#1
|
|||
|
|||
|
Can Cutler-Hammer breakers be used inside Commander panels? There were some mixed in but they seemed to fit properly.
Chris |
|
#2
|
|||
|
|||
|
Please Note:
wsiegel is a non-member guest and is in no way affiliated with InterNACHI or its members.
Did you read the information plate on the cover. It will list the breakers that can be used with that panel. Those breakers may work, but it becomes a UL listing issue.
|
|
#3
|
||||
|
||||
|
Please Note:
Marc D. Shunk is a non-member guest and is in no way affiliated with InterNACHI or its members.
Challenger/Commander are the same, and the Cutler-Hammer type BR breaker is okay'd for the Challenger panel. Here's a copy of the UL letter. http://www.eatonelectrical.com/unsec...T01221002E.PDF
There was a transitional period of time in which Challenger and Commander panels said Cutler-Hammer/Challenger and Cutler-Hammer/Commander right on them. |
|
#4
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
There is also a situation of "classified" breakers. It is usually a Challenger breaker in a SqD panel. U/L says it was evaluated and approved, SqD says they are not on the label so you can't do it. Inspectors are split on the issue.
The last I heard they were including a sticker with the breaker you could put on the door. |
|
#5
|
||||
|
||||
|
Please Note:
relliott is a non-member guest and is in no way affiliated with InterNACHI or its members.
It is like generic medicine.Manufacturer has final say though when it comes to liability.
|
|
#6
|
|||
|
|||
|
Please Note:
Greg Fretwell is a non-member guest and is in no way affiliated with InterNACHI or its members.
I tend to vote with those who say, if a NRTL says it is OK it is OK.
ConAgra says Peter Pan Peanut butter should be spread on Peppridge Farm bread too. |
![]() |
| Thread Tools | |
|
|
Similar Threads
|
||||
| Thread | Thread Starter | Forum | Replies | Last Post |
| National Electrical Code Information and Discussion | jtedesco1 | Electrical Inspections | 50 | 6/15/10 8:28 PM |
| Panel Inspection Safety | roconnor | Electrical Inspections | 10 | 9/24/06 10:02 PM |
| Bryant Panel and Gould Breakers | tneumann | Electrical Inspections | 27 | 4/28/06 9:04 AM |
| Different Circuit Breakers Used in Panel | jtedesco1 | Electrical Inspections | 10 | 2/6/06 11:45 PM |
| Bad electrical problem | Pest Guy | Electrical Inspections | 4 | 1/20/06 10:26 PM |