Can Cutler-Hammer breakers be used inside Commander panels? There were some mixed in but they seemed to fit properly.
Chris |
|
#2
|
|||
|
|||
|
Did you read the information plate on the cover. It will list the breakers that can be used with that panel. Those breakers may work, but it becomes a UL listing issue.
|
|
#3
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Challenger/Commander are the same, and the Cutler-Hammer type BR breaker is okay'd for the Challenger panel. Here's a copy of the UL letter. http://www.eatonelectrical.com/unsec...T01221002E.PDF
There was a transitional period of time in which Challenger and Commander panels said Cutler-Hammer/Challenger and Cutler-Hammer/Commander right on them. |
|
#4
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
There is also a situation of "classified" breakers. It is usually a Challenger breaker in a SqD panel. U/L says it was evaluated and approved, SqD says they are not on the label so you can't do it. Inspectors are split on the issue.
The last I heard they were including a sticker with the breaker you could put on the door. |
|
#5
|
||||
|
||||
|
Please Note:
relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
It is like generic medicine.Manufacturer has final say though when it comes to liability.
|
|
#6
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I tend to vote with those who say, if a NRTL says it is OK it is OK.
ConAgra says Peter Pan Peanut butter should be spread on Peppridge Farm bread too. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical | 44 | 4/18/08 12:43 AM |
| Panel Inspection Safety | roconnor | Electrical | 10 | 9/24/06 10:02 PM |
| Bryant Panel and Gould Breakers | tneumann | Electrical | 27 | 4/28/06 9:04 AM |
| Different Circuit Breakers Used in Panel | jtedesco1 | Electrical | 10 | 2/6/06 11:45 PM |
| Bad electrical problem | Pest Guy | Electrical | 4 | 1/20/06 10:26 PM |