breakers manufactured by a company other than the panel manufacturer. Panel manufactures warn that the use of other types of breakers "voids the warranty, may void the UL listing, and could result in property loss and personal injury." An evaluation of the acceptability of the breakers is recommended."
If you read the label inside the panel, that's the language often used. “The things that will destroy America are peace at any price, prosperity at any cost, safety first instead of duty first, the love of soft living, and the get-rich-quick theory of life.” Theodore Roosevelt Joe Funderburk, CMI Alpha & Omega Home Inspections, LLC Inspecting Upstate SC & Charlotte Metro, NC NACHI ID: NACHI05120170 www.aohomeinspection.com |
|
#10
|
|||
|
|||
|
hey......back from Danville.....wanted to chime in again on this. If a manufacture ( like Square D) tells someone even on a sticker that using a breaker other than theirs violates a warranty....they are in BIG trouble due to the Magnesson-Moss Act......if the replacement breaker is 3rd party tested and approved it will NOT void the warranty...This is against the law to make that statement...."Classified" breakers are UL listed........they are approved for the replacement in many enclosures.......but ONLY breakers that are 3rd party tested.....
Paul W. Abernathy |
|
#11
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
Quote:
See the UL Panelboards Marking Guide FIELD INSTALLED UNITS OR EQUIPMENT 38. A panelboard to which a unit, such as a circuit breaker, switch, or the like, may be added in the field is required to be marked to identify the units that can be added. Units made by different manufacturers or of a different style are not identical in all details and therefore may not be interchangeable. Plug-in clips and blades must be matched if poor connections and overheating are to be avoided. Additionally, over-surface and through-air electrical spacings, between live parts of opposite polarity and to grounded metal, often depend on the proper mating of units and the bases into which they are plugged or bolted. Circuit Breakers Marking Guide Commercial Cooking Equipment Marking & Application Guide Dampers Marking Guide Dead-front Switchboards Marking Guide Electrical Heating and Cooling Equipment Marking Guide Luminaires Marking Guide Panelboards Marking Guide Swimming Pools and Spa Marking Guide Wire and Cable Marking Guide http://www.ul.com/regulators/2007USWhiteBookFinal.pdf |
|
#12
|
||||
|
||||
|
Quote:
Gary Porter GLP's Home and Mold Inspections 321-239-0621 Certified Commercial Mold Inspector Serving Orlando, Kissimmee, Winter Park, Winter Springs, Oviedo, Titusville, Celebration, Harmony, Avalon, Windermere, Deltona, Debary, Sanford Orange County, Seminole County, Volusia County, Osceola County www.homeandmoldinspections.com |
|
#13
|
|||
|
|||
|
•Magnusson-Moss Warranty Act prevents manufacturers from making warranties contingent upon the use of their replacement parts, as long as the third-party part is safe. Since UL has proven safety, the panelboard manufacturer’s warranty is still effective when using CL or CHQ breakers.
Paul W. Abernathy |
|
#14
|
||||
|
||||
|
For years, consumers were screwed by automakers voiding warranties because non-OEM replacement parts were used. Good to see this trickled down to common consumer products.
tom |
|
#15
|
|||
|
|||
|
Please Note:
jtedesco1 is a non-member guest and is in no way affiliated with InterNACHI or its members.
|
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| AFCI Questions and Answers - Mike Holt | pabernathy | Electrical Inspections | 7 | 4/16/12 9:51 PM |
| "UFER" Ground? see last paragraph. | jtedesco1 | Electrical Inspections | 19 | 8/23/11 3:56 PM |
| Article 240 : Overcurrent Protection Article | pabernathy | Electrical Inspections | 0 | 5/23/07 11:40 AM |