There is no grommet or clamp where the furnace conductors enter the junction box within the furnace. I want to make sure that the NEC still applies to the wiring within the furnace. What is required to protect/secure the wires here?
|
|
#2
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
Yes there should be a bushing there. I bet it was thrown away or lost by the installer
|
![]() |