Default Mismatched dead front

I recently inspected a residence that had an ITE distribution panel with a new Siemens dead front. I'm assuming a Siemens dead front was used because the electrician couldn't find an ITE dead front, and someone didn't want to replace the entire panel. The problem was that the Siemens dead front was larger than the box, and only two screws (of six) lined up properly to secure the dead front. The top two and bottom two did not line up, and the electrician merely screwed them in to the drywall using wood screws. Needless to say, these four screws were holding nothing when I removed the dead front. The spacing and size of the breaker slots wasn't perfect either, but it was good enough to allow access to all the breakers.

I tagged the panel, citing that the dead front needed to be fastened securely around its entire perimeter. My question is: is there some code that stipulates that the dead front must match the rest of the panel, i.e., Siemens with Siemens, Square D with Square D, etc.? Also, how about specific code addressing the ill-fitting dead front.?

The buyer asked me what I thought could be done to fix things. I told her I thought an electrician could mark the dead front where the screw holes are supposed to be, remove it, drill new holes in the dead front at those locations, and re-attach it to the box with proper screws in the four new holes and the two old ones. Anybody think that's a good idea? I realize the ideal thing is to replace the entire panel, but the panel was perfect except for the mismatched dead front.

Thanks for any responses!
Reply With Quote
  #2  
Old 2/9/07, 1:08 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: Mismatched dead front

I usually find that wnen a panel cover does not match the panel, that the box was an old fuse panel that was converted to a breaker box - not allowed.

All boxes must be UL listed. By using different cover panels, you are no longer UL listed, and the warranty on the box is voided.



Bill Siegel
Florida Home Inspection Team Inc.
Reply With Quote
  #3  
Old 2/9/07, 9:54 PM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Mismatched dead front

Quote:
Originally Posted by wsiegel
I usually find that wnen a panel cover does not match the panel, that the box was an old fuse panel that was converted to a breaker box - not allowed..
I think it is important to note that there are several UL listed kits to do just this. Here is one manufacturer's measuring and ordering instructions: http://www.inspect-ny.com/fpe/CHRetrofitGuide.pdf

I have used these kits on old fuse panels, FPE panels, and Zinsco panels. Mostly when the panel is flush mounted, and the existing can has the branch circuits in pipe.
Reply With Quote
  #4  
Old 2/9/07, 11:29 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: Mismatched dead front

Marc,

That is very interesting. It seems every day there is something new to learn.
My question now is - Are the retrofit panels marked so we can list them as such in our report, or do we need a sparky to verify them?



Bill Siegel
Florida Home Inspection Team Inc.
Reply With Quote
  #5  
Old 2/10/07, 10:22 AM
Marc D. Shunk's Avatar
Marc D. Shunk Marc D. Shunk is offline
Active Poster
 
Join Date: Dec 2006
Location: Central PA
Posts: 1,967
Please Note: Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Default Re: Mismatched dead front

Quote:
Originally Posted by wsiegel
Are the retrofit panels marked so we can list them as such in our report, or do we need a sparky to verify them?
There is labeling inside the panel cover to indicate that they are a retro-fit kit. I'm just not famaliar enough with the rules of your trade to speak about whether you'd need the panel looked at by another tradesman or not.
Reply With Quote
  #6  
Old 2/10/07, 10:56 PM
William E. Siegel William E. Siegel is offline
InterNACHI Member
 
Join Date: Oct 2006
Location: Hialeah, Fl
Posts: 1,788
Default Re: Mismatched dead front

I would imagine that a permit would be required for a retrofit (like anyone would really get one), so, until I find out for sure, I will continue to defer for certification.



Bill Siegel
Florida Home Inspection Team Inc.
Reply With Quote
Reply

Thread Tools

Posting Rules
You may not post new threads
You may not post replies
You may not post attachments
You may not edit your posts

BB code is On
Smilies are On
[IMG] code is On
HTML code is Off
Trackbacks are On
Pingbacks are On
Refbacks are On


Similar Threads
Thread Thread Starter Forum Replies Last Post
Wrong screws on panel front kgraham Electrical 12 4/5/07 6:26 PM
70 MPH... Is that my Trucks front wheel passing us!?! jsieg Misc. Discussion 9 4/2/07 8:51 AM
Dead front question dsmith6 Electrical 14 12/4/06 2:23 PM


All times are GMT -4. The time now is 5:30 AM.


Copyright © International Association of Certified Home Inspectors, Inc. 1 2 3 4 5 6 7 8 9 10 11 12 13 14 15 16 17 18 19 20 21 22 23 24 25 26 27 28 29 30 31 32 33 34 35 36 37 38 39 40 41 42 43 44 45 46 47 48 49 50 51 52 53 54 55 56 57 58 59 60 61 62 63 64 65 66 67 68 69 70 71 72 73 74 75 76 77 78 79 80 81 82 83 84 85 86 87 88 89 90 91 92 93 94 95 96 97 98 99 100 101 102 103 104 105 106 107 108 109 110 111 112 113 114 115 116 117 118 119 120 121 122 123 124 125 126 127 128 129 130 131 132 133 134 135 136 137 138 139 140 141 142 143 144 145 146 147

Popular Sections

:

All Sections

Popular

Membership

Inspection Standards

Education

Chapters & Members

Articles & Links

Other Organizations

 

 

 

NACHI.ORG Statistics

 

 

no new posts